Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/10/2016 11:11 AM

I have a squirrel cage blower that speeds up a lot (about 3 times faster) and increases the airflow a lot when the outflow or inflow is partially blocked. It speeds up progressively as the inlet or outlet is blocked to about half and then maintains that speed as it is blocked further. There is no sail sensor. The motor is a GE single phase, capacitor start, 1/3 hp model number 5KCP39JG9479ET. I have 110v connected to yellow and black wires. There are also red and blue wires that came with heat shrink tubing on the ends. There is also a yellow wire quick connected to a blue wire and a brown wire quick connected to an orange wire. i have never seen anything like this. Has anyone else seen something like this?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
8
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 11:19 AM

Of course it does. The power used by any fluid mover is the double-partial-integral of the change in pressure and the change in volumetric flowrate; in the simplified analogy of a pump working with incompressible liquids it is the pressure rise between outlet and inlet, multiplied by the volumetric flowrate, as simple quantities.

If the airflow is blocked, the flowrate tends to zero, and therefore so does the power requirement. No wonder the motor speeds up - although electrical power is applied to it, it hasn't got any work to do!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 8)
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9921
Good Answers: 1142
#17
In reply to #1

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 9:39 PM

Exactly! I noticed as a kid that the vacuum cleaner increased in pitch when the hose was plugged. I thought at the time that the motor was working harder. Only later did I realize that if it were working harder it would slow down, not speed up. Good answer!

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#19
In reply to #1

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 11:53 PM

"The power used by any fluid mover is the double-partial-integral of the change in pressure and the change in volumetric flowrate; in the simplified analogy of a pump working with incompressible liquids it is the pressure rise between outlet and inlet, multiplied by the volumetric flowrate, as simple quantities."

Almost - but not quite. Your statement suggests that if flow rate is zero, then any power consumed is the pressure rise multiplied by zero, which will equal zero, and while that is correct for fans and centrifugal fluid movers, try closing the discharge of a positive displacement pump and you will get an entirely different result.

Flow rate will be zero - but pressure and load will increase exponentially until either the overload pops, the shaft breaks, or the housing ruptures - the pump will definitely not increase in speed until something breaks.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9921
Good Answers: 1142
#28
In reply to #19

Re: squirrel cage blower speeds up when airflow is blocked

09/11/2016 3:59 PM

I would assume "blower" implies gas, not liquid, and in any case a centrifugal pump is not positive displacement (like a piston pump), so I would expect the motor would speed up like my vacuum cleaner (without breaking anything ).

What is really happening is that the impeller moves around gas that is already moving rather than having to accelerate slow moving gas from the inlet, thus doing less work.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#31
In reply to #19

Re: squirrel cage blower speeds up when airflow is blocked

09/12/2016 6:16 AM

If you rupture your piping downstream of your positive displacement pump, then your pressure differential drops to zero at all flow rates. So no work is done. Your ball, because now you've got to mend it and prevent recurrence.

__________________
Good moaning!
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#33
In reply to #19

Re: squirrel cage blower speeds up when airflow is blocked

09/12/2016 1:55 PM

In the fan/blower at no flow, that just means there is no flow at the outlet. It does not mean that there is no bypass air flow, so there still is work being done on the air, and released, so the air might should heat up (slowly, depends on heat dissipation rate compared to actual power expended).

I agree with your statement about positive displacement pumps. Amazing how all that work can show up as black smoke.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#2

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 11:22 AM

Blocking the inlet or outlet of a centrifugal blower/pump will allow the speed to increase as the work being done by the impeller/fan is reduced.

I doubt that the air flow (Volume) is increased when partially restricted. Velocity, maybe if the outlet is blocked. Blocking the inlet will produce less flow but won't increase the outlet velocity.

Register to Reply
Anonymous Poster #1
#3

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 11:23 AM

pull a boat motor our of water while its running.......you'e removed the Load....drop it back in the water and the motor RPM drops, same thing, Slack explained it

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #3

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 12:17 PM

Looking for a Good Analogy button.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#10
In reply to #3

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 3:26 PM

Sorry, but no cigar.

In the case of the boat, you are removing the pump from the fluid. (changing the density of the fluid from that of water to only air)

That is NOT the same as restricting the flow of the fluid through the volute of the pump.

Do not pass Go. Do not collect $200.00.

Register to Reply
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#24
In reply to #10

Re: squirrel cage blower speeds up when airflow is blocked

09/11/2016 6:53 AM

....and now you have an overheated motor since you removed the source of it's cooling as well!

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 11:31 AM

That's a 230v 3-speed motor...You should have 1 leg to yellow and the other to black would be high speed, the blue would be medium and the red low speed...You should have 2 brown wires for the capacitor the other wires are for the rotation direction....

https://www.grainger.com/product/GENERAL-ELECTRIC-1-3-HP-3M816

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#7
In reply to #4

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 11:49 AM

This motor is wired to 110V?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8
In reply to #7

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 11:59 AM

That would be a problem...but I'm hoping he meant 110v to each leg...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Participant

Join Date: Sep 2016
Posts: 2
#13
In reply to #4

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 4:30 PM

Since it is a 230v motor running at 115v, it is running way under powered and when unloaded it then speeds up 3 times faster. When I plugged it into 230v, it only sped up a small amount when I closed off half the port which is what I have seen before. I guess I need to find a 115v motor for the blower. Thanks all!

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#5

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 11:35 AM

A sail sensor on a squirrel cage blower???????????

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #5

Re: squirrel cage blower speeds up when airflow is blocked

09/10/2016 11:42 AM

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/10/2016 3:44 PM

This motor is meant to run with a certain amount of resistance...If you remove it the motor will draw more amps and overheat, the same thing happens if you restrict the air too much....The motor runs at 1100 rpm regardless...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#12
In reply to #11

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/10/2016 3:58 PM

Sorry, no cirag youeither. (Surprise)

The motor is happy running with no load/resistance. It will use much less power and run cooler because it is not doing any work beyond turning the armature.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#14
In reply to #12

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/10/2016 5:32 PM

I have to disagree. this is a blower motor running with the squirrel cage intact....Although it seems logical that as you open it to the free air that the amps would decrease, but that is not the case, they actually increase....I've seen this many times, and it's why you can't get a true amp reading with the air handler open...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#15
In reply to #14

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/10/2016 6:38 PM

What you are saying is logical for any centrifugal blower, pumping any fluid. If it moves more air/fluid, it will draw more current. "This motor is meant to run with a certain amount of resistance" is a foreign concept to me.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#16
In reply to #15

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/10/2016 8:59 PM

Resistance to air flow....Carry a certain load? Do a certain amount of work...Well it doesn't matter anyway he was trying to run it on 110v to begin with....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#29
In reply to #15

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/11/2016 5:10 PM

..."ECM blower motors behave differently because they are programmed to adjust their output according to the resistance they are working against, but that is an entirely new discussion which I will save for another article."...

http://hvacrfundamentals.blogspot.com/2009/08/understanding-centrifugal-fan-motor.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#30
In reply to #29

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/11/2016 5:19 PM

OK, I defer to you.

Register to Reply
Active Contributor

Join Date: Jul 2016
Posts: 22
#22
In reply to #14

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/11/2016 5:46 AM

Rubbish, go back to school and learn basic physics.

Register to Reply Off Topic (Score 3)
Active Contributor

Join Date: Jul 2016
Posts: 22
#20
In reply to #11

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/11/2016 12:47 AM

You obviously don't understand electric motors or centrifugal fans. The higher the volume produced the more power is required. Conversly lowering volume will reduce power required. Reducing volume therefor load will DECREASE power required ie. Amps x volts and motor will run at no load speed. Most motors have little difference between no load and full load speed, definitely not 20% or more. Overload speeds vary but not for long as fusion follows.

Register to Reply Score 2 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#25
In reply to #20

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/11/2016 11:41 AM

A blower that has the air flow blocked will draw less amps initially , that's true, but it will overheat after a while and eventually draw more amps...I don't think fusion is possible here....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#26
In reply to #25

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/11/2016 11:58 AM

The thermal OL will solve the overheating problem, if ever there is one.

Anyway, if this is a squirrel cage blower motor, depending on the design, there is no airflow over or around the motor from the fan because the motor is outside the airbox.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#27
In reply to #26

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/11/2016 12:19 PM

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Jul 2016
Posts: 22
#18

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/10/2016 11:52 PM

Any fan will decrease power required as flow decreases so your motor is probably over loaded at full volume and speeds up to correct speed as load is reduced. I suggest getting hold of a potable tachometer to check motor speeds at different air flows (loads).

Register to Reply Score 1 for Off Topic
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#21

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/11/2016 5:31 AM

That is totally normal.

Nothing new.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#23

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/11/2016 6:13 AM

Back to the basics:

When the flow is blocked,the motor load decreases in a Centrifugal Blower.

Try this:

Put an ammeter on the power to a vacuum cleaner.

Watch the amps drop when you restrict the flow.

No theory required to understand this.Simply accept it.

I don't understand women,but I certainly enjoy them.

Self explanatory.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#32

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/12/2016 1:18 PM

So many side tracks...

The motor is designed for 230V, the OP applied 115V to it. At 1/2 voltage, the motor will only develop 1/4 of it's normal PEAK and STARTING torque, which is used to accelerate it and 1/2 running torque if it does manage to get to full speed. At 1/2 torque and with dampers wide open allowing possible full low, the motor slip will increase drastically. So the load on the motor causes it to slow down and you do NOT get full flow. But because the torque is artificially hampered by the wrong voltage, the current is also kept in check (current follows torque), so it's possible that the motor will NOT overload, at least not immediately. That motor has built-in thermal protection that automatically resets. So I would think that either the load is so low on it that the motor is NOT overloading, or maybe it is, then the motor cools off and resets itself and the OP never noticed.

As the dampers are closed, the flow is restricted so the load on the motor becomes less and the motor is able to accelerate more it with the artificially low torque it is able to produce. It will still not allow full speed from the motor until maybe the dampers are closed all the way and there is no flow at all.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#34

Re: Squirrel Cage Blower Speeds Up When Airflow is Blocked

09/12/2016 2:44 PM

A SC motor cannot go faster than mains frequency (depending on no of poles) so if it speeds up 3 x time, then it suggests it was running at 1/3rd mains frequency to start with - which I find a bit odd?.

But I don't much about blower motor design however - so it might be normal practice - but it struck me as a bit odd.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply Score 1 for Off Topic
Register to Reply 34 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Anonymous Poster (1); Crabtree (1); HiTekRedNek (1); horace40 (1); James Stewart (1); JRaef (1); lyn (8); PWSlack (2); richma (3); Rixter (2); SolarEagle (9); spades (1); thenelson (1); Tom_Consulting (1)

Previous in Forum: Gyroboards Impossible Energy Consumption   Next in Forum: VT Primary Earthing in Ungrounded Systems

Advertisement