Bus Tie Duct Voltage drop

09/10/2016 8:30 AM

Dear Sir,

We have installed bus tie duct 5000Amp, Length 55 meter, Bus bar size 120x10x4 each phase, 120x10x2mm sharp edge for neutrl, (Bus tie duct box size (W900mmx H 300MM) there is 30volts drop at yellow phase when load reach 2500A, noted readings are as, red to neutral 240V Blue to neutral volts 240 but same time yellow to neutral volts 210V, due to this drop we are facing tripping problem with our plant, can you explain how can we control this drop.

Regards,

AI

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Bus Tie Duct Voltage drop

09/10/2016 9:29 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Bus Tie Duct Voltage drop

09/10/2016 11:42 AM

Yep. Take 2/3 of the single phase loads off the yellow phase, split them, and put half each onto the red and onto the blue phases.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Aug 2016
Posts: 14
#8
In reply to #2

Re: Bus Tie Duct Voltage drop

09/12/2016 3:10 AM

Sir we have all load three phase, load already balance.

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Bus Tie Duct Voltage drop

09/10/2016 4:37 PM

Better yet, get yourself a non-contact thermometer and scan for hotspots. More than likely one of the bolted connections isn't tight enough and has a slightly higher resistance than the others. Over time this will lead to discoloration then thermal runaway, more frequent trips, and ultimately a much more expensive repair.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #3

Re: Bus Tie Duct Voltage drop

09/10/2016 11:14 PM

Good point...I would have thought this would be checked already....but if he hasn't, definitely would be the most likely cause and first thing to check, a loose connection....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#5
In reply to #4

Re: Bus Tie Duct Voltage drop

09/11/2016 12:09 AM

Absolutely! Here's a similar photo. These were 3 very nearly equally loaded phases, 2 cables per phase (the bottom 3 of 5 visible cable pairs). Just out of the photo to the right are three 600 Amp fuses. It doesn't take a whole lot of expertise to see that there is a problem with the top phase. I had previously tightened the connections, so it was down to either the fuse or the fuse holder. It turned out to be a defective ageing fuse.

Somewhat confusing the image is the fact that there were Rogowski coils measuring the currents at the time the photo was taken.

It used to be that the IR cameras were several thousand dollars and up. This image was taken with a "FLIR One™" camera attachment on my iPhone. It cost $250, and has paid for itself MANY time over! A similar attachment is available for Android phones, so there is no longer the excuse that "We can't afford one". Anyone who can't afford a $250 camera, shouldn't be anywhere near 5000A busbars!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #5

Re: Bus Tie Duct Voltage drop

09/11/2016 2:40 PM

Flir... A great tool...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Aug 2016
Posts: 14
#9
In reply to #4

Re: Bus Tie Duct Voltage drop

09/12/2016 3:15 AM

Connection checked 2 time within month , there is no any loosing with any joint plate. we have three transformers each 3000KVA, have same size BTD with 45m, 50m, 55meter, each BTD have voltage drop at yellow phase , distance between each phase bus bar 100mm.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#14
In reply to #9

Re: Bus Tie Duct Voltage drop

09/12/2016 10:58 AM

If three different transformers all have the same problem, especially with different lengths of busbars, then the cause is not in the busbars or transformers, but in the supply that feeds those transformers.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Active Contributor

Join Date: Aug 2016
Posts: 14
#18
In reply to #14

Re: Bus Tie Duct Voltage drop

09/17/2016 2:41 AM

WE check wit detail when load is 3000Amp , same time we check voltage at 1st end transformer side LV bushing, same time we check at 2nd end of BTD where connected with Main LT Panel, drop is between 1st end to 2nd end, at transformer lv bushing voltage are equal on red, yellow and blue but at 2nd end yellow have 20-25voltage drop.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#19
In reply to #18

Re: Bus Tie Duct Voltage drop

09/17/2016 1:10 PM

If this is true on all three transformers, then there must be a design problem.

You say"Bus bar design II II II II II II II 1st two neutral 2nd 4 red 3rd four yellow 4th 4 blue"

Since the yellow bus bars are in between the red and blue ones, It's hard to imagine a magnetic problem, unless perhaps the louvers cut in the ducting were oriented such that a continuous strip of steel follows the yellow, while the louvers make the steel discontinuous near the red and blue bars.

Thermally, heat from both the red and blue bars will contribute to the heat in the yellow bars, while the red and vlue bars only have an additional heat source on one side, so it would be expected for the yellow bars to be a little warmer. Of course warmer bars have a higher resistance, so more voltage drop would be expected.

Again, an infrared camera image would show all this instantly. When (not if - this is imperative) you get some IR images, look not only at the temperatures of the bus bars, but also at the temperatures of the ducting. Hot ducting indicates magnetic losses.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Active Contributor

Join Date: Aug 2016
Posts: 14
#20
In reply to #19

Re: Bus Tie Duct Voltage drop

09/19/2016 1:52 AM

temperature is not issue.

as we energize the BTD within 30s load reach at 3000A within 30s temperature cannot rise , as ampere start increasing from 1000A than voltage drop start at yellow phase.

i think when load increase red and blue busbar flux link with yellow, that is why yellow resistance increase and drop is happen.

its only my observation.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#21
In reply to #20

Re: Bus Tie Duct Voltage drop

09/19/2016 4:38 AM

In that case, then you may need to add some crossovers, as is done in transmission lines, to simulate the twisting of standard cables. 45-55 m are long distances for parallel conductors. Whoever installed the busbars should have known about that...

Obviously I know nothing of your plant layout, but I get the impression that each transformer feeds a single large load. The best solution would probably be moving the transformers nearer to the loads, to get rid of most of the busbar lengths.

In fact probably the first question that should have been asked is: Is this a problem that was found when first commissioning a new facility, one that appeared when a new installation was added to an existing plant, or one that appeared in a system that previously had no problem?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#22
In reply to #20

Re: Bus Tie Duct Voltage drop

04/19/2017 7:51 AM

If you can not locate a temperature increase within your 30 second window, operate the system for a longer length of time until you can observe a temperature rise. You will ,perform this procedure only to locate the higher impedance connection(s). Disassemble the faulty connections, clean and inspect. We often use a product called Cool-Amp (an electroless silver plating technology)to insure low impedance connections.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#23
In reply to #22

Re: Bus Tie Duct Voltage drop

04/19/2017 9:40 AM

Thanks for bringing Cool-Amp to our attention! Do you have any experience using it (and/or Conducto-lube) on old (30-50 years) high current devices? My specific current point of interest is on the blades of 600 Amp fuses and the fuse-holder contacts that mate with them.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#24
In reply to #23

Re: Bus Tie Duct Voltage drop

04/19/2017 12:44 PM

I prefer to use silver plating, but it is usually an electrolytic process that must be done in tanks. However the Cool-Amp process is done with a wet cloth and does a respectable job. It can also be used to refinish silver instrument dials. We have bus bars in our resistance welding machines that have been in place for more than 20 years with less than 1 micro-ohm of measured resistance variation. To get this kind of stability we sometimes use washers between our bus conductors stamped from 100 mesh woven silver wire. These washers deform and are crushed during bolting of the bus assembly. This forms a hermetic connection that is water resistant and gas-tight.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#25
In reply to #24

Re: Bus Tie Duct Voltage drop

04/19/2017 4:28 PM

Thanks again. It sound like it's worth trying.

We also do a lot of resistance welding, but mostly welding thin foils to each other or to a thicker substrate.

What kind of instrument do you use to measure µΩ?

That mesh washer sounds like a great idea for appropriate applications.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#26
In reply to #25

Re: Bus Tie Duct Voltage drop

04/19/2017 9:33 PM

A μΩmeter of course!

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#28
In reply to #26

Re: Bus Tie Duct Voltage drop

04/25/2017 12:06 PM

Thanks for the link! Very informative, although it was disappointing to note a glaring error on page 3:

They say:“6000 A across a 100 μΩ bus = 3600 Watts.
6000 A across a 1 μΩ bus = 36,000 Watts, which will result in excessive heating.

But: P=I2*R = 60002 * 100µΩ = 36,000,000 A2* 0.000,100 Ω = 3,600 W (correct)

While: P=I2*R = 60002 * 1µΩ = 36,000,000 A2* 0.000,001 Ω = 36 W

(They moved the decimal point the wrong direction!)

Sorry I didn't see your reply 'till today 4/25.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#27
In reply to #25

Re: Bus Tie Duct Voltage drop

04/25/2017 10:32 AM

We use an instrument manufactured by RoMan called an IM-91 Impedance Master. It is obsolete, but ideal for these measurements. We maintain a collection of NIST certified instrument shunts to verify calibration.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#29
In reply to #27

Re: Bus Tie Duct Voltage drop

04/25/2017 12:29 PM

Thanks. I saw one on eBay for around $400... What is the chance that it is usefully accurate? I don't need precision; I can compare connections in various locations, and watch for high values that need cleaning/tightening/replacement.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#30
In reply to #29

Re: Bus Tie Duct Voltage drop

04/25/2017 1:39 PM

I can't advise on the condition of a used one, but I do have a copy of the user manual that I'd be happy to send you.

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#7

Re: Bus Tie Duct Voltage drop

09/11/2016 10:04 PM

It is important that we know the bus bar material. Copper, aluminum, or something else?

Register to Reply
Active Contributor

Join Date: Aug 2016
Posts: 14
#10
In reply to #7

Re: Bus Tie Duct Voltage drop

09/12/2016 3:17 AM

Copper

Register to Reply
Active Contributor

Join Date: Aug 2016
Posts: 14
#11

Re: Bus Tie Duct Voltage drop

09/12/2016 3:23 AM

yet not received any suggestion which can resolve my problem.

Register to Reply
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#12

Re: Bus Tie Duct Voltage drop

09/12/2016 6:42 AM

So assuming the currents are equal and all joints are equal (and good), one thing left to consider is the busduct design itself. I have seen examples where the centre phase (L2, yellow) runs hotter than the outer phases, partly down to restrictions of ventilation for air spaced bars, or poor design and therefore increased impedance (volt drop). Have you considered a phase crossover along the run? What is the maximum length of run suggested by the busduct manufacturer?

__________________
rogerggbr
Register to Reply
Active Contributor

Join Date: Aug 2016
Posts: 14
#13
In reply to #12

Re: Bus Tie Duct Voltage drop

09/12/2016 10:07 AM

Ventilation system is natural. only installed louvers for ventilation.

Bus bar design II II II II II II II 1st two neutral 2nd 4 red 3rd four yellow 4th 4 blue

Distance between phase to phase 100mm and phase to ground 90mm phase to neutral 90mm , bus bar insulation supporting sheet at 800mm.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#15
In reply to #13

Re: Bus Tie Duct Voltage drop

09/12/2016 2:08 PM

Perhaps yellow phase is facing a back emf due to greater proximity to steel somewhere along its length, I don't know. Just a thought.

You should be seeing signs of that metal heating up inductively though.

Make sure your phases are indeed equal at point of entry to this plant location.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
2
Participant

Join Date: Jun 2012
Location: Australia
Posts: 4
Good Answers: 1
#16

Re: Bus Tie Duct Voltage drop

09/12/2016 10:01 PM

ok, you need to simply measure voltage at all points, start at the supply. See where the (yellow phase) voltage is at 240V. If at the first point you find unbalanced voltage, then you go backwards further towards supply source until drop is found. If you find balanced voltage at your starting point, then you go forward until you find voltage difference. Your reference will be neutral, as neutral doesnt seem the issue - because you have correct/good/balanced readings on other phases to neutral.

When you find your voltage drop point, then critically you will be testing for voltage on EACH AND EVERY conductor/connection at that point to specifically see where the issue is - ie; if it is a lugged cable connection bolted to busbar, you will check voltage on busbar, voltage on the bolt, voltage on lug surface and voltage on the (copper?) cable by poking multimeter lead into/onto the cable at the lug (if lug has 'open' front for viewing cable insertion depth, measure there. If not measure cable voltage at the insertion point of cable into lug where there will be some slightly exposed copper where cable has been stripped back). If any protective insulation is covering lug, then need to poke a small hole into access the cable. Alternately and similarly, when you find the voltage drop area, you can measure voltage difference across the connection area - you will see where the voltage difference is if you go to 1st conductor point and last conductor point and see 30V difference, then test at each point described above. Obviously, near 0VAC difference is good connection, and any voltage difference across connections is the faulty connection. It could be you find the difference from cable into lug TO lug - so that means poor/faulty crimping of the lug. Or between bus bar and lug = face of lug or face of busbar is poor/dirty/oxidised, or from busbar to busbar connection = face of either/both busbar is poor/dirty/oxidised,

If measuring voltage is too dangerous, then what should have happened when duct 1st installed was 'ductor' testing of all connections to test for this very issue before switching system on. Ductor testing is dead commissioning testing with rated current at very low safe voltage, prior to turn on to find problem connections. It is certainly possible to have slightly bad connections showing as little difference in temperature from thermal camera, or not realising that every single connection is a possible source of VD, and you have not pointed thermal camera at every joint.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Aug 2016
Posts: 14
#17
In reply to #16

Re: Bus Tie Duct Voltage drop

09/17/2016 2:33 AM

Sir Thanks for your answer.

can you explain how much distance required between phase to phase bus bar?

bau bar size 120x10mm, 4 bus bar for each phase.

please explain with calculation

Thanks

Register to Reply
Register to Reply 30 comments