Controlling 8-Pin Relays With Proximity Switches

08/31/2016 11:50 AM

i am in far northern Yukon, trying to control a double acting hydraulic cylinder with 2 prox switches and an 8pin relay. An electrician told me I could do this with 2-5 pin relays, but I could not create a latching circuit. I do have a single 8 pin available. This is a 12v circuit, the relays will control a simple solenoid valve switching from in and out on the cylinder. The prox switches are Turck brand with a nc and a no contact. I was told they are neg switching, which seems to work. Logic tells me I should be able to do this with a single 8pin relay, but I keep getting bogged down with the latching part. It would be wired with both a momentary start switch and a stop switch. Any and all input would be appreciated to help me keep the little hair I have remaining.

The goal is to be able to hit the momentary switch, starting the cycle, and have the cylinder travel in and out continuously controlled by the prox switches until the stop switch is hit. The hydraulic solenoid valve can be switched positive or neg.

thanks for reading!

Register to Reply
Pathfinder Tags: Prox switches and relays
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#1

Re: Controlling 8pin relays with prox switches

08/31/2016 12:43 PM

From your narrative is sounds as if you are controlling the relay with a start (NO/momentary) and stop (NC/momentary) switches. The prox switches are controlling the solenoids - this latching relay is replacing a simple on/off maintained switch (toggle switch) with a Push-To-Start and Push-To-Stop scheme.

Is this correct?

__________________
Semper Ubi Sub Ubi
Register to Reply
Participant

Join Date: Aug 2016
Posts: 3
#12
In reply to #1

Re: Controlling 8pin relays with prox switches

09/01/2016 10:45 AM

Thanks for your response.... I have determined there is no need for a start switch, the system could start by simply providing positive or negative to the coil in relay controlled through a toggle as you said. The prox limit switches control the relays which provide the required amperage to the forward- reverse solenoid valve. The push to start and push to stop complicate things needlessly I am now thinking.��

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#2

Re: Controlling 8pin relays with prox switches

08/31/2016 12:45 PM

Here is a crude drawing of how it can be done. Sorry I don't have a drawing program on this computer.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Controlling 8-Pin Relays With Proximity Switches

08/31/2016 2:07 PM

Here's what I understand: The hydraulic solenoid directs fluid one way when energized and the other way when de-energized. Is this correct? (I am assuming so).

I am assuming that the limit switches are momentary.

I'm thinking that you need two latches, one to control the current through the solenoid (latching one of the limit switches) and the other to latch the start switch.

Your 8 pin relay, I believe is a double throw, double pole relay, but with only one coil it can only create one latch.

You need two 5 pin relays (Single pole double throw).

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#5
In reply to #3

Re: Controlling 8-Pin Relays With Proximity Switches

08/31/2016 3:48 PM

Here is a drawing of a relay latch circuit. When Sw1 is closed, the relay energizes and holds itself energized through the contacts CT1. When Sw2 is opened, the relay releases.

If my understanding of your circuit is correct, you need two of these latches. One is for the Start and Stop buttons. When you push the Start button (Sw1), the circuit has to stay energized until you push the Stop button (Sw2). This latch powers the rest of the circuit (the second latch, hydraulic solenoid, and limit switches) from the hot side of the relay.

The second latch is for the limit switches. (I am assuming that the limit switches are momentary acting.)

For the sake of argument, I am assuming that an energized solenoid directs the cylinder to the right, and de-energized to the left. In this case, the normally open contacts of the left limit switch would be Sw1. When the cylinder is full left, Sw1 closes momentarily energizing the hydraulic solenoid and the relay (which remains latched), and the cylinder moves to the right.

When the cylinder reaches the right limit switch, Sw2, the normally closed contacts open and break the circuit to the relay and solenoid. The solenoid is now de-energized and the cylinder moves to the left.

I hope this helps.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Controlling 8-Pin Relays With Proximity Switches

08/31/2016 3:58 PM

A latch would typically be needed to keep a coil energized, but why would one be needed to keep a coil deenergized? It seems that one four-pin relay (SPNO) would be enough; or is something wrong with post 2?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#7
In reply to #6

Re: Controlling 8-Pin Relays With Proximity Switches

08/31/2016 4:41 PM

I made a few assumptions:

  • The limit switches are momentary with NO and NC contacts
  • The hydraulic solenoid is energized to direct the cylinder one way and de-energized to direct it in the other direction

The Start - Stop circuit is fairly straightforward. A relay latches to keep it on after the Start button is pushed and released. Pushing the Stop button (normally closed) opens the circuit and releases the relay.

If the limit switches are momentary (my assumption), then a second latch is needed to keep the solenoid energized for cylinder travel in one direction. This circuit is just like the first one, only the limit switches take the place of "Start" and "Stop".

You have two different functions here, and I don't see how one relay can accomplish that.

As I said, this is all based on my understanding of the OP's intended circuit.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#16
In reply to #5

Re: Controlling 8-Pin Relays With Proximity Switches

09/02/2016 7:35 AM

Presuming that de energized is the retracted position,put the retracted limit switch in parallel with the start switch,and the extended limit switch in series with the stop switch.

When the cylinder extends,it will break the latch circuit,causing the cylinder to retract.

When it hits the retract switch, it will re-energize the start/latch circuit.

Use one set of contacts to latch the relay,and the other set to energize the coil in the extended position.

Remember: All start switches in parallel,all stop switches in series.

Sorry,no schematic,but I hope my explanation is sufficient.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#4

Re: Controlling 8-Pin Relays With Proximity Switches

08/31/2016 3:19 PM

Here's how you can get the latch:

The switches are momentary contact.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#8

Re: Controlling 8-Pin Relays With Proximity Switches

08/31/2016 9:04 PM

If you require "no volt protection" then what you want to do can't be achieved with just one relay.

If, however you don't need no volt protection, then replace the on/off push buttons with a simple SPST switch, and it can then be done with one relay.

The attached circuit should assist.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#9
In reply to #8

Re: Controlling 8-Pin Relays With Proximity Switches

08/31/2016 11:31 PM

A slightly revised version of my first circuit that disconnects supply from both sides of solenoid when switch is off.

If the solenoid should require a reversed polarity to the proximity switches, then simply move the On/off switch to the other supply leg as shown below

Register to Reply Score 1 for Good Answer
Participant

Join Date: Aug 2016
Posts: 3
#10

Re: Controlling 8-Pin Relays With Proximity Switches

09/01/2016 10:18 AM

I am overwhelmed by the responses, thank you all. In answer to your questions.... The prox switches are momentary. The hydraulic solenoid requires energizing on both forward and reverse cycles. The momentary starting switch is not a must, but it does need a stop switch.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#13
In reply to #10

Re: Controlling 8-Pin Relays With Proximity Switches

09/01/2016 11:30 AM

There are two coils on the solenoid valve, one for in stroke, one for out stroke

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#15
In reply to #10

Re: Controlling 8-Pin Relays With Proximity Switches

09/01/2016 6:19 PM

Then simply fit a latching emergency stop button in series with the on/off switch in my circuit

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#17
In reply to #10

Re: Controlling 8-Pin Relays With Proximity Switches

09/02/2016 7:44 AM

I suggest that you use a single-coil 4way solenoid valve,similar to an ASCO:

http://www.asco.com/en-us/Pages/solenoid-valves.aspx

This will simplify wiring,reduce energy consumption and improve reliability,and give fail-safe operation in the retracted position in case of a power failure.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#11

Re: Controlling 8-Pin Relays With Proximity Switches

09/01/2016 10:44 AM

I would do this with an arduino and a couple of Opto22 solid-state relays. I did this with a waste water tank transfer setup that was started by one switch and turned off by another.

__________________
Most people are mostly good most of the time.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#14

Re: Controlling 8-Pin Relays With Proximity Switches

09/01/2016 12:35 PM

As long as we are not building a polar bear trap.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Auminer (2); Deefburger (1); Doorman (1); HiTekRedNek (2); James Stewart (1); Mikerho (1); Rixter (3); rwilliams (1); spades (3); Tornado (1); WJMFIRE (1)

Previous in Forum: Differential & Restricted Earth Fault Protection Of Transformer   Next in Forum: Testing Tranformer Oil Rated for 50Hz Power Trafo at 60Hz Test Voltage

Advertisement