VT Primary Earthing in Ungrounded Systems

09/10/2016 11:31 AM

Why is star connected earthed (3 separate single phase VT's) Voltage transformer not considered as a source of earth in ungrounded systems?

Instead the secondaries are connected in broken delta to detect the earth faults. If the VT's are star connected and earthed the fault current should flow through VT Primary winding to earth and the line CT's should detect the current.

What am I missing?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: VT Primary Earthing in Ungrounded Systems

09/10/2016 11:47 AM

A few more years of schooling...?

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #1

Re: VT Primary Earthing in Ungrounded Systems

09/10/2016 11:57 AM

Ahem. That's a little unfair. One never stops learning in this world, particularly on CR4.

"The only stupid question is the one that no-one asks." - Anon

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: VT Primary Earthing in Ungrounded Systems

09/10/2016 11:52 AM

A1) Because ungrounded systems have no earth reference at the source of supply. Therefore there can be no significant earth fault current with such an arrangement.

What the VTs are doing is monitoring the phase voltage with respect to earth; if one of the phases drops with respect to earth then it can be inferred that there is less-than-perfect insulation between the phase and general earth potential. That constitutes a fault that needs to be eliminated, however it can be tolerated for a while, and that is why such arrangements are used were a loss of power could be extremely hazardous; hospitals sometimes use ungrounded systems, for example - one wouldn't want equipment that is sustaining life to go off when a pesky earth fault appears somewhere else on the distribution network!

See the Wikipedia page entitled Earthing Systems for a better understanding.

A2) Nothing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: VT Primary Earthing in Ungrounded Systems

09/10/2016 11:00 PM

Because a VT (Voltage Transformer) is a high impedance device, rendering it useless a grounding device which must be able to handle the available short circuit current without failing.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#5
In reply to #4

Re: VT Primary Earthing in Ungrounded Systems

09/10/2016 11:36 PM

Take a look at zig-zag grounding transformers, which are designed to provide a source of ground fault current for an ungrounded system.

I have never seen them applied on an effectively ungrounded system, such as a Y sourced system at a great distance. There is much information on the pitfalls of operating power systems with no ground reference, a common practice in the 1950s & 1960s.

http://ecmweb.com/content/basics-zigzag-transformers

https://electricalnotes.wordpress.com/2012/05/04/zig-zag-connection-of-transformer/

http://apps.geindustrial.com/publibrary/checkout/Zig-Zag-Trans?TNR=White%20Papers|Zig-Zag-Trans|generic

Reply
Anonymous Poster #1
#6

Re: VT Primary Earthing in Ungrounded Systems

12/06/2016 5:31 AM

There is a small fault current in ungrounded systems. Does this small current flow through the primary windings of the potential transformer?

1. What effect does this small current have on PT Primary winding if it flows?

2. How this small current affect the secondary voltage?

Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#7
In reply to #6

Re: VT Primary Earthing in Ungrounded Systems

12/06/2016 8:30 AM

The small current is not considered fault current, except what is allowed by the PT winding if grounded, it is normally charging current for the distributed capacitance of each of the 3 phases to ground or earth potential.

1. If you have wye connected PTs also grounded, then one primary winding will show zero voltage

2. The secondary will transform the primary voltage.

The link below shows simplified operation of wye grounded PTs

http://www.electrotechnik.net/2009/03/using-broken-delta-protection-for-earth.html

Also below is more detail for your questions

http://www.i-gard.com/Downloads/techlib/Application%20Guides/C-400EA%20Application%20Guide.pdf

Reply
Anonymous Poster #1
#8
In reply to #7

Re: VT Primary Earthing in Ungrounded Systems

12/06/2016 10:05 AM

The charging current of the faulted phase goes to zero. The vector sum of the charging currents in the unfaulted phases is 3 times the normal values and flows through the ground.

Will this current flow to ground through the neutral of the primary winding of VT, if the primary neutral is grounded?

Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#9
In reply to #8

Re: VT Primary Earthing in Ungrounded Systems

12/06/2016 2:28 PM

1. Read bottom of Page 2 in second reference given above.

2. You answered that in your first statement.

Not sure what you are driving at...

Reply