3 Phase vs. Single Phase Heating Elements

06/05/2016 5:19 AM

Hi guys, I am an ceramics engineer and i have found a problem in our furnace.

We have a electrical furnace which has 3 different heating zone and each one is controlled by a separate controller. recently we renewed the heating elements inside the furnace. the company which did it has changed the wiring from 3 phase to single phase and has reduced the amount of used heating wires inside the furnace.

I want to know is it going to have a serious effect on lifetime of heating elements, precision of furnace or energy consumption? Can you please say me whats the difference between 3 phase and single phase wiring in electrical furnaces? whats the benefits and disadvantages of each one?

Thanks for your help advanced.

Register to Reply
Pathfinder Tags: 3phase electrical furnace
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#1

Re: 3phase vs. single phase heating elemts

06/05/2016 5:54 AM

Would be nice to view the wiring diagram for your heaters, (before and after.) but, for wiring three phase heating elements you normally wire them in series, while for single phase you'd wire them in parallel.

As a lot of people know, on the when wired in series, if one element would fail, all would fail like the old Christmas tree lights. But on heaters the loss of a single element in a series connected with three phase floating wye configuration, will immediately cut the input power to the furnace in half and that the loss of a second element will cut the furnace input power to zero.

Here is a link of heater wiring configuration for comparison.

http://www.rayteq.com/series_vs_parallel.shtml

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Score 1 for Good Answer
Member

Join Date: Jun 2016
Posts: 8
#2
In reply to #1

Re: 3phase vs. single phase heating elemts

06/05/2016 6:35 AM

Thank you Phoenix for your answer

All i know for the moment is that the furnace was using 90A from each phase with a delta wiring before renew. but now it uses around 130A from each phase and each zone of furnace is connected to one phase. the company claims that the current has increased but total time has decreased and so the energy consumption is the same. Also i know we had 432m of 3mm diameter heating wire before and 144 m of 3.5 mm heating elements. elements are the same type and just weigh has decreased by 2.2 factor.

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#3
In reply to #2

Re: 3phase vs. single phase heating elemts

06/05/2016 7:29 AM

Hamids740

There have been discussions simular to on this site. I just did a quick search, but there seems to be some differences in the wiring that can play a big part.

http://cr4.globalspec.com/thread/67458/3-Phase-Heating-Element-Problem

There are other members here that either has the knowledge and expertise or excellent research abilities that can help better then myself.

But I'm sure they would request more details.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#8
In reply to #2

Re: 3phase vs. single phase heating elemts

06/05/2016 4:17 PM

I am assuming from your posts that the heaters were originally wired as Delta three phase and now they are wired as Wye. In the diagram below, Ra, Rb, and Rc are the original heater coils and R1, R2, and R3 are the new heater coils.

For the circuit to be equivalent, you need to figure the new resistances using the Delta-Wye transformations.

https://en.wikipedia.org/wiki/Y-%CE%94_transform

Set Ra = Rb = Rc = 1. Then R1 = R2 = R3 = 1/3

Calculate resistance from your dimensions:

The heater coil resistance is directly proportional to the length and inversely proportional to the square of the diameter (in mm):

144000/(3.5)^2 = 11750 (new, R1, R2, R3)

432000/(3)^2 = 48000 (old, Ra, Rb, Rc).

From the heater dimensions it looks like R1, R2, & R3 are 1/4 of Ra, Rb, & Rc, (3/4 of what it would be as equivalent) so the heater now draws more current and dissipates more power. The current draw would be 4/3 of the old configuration, about 120 A vs 90 amps, close to what you are reporting.

Register to Reply Good Answer (Score 2)
Member

Join Date: Jun 2016
Posts: 8
#9
In reply to #8

Re: 3phase vs. single phase heating elemts

06/05/2016 4:39 PM

Thanks for your through complete answer

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#10
In reply to #8

Re: 3phase vs. single phase heating elemts

06/06/2016 12:38 AM

Dear sir

I think your reply is irrelevant now.

Original configuration of elements was either delta or star formation. Generally it will be star formation for three phase input supply

Revised configuration is for single phase supply. In this case all elements will be in parallel only and there will not be series connection.

Naturally in single phase formation,the total current drawn by the lead cable will be more than in 3 phase formation.

But power consumption and heat generation will be same.

In three phase system even if one phase supply fails 66% of elements will be on and some heat will be generated, but in single phase formation if single phase fails, no element will be on and no heat will be generated.

In single phase the looping cable size to be rated that of lead cable.

For example, assume there are 3 elements of 5 kw each connected in star formation in three phase system of 415 volts.

Total load 15 kw

Line current of each phase will be (15x 1000)/(1.732x415) =20.86 Amps

If the same elements are connected in single phase formation, the line current would be 15 x 1000/230 = 65 Amps.

In this instance the led cable and looping cable are to be rated for more than 65 Amps.

Please check whether this aspect is considered while changing to single phase formation.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Member

Join Date: Jun 2016
Posts: 8
#12
In reply to #10

Re: 3phase vs. single phase heating elemts

06/06/2016 5:20 PM

Thank you for your answer. This is actually what i am looking for.your answer is completely helpful for me. but increasing the current in that case mean more current in each single heating element and then less life time?

Again thanks for your answer

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#15
In reply to #12

Re: 3phase vs. single phase heating elemts

06/06/2016 9:11 PM

Whatever current your heaters run at, it is assumed they are designed and rated to work continuously at that temperature - thus you would not expect them to burn out.

I am not a heater expert, but looking at my domestic cooker, the grill pan is rated at 2kW and glows red hot and will run continuously red hot at that temperature without burning out because that is what it is designed to do.

My 2kW electric kettle, on the other hand, without any water to take away the heat fast enough, or if it boils dry, will glow red hot for a few minutes and then likely burn out, but the auto thermostatic cut-out works to protect the heater because the element, although consuming the same current, and thus the same heat, is not designed or rated to run at red hot temperatures - and will soon burn out if the rated current is not reduced.

In other words, your elements, however connected, should be rated for the temperature they reach - and should last just as long - life is shortened when they 'overheat' - which is as much to do with heat dissipation in the process as it is to do with the current in the first place (eg. kettle without water),

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#16
In reply to #12

Re: 3phase vs. single phase heating elemts

06/07/2016 1:35 AM

I wanted to clarify here that the current drawn by individual element will be same in both single phase and 3 phase arrangement.

Taking the example from my previous post,

In single phase, each element is 5 kw, therefore current drawn by this element is =5 x 1000/230= 21.7 Amps.

In three phase system the Current drawn by individual element will be=(15 x 1000)/(415 x 1.732) =20.86 amps.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#18
In reply to #16

Re: 3phase vs. single phase heating elemts

06/07/2016 7:31 AM

I am afraid your numbers are adrift. You have used 415v 3-ph and 230v 1-ph in your calculations.

415v 3-phase gives 240v single phase, or 230v 1-phase gives 400v 3-phase.

Which is it?

Apart from the precision of the result, the only difference as I can see, is you need a 2 large cables to feed 3 single phase heaters in parallel, or 3 smaller cables to feed 3 heaters in Star. Nothing has changed total heatwise. Temperature control is a separate issue.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#19
In reply to #10

Re: 3phase vs. single phase heating elemts

06/07/2016 10:20 AM

One of your statements is way off. You state single phase heaters are all in parallel. Then you turn around and state that the power goes to zero if even one element fails. WRONG. You need to back-up there, cowboy, and take another shot at that tin can.

If this is an industrial plant making some parts that are heat bonded, the whole thing is getting ready for a big ol' oops. If this is someone's home toaster oven, good luck, and don't burn the bread.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Member

Join Date: Jun 2016
Posts: 8
#6
In reply to #1

Re: 3phase vs. single phase heating elemts

06/05/2016 8:23 AM

Thanks again, i have request from the for wiring diagram and all details, as soon as i recieved it i will upload it here.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: 3phase vs. single phase heating elemts

06/05/2016 7:38 AM

What reason did the company give for altering the wiring?

A drawing would be a great help to us.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Jun 2016
Posts: 8
#5
In reply to #4

Re: 3phase vs. single phase heating elemts

06/05/2016 8:21 AM

The reason that did it was a mistake actually. When they brought new furnace and started it for the first time, they understood with the same wiring of past furnace need around 270A because of probably less amount of heating elements, so not to change the whole heating elements they decided to change to the wiring connection.

and now i want to know whats the disadvantage of it.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7

Re: 3 Phase vs. Single Phase Heating Elements

06/05/2016 11:58 AM

Resistance heating is pretty much you get what you pay for,, watts used = heat produced...If the total amps drawn is the same then you have the same amount of heat produced...If you are drawing more amps then you are producing more heat....So it takes the furnace less time to satisfy the thermostat by producing more heat...this is generally an energy saving strategy, as long as the more rapid heating has no ill effect...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#11

Re: 3 Phase vs. Single Phase Heating Elements

06/06/2016 9:33 AM

I am not able to come up with an explanation because I have no knowledge or experience of working with industrial heaters. But you refer to the affect on heat, and you have a lot of answers to help you, but I am puzzled because no mention has been made of the actual working temperature you wish to achieve.

Different ways of connecting elements might have an effect on the working temperature you want. Perhaps that's the reason.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Member

Join Date: Jun 2016
Posts: 8
#13
In reply to #11

Re: 3 Phase vs. Single Phase Heating Elements

06/06/2016 5:22 PM

the working temperature is around 1250 C and the volume of furnace is about 1 cubic meter.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#14

Re: 3 Phase vs. Single Phase Heating Elements

06/06/2016 7:42 PM

In general terms, Rixter and Ramvinod have given good answers; but in specific terms we do not have enough information from the OP to determine what is really going on. There are several combinations of star/delta/series/parallel in which a multitude of heating elements can be wired. We haven't even been given the ratings of any of the individual elements.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: 3 Phase vs. Single Phase Heating Elements

06/07/2016 3:12 AM

The correct destination for this query is the company that carried out the modifications.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#20

Re: 3 Phase vs. Single Phase Heating Elements

06/07/2016 12:14 PM

who's the joker giving Ramvinod #10 a GA for an answer that is mathematically wrong.

415v 3-ph is not 230v 1-ph

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: