Selection of HRC fuse & MCB rating

09/07/2016 1:05 AM

Hi!

Though the subject is related to very fundamental of electrical engg. still I want to raise it as many has a wrong idea on selection of proper rating of Fuse vs MCB.

It is also true that every time it may not be possible to check time current characteristic curve to select Fuse or MCB.

Suppose the total load current is 10A DC in a 110v dc circuit, can u please suggest what should be the rating of HRC fuse & MCB rating separately.

Is there any thumb rule for selection?

Note: For MCB you can consider resistive plus inductive load "c" curve.

__________________
Enjoy the question till you get the answer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Selection of HRC fuse & MCB rating

09/07/2016 1:17 AM

The fuse and/or mcb is sized to protect the wire, the wire is sized to handle the load...

https://www.bluesea.com/resources/1437

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Aug 2016
Posts: 32
#2
In reply to #1

Re: Selection of HRC fuse & MCB rating

09/07/2016 1:40 AM

Thanks.

In a particular circuit if we use 2.5 sq.mm PVC CU cable whose current capacity rating is more than 25A , then what should be

rating of FUSE or MCB ?

__________________
Enjoy the question till you get the answer
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#3
In reply to #2

Re: Selection of HRC fuse & MCB rating

09/07/2016 2:21 AM

From the above link I read that there might still be a difference for the fuse size dependent on the length of the circuit.

But then your wire seems to have a higher load carrying capacity. I would still go with he above scheme to be on the safe side.

__________________
Common Sense Dictates
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#13
In reply to #2

Re: Selection of HRC fuse & MCB rating

09/07/2016 3:51 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4

Re: Selection of HRC fuse & MCB rating

09/07/2016 3:16 AM

What's the matter? Don't you subscribe to your local national electrical code, or something?

__________________
Good moaning!
Register to Reply Score 1 for Off Topic
Associate

Join Date: Aug 2016
Posts: 32
#5
In reply to #4

Re: Selection of HRC fuse & MCB rating

09/07/2016 3:48 AM

Hi!

No I am not getting suitable answer from local.

Kindly help me in getting the rating of fuse & MCB rating.

Please refer the chain message.

Regards

__________________
Enjoy the question till you get the answer
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#6
In reply to #5

Re: Selection of HRC fuse & MCB rating

09/07/2016 3:55 AM

Then use somebody else's, then. If you adopt UK standards, then you could apply BS7671, for instance, and you wouldn't need to post here. Some people are trying to get some sleep, you know?

__________________
Good moaning!
Register to Reply Score 1 for Off Topic
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #5

Re: Selection of HRC fuse & MCB rating

09/07/2016 12:32 PM

The MCB is there to prevent average current over a threshold value from over-heating motors and similar load devices. If heaters, then the load may not be induction much at all, and also consider DC voltage source to eliminate the effect of inductive load, unless the DC is chopped back to AC down path.

A fuse is for overall circuit protection from surge (short-circuit, or major ground fault) current. The fuse burns out so the wires and motor does not. Typically the breaker may trip before the fuse blows, but if MCB is "sticky" and failing, then fuse is last line of defense. I think you will want probably something more than a 10 A fuse if the circuit is designed for 10 A nominal DC current. 15 A or 20 A if no 15 A can be had.

The MCB should be at least 150% of circuit, so it does not trip all the time, then fail, having been worn out.

The above is only suggestions, and you should not follow this rule of thumb, unless local codes and laws permit such a consideration within your country's standards.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#11
In reply to #10

Re: Selection of HRC fuse & MCB rating

09/07/2016 12:47 PM

If you're saying a 10 amp fuse blows at 10 amp, that's not right. It blows at about 20 amp. See #8.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#12
In reply to #11

Re: Selection of HRC fuse & MCB rating

09/07/2016 1:45 PM

You are right, after further review, the call on the field is overturned, 1st and 10 for Codemaster, it was indeed a fumble.

Having said that, I am probably wrong about the breaker too.

The only thing left in my defense, I did make a disclaimer at the bottom of my post, referring the enquirer back to the local codes. Hell, put a five or six amp fuse in there, and see if it holds, then move up to the ten amp one later. As far as the breaker, I agree the enquirer needs specific information about draw of his circuit to compare against the time characteristic of the breaker.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#14
In reply to #12

Re: Selection of HRC fuse & MCB rating

09/07/2016 4:35 PM

Re MCBs, found this on wiki if it's any interest.

International Standards, IEC 60898-1 and European Standard EN 60898-1, define the rated current In of a circuit breaker for low voltage distribution applications as the maximum current that the breaker is designed to carry continuously (at an ambient air tempe

International Standards, IEC 60898-1 and European Standard EN 60898-1, define the rated current In of a circuit breaker for low voltage distribution applications as the maximum current that the breaker is designed to carry continuously (at an ambient air temperature of 30 °C). The commonly available preferred values for the rated current are 6 A, 10 A, 13 A, 16 A, 20 A, 25 A, 32 A, 40 A, 50 A, 63 A, 80 A, 100 A,[5] and 125 A (similar to the R10 Renard series, but using 6, 13, and 32 instead of 6.3, 12.5, and 31.5 – it includes the 13 A current limit of British BS 1363 sockets). The circuit breaker is labeled with the rated current in amperes, but excluding the unit symbol, A. Instead, the ampere figure is preceded by a letter, B, C, or D, which indicates the instantaneous tripping current — that is, the minimum value of current that causes the circuit breaker to trip without intentional time delay (i.e., in less than 100 ms), expressed in terms of In:

TypeInstantaneous tripping current
BAbove 3

In

CAbove 5

In up to and including 10 In

DAbove 10

In up to and including 20 In

KAbove 8

In up to and including 12 In

For the protection of loads that cause frequent short duration (approximately 400 ms to 2 s) current peaks in normal operation.

ZAbove 2

In up to and including 3 In for periods in the order of tens of seconds.

For the protection of loads such as semiconductor devices or measuring circuits using current transformers.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #10

Re: Selection of HRC fuse & MCB rating

09/08/2016 3:34 AM

<...prevent average current over a threshold value from over-heating motors and similar load devices...>

Ahem, er, actually that's the job of the motor overload unit. The MCB or fuse is there to protect the circuit conductors. BS7671 gives full protocols for coordination of protection.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#7

Re: Selection of HRC fuse & MCB rating

09/07/2016 4:26 AM

I have about 40 years work experience in this field. One common mistake done by most people is not considering "Temperature De-rating". I used to ask my US or Europe equipment supplier to consider this point as in India ambient temperature goes up 50'C outside and inside some panels up to 70'C.

__________________
Subramanyam
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#8

Re: Selection of HRC fuse & MCB rating

09/07/2016 5:00 AM

The obvious answer for a fuse is a rating of 10 amp. Fuses are designed to blow at 2x rating, ie 100% overload. But why an HRC fuse? My understanding is these are used when the load is a motor, to handle the high starting current but still protect when running. What is the load?

On MCBs I have curves somewhere showing trip time vs current. You can find them on the web, if I remember right you can select an MCB from these.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Selection of HRC fuse & MCB rating

09/07/2016 5:20 AM

Full protocols for breaker and fuse selection for circuit protection may be found within the pages of British Standard 7671. <sigh>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#15

Re: Selection of HRC fuse & MCB rating

09/07/2016 10:00 PM

Homework?

Register to Reply
Associate

Join Date: Aug 2016
Posts: 32
#17
In reply to #15

Re: Selection of HRC fuse & MCB rating

09/08/2016 4:23 AM

Hi!

From the discussion it is evident that for a 10A DC resistive load fuse rating could be 15A to 20A.

For MCB rating it can be 10A ( for curve C) as it will operate at the zone of 10 times of current during short ckt.& otherwise due to over load it will also trip but more time is required for that .

Your suggestion please.

__________________
Enjoy the question till you get the answer
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#18
In reply to #17

Re: Selection of HRC fuse & MCB rating

09/08/2016 6:32 AM

You haven't got it, have you? You use a fuse or a breaker to protect the wiring. The load looks after itself, though a separate overload device to protect a motor is a very good idea.

Now, what you are trying to do is reinvent the wheel. All you've got to do is follow your local electrical code and you're fine. Don't follow it, and you're on your own.

If you're on your own then you can't expect any backup from your fire insurance company or your professional indemnity insurance company. Remember, as an Engineer, your job is to retire without having killed or maimed anyone during your career. As you seem unaware of this, and unwilling to learn it, this is my stop, and I'm getting off. Cheerio.

__________________
Good moaning!
Register to Reply
Associate

Join Date: Aug 2016
Posts: 32
#19
In reply to #18

Re: Selection of HRC fuse & MCB rating

09/08/2016 7:00 AM

Hi!

There is no local no global!

Only knowledge & process speak. If you see in earlier days all electrical equipment were too large for its over design which in todays scenario it is much smaller & compact.

In earlier days the weight & size of ceiling fan is not same as that of todays'!

How it has happened?

It is due to quality value engineering & it is accepted by all customer.

Hence, minimum cost & maximum efficiency should be the major criteria while designing anything.

It is not reinvention or related to any insurance company.

It is just a revisit on selection criteria.

Hope you agree with this logic.

Cheers!!

__________________
Enjoy the question till you get the answer
Register to Reply Score 1 for Off Topic
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#21
In reply to #19

Re: Selection of HRC fuse & MCB rating

09/08/2016 10:28 AM

Better magnets?

Probably in India you should use smaller fuse value due to the heat. It is getting hot in here just talking about it. God bless you for living there, you deserve it!

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#20
In reply to #17

Re: Selection of HRC fuse & MCB rating

09/08/2016 8:35 AM

Where do you get fuse rated 15 or 20A from? Have you read my #8? 15 or 20A fuse would run the load OK, but so would replacing the fuse with a length of copper wire!

I'm no expert, and don't know offhand how the appropriate type of MCB - B,C,D etc is selected. I would tell the supplier the maximum current and type of load, and let him recommend something.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#22
In reply to #20

Re: Selection of HRC fuse & MCB rating

09/08/2016 10:28 AM

LOL!

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 22 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Codemaster (4); Crabtree (3); IdeaSmith (1); James Stewart (4); kvsubramanyam (1); lyn (1); PWSlack (2); Shibnath Mukherjee (4); SolarEagle (2)

Previous in Forum: Current Reading is Uniform in All the Phases   Next in Forum: Effects Of Overloading On Generators

Advertisement