Digital Multimeters & Contactor Coils

07/11/2016 6:09 AM

A couple weeks back I diagnosed a "faulty" contactor on an Electrolux industrial washer as open circuit.

I used a fluke 179, a fluke 1653b and an old school kyoritsu insulation tester(analogue) on ohms and had full open circuit reading.

My boss pulls out some wierdo old school tester and showed the coil to be intact.

So I still decided to sell the new contactor to the customer & open the old one to which I found a little blue component. maybe a little cap I'm not sure... ( allen Bradley contactor)

Can someone explain this to me please or direct me to relevant information.

Cheers

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Digital Multimeters & contactor coils

07/11/2016 6:28 AM

If everybody shows up with a multimeter, perhaps this can be settled by some sort of voting process.

Did the new contactor work?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Jan 2015
Posts: 8
#2
In reply to #1

Re: Digital Multimeters & contactor coils

07/11/2016 6:47 AM

I didn't realize this at the time, I was given a fault code of 082 or something along those lines by the operator. I looked in the manual & found the closest thing with an 8 was related to the heating circuit, hence ending up at the contactor coil.

the contactor brings in a heater bank & which is no longer use due to a new "ozone system".

I didn't actually test the new contactor as the machine has been reconfigured.

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#3
In reply to #2

Re: Digital Multimeters & contactor coils

07/11/2016 7:37 AM

So, the Contactor isn't used anymore, right?

Is this no longer an issue, or are you questioning who is correct.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
6
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Digital Multimeters & Contactor Coils

07/11/2016 10:40 AM

Sooooo many issues, my arthritic finger may give out.

A "heating coil" is not the same as a contactor coil. A heating coil is a coil of resistive wire made for the PURPOSE of creating heat, as in a water heater. A contactor coil is an electromagnet intent on moving the contacts of the contactor to act as a switch. Not directly related to each other.

A contactor coil is just a long long piece of insulated wire, called "magnet wire", wrapped around a bobbin. That bobbin is then placed over a steel frame that creates the electromagnet. If you check the resistance on the bench, the only resistance you read is that of the wire itself because until

it interacts with the steel frame, it's just a short circuit. If your meter scale is too high, it appears to be "shorted" meaning virtually no resistance. If you read infinite resistance, that usually means the magnet wire is broken somewhere. But if your meter scale is too low, that might be reading the magnet wire resistance and interpreting that as open. Without knowing what the actual setting and reading was, it's hard to judge what you saw that led you to believe it was open. The apparent fact that it worked(?) would indicate you were wrong.

The little blue thing is likely a surge suppressor across the coil terminals, typically an MOV (metal oxide varistor) used on the coil to protect other sensitive electronics in the equipment from the effects of turning the coil on and off, called "inductive kickback" where the rapidly changing magnetic field of the coil creates a voltage spike on the source. Typically if the blue ones are still blue, they are OL because of they fail, they turn brown, or vaporize altogether.

Whew, made it...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 6)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: Digital Multimeters & Contactor Coils

07/11/2016 11:03 AM

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
7
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Digital Multimeters & Contactor Coils

07/11/2016 1:34 PM

The blue one on the right is still good, the one on the left has sacrificed itself in the line of duty. I'm showing this to allow you to see how different it would look if no good.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 7)
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JDriethmuller (1); JRaef (2); phoenix911 (1); SolarEagle (1); Tornado (1)

Previous in Forum: HVDC Voltage Designations   Next in Forum: Induction Motor

Advertisement