Generator Solenoid Switch

06/14/2016 9:16 AM

I there any negative effect when a 24V solenoid switch is permanently connected to 24V DC supply?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: GENERATOR SOLENOID SWITCH

06/14/2016 9:22 AM

It will be either permanently open or permanently closed, depending on how it is connected.

How did you get your job?

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: GENERATOR SOLENOID SWITCH

06/14/2016 9:25 AM

There will be smoke if the solenoid is not continuously-rated.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Power-User

Join Date: Nov 2015
Posts: 335
#3

Re: GENERATOR SOLENOID SWITCH

06/14/2016 9:29 AM

Solenoid Coil is NEMA class rated basing on the number of hours of operation at a certain temperature. If the coil is provided with enough ventilation or at a tolerable environment and not overheated. It should last at its lifespan.

And, if contacts rating is not overloaded I think it should be fine.

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: GENERATOR SOLENOID SWITCH

06/14/2016 10:12 AM

....so the negative effect, about which is what the original poster asked, would be from the vendor's perspective in extending the time between replacements, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2015
Posts: 335
#8
In reply to #4

Re: GENERATOR SOLENOID SWITCH

06/14/2016 8:53 PM

Perhaps...But, the positive side for the OP is getting answers free of charge. Though, he should consider CR4 disclaimer in anything said on this site, like Jackofalltrades were saying.

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #3

Re: GENERATOR SOLENOID SWITCH

06/14/2016 2:01 PM

Given the history of the OP, we would have no way of knowing that the coil is NEMA rated.

Register to Reply
Power-User

Join Date: Nov 2015
Posts: 335
#9
In reply to #6

Re: GENERATOR SOLENOID SWITCH

06/14/2016 9:01 PM

I am not accustomed to any standard other than NEMA for coils based on experience, perhaps there are other standards out there.

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10
In reply to #3

Re: GENERATOR SOLENOID SWITCH

06/14/2016 10:57 PM

"...Solenoid Coil is NEMA class rated basing on the number of hours of operation at a certain temperature..."

No it is not, the NEMA ratings are for equipment that might be exposed to liquids, dust, etc., refer to the ability to operate properly under those conditions, and are similar to the IEC Standard 60529 IP (Ingress Protection) ratings.

The operating parameters are set by the manufacturer and are based upon the insulation materials' class/temperature ratings, and/or the operating conditions.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: Generator Solenoid Switch

06/14/2016 11:52 AM

A negative effect on what?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Generator Solenoid Switch

06/14/2016 3:56 PM

This could cause the generator to burn out, but it depends on how the solenoid has been connected up in the circuit.

Given your previous questions I think we are all a little concerned you may be in over your head, potentially putting what look like paying commercial customers at risk. Please be aware that CR4 is not a substitute for proper training or qualifications, especially in a job. It is unethical.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#11

Re: Generator Solenoid Switch

06/15/2016 1:48 AM

Assuming that by "24V solenoid switch", you are referring to a relay, and that you mean that the 24V supply is permanently connected to the coil of that 24V relay (not the switch terminals of the relay), then the answer is YES!

1. The solenoid is constantly wasting energy.

2. There is no reason for the solenoid to be there. A simple switch with no solenoid would do the same job.

3. There is a possibility of the solenoid overheating, especially if it is mounted in a confined space.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#14
In reply to #11

Re: Generator Solenoid Switch

06/15/2016 10:41 AM

Is the function of the solenoid to act as a drop out relay?

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#12

Re: Generator Solenoid Switch

06/15/2016 4:57 AM

Depends on the specific model. Some solenoid switches (relays, most people call them) are rated for continuous energising, others aren't. I'd check with the supplier.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#13

Re: Generator Solenoid Switch

06/15/2016 8:18 AM

Negative effect = wasted money. Why have it in there if it is never used? I assume an air control solenoid, and a manual valve will do the same thing, unless you forgot to mention this is in the E-stop circuit. (???) We do this on most process skids - the incoming solenoid for instrument/valve air is on all the time unless the E-stop is tripped or the main power is shut off, and on some, with Cat 3 safety requirements, there are two in series, always on as long as previously mentioned parameters are met.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Codemaster (1); dkwarner (1); jack of all trades (1); JohnDG (1); Jpfalt (1); lyn (2); Mr. small (3); Phys (1); PWSlack (1); RAMConsult (1); redfred (1)

Previous in Forum: Off-Grid Inverter Driven Fridge Starting Problem   Next in Forum: Please Explain How This Ground Detection Circuit Works ?

Advertisement