Dear Friends

In our Corrugator plant, the temperature rises up to 45C in summer season. We have installed panel ACs with all field panels of machines having PLCs and drives. As per your experience, what should be the set point temperature of ACs to avoid any problem with equipments and ACs byself. Some one tell set below 30C, some one 35C and some one at 40C.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Temperature setting of panel Air Conditioners

10/02/2016 2:03 PM

Your machines should have a maximum operating temperature from the supplier/manufacturer...another concern is humidity, for glues and other humidity sensitive operations, then there is an ideal temperature for workers...which will correlate with the physical activity levels....For workers it can be between 72°-77°F for humidity 35 to 60% rh....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Temperature setting of panel Air Conditioners

10/02/2016 4:00 PM

It depends on what temperatures the wire sizes were selected for. If this is not known, you may need to do some reverse engineering of your panels.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #2

Re: Temperature setting of panel Air Conditioners

10/02/2016 9:27 PM

Whoever voted this as OT is desperately incompetent.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#6
In reply to #4

Re: Temperature setting of panel Air Conditioners

10/02/2016 11:42 PM

Even though it's Lyn, I fixed it.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Temperature setting of panel Air Conditioners

10/03/2016 12:13 AM

Thanks!

The NEC uses 30ºC (86ºF) as a baseline value for many calculations. This ambient temperature is often exceeded, and almost as often is not accounted for. A "Code God" could do well to bump that up to 40ºC (104ºF).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#3

Re: Temperature setting of panel Air Conditioners

10/02/2016 5:04 PM

The thermostat should be set at whatever setting will yield the desired air temperature in the building. Picking an arbitrary setting lacks any resemblance to a common sense approach.

Since operator health and safety are not a consideration, the operating environment for most commercial equipment is 0-70°C.

45°C is well within the operating limit of the equipment, but seems to be an inhuman working condition for employees, depending on indoor humidity levels, and whether or not that matters.

Register to Reply Score 1 for Off Topic
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Temperature Setting of Panel Air Conditioners

10/02/2016 10:35 PM

Most electronics are going to be rated for 40C max, circuit breakers are calibrated for 35C ambient. Circuit breakers will not fail at higher temperatures, but they may nuisance trip. However I would not be comfortable letting anything electronic be exposed to even 40C for any length of time. I generally set enclosure AC units for 30C, that helps avoid having eddies and swirls in air flow inside cause individual components to overheat.

I recently saw some VFDs crammed into an enclosure fail. The AC was set for 70F (21C), but there were areas inside where the temperature still exceeded 110F because of eddies behind barriers. Capacitors over heated and swelled, causing a power supply board failure.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
2
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 232
Good Answers: 16
#9
In reply to #5

Re: Temperature Setting of Panel Air Conditioners

10/03/2016 2:40 AM

I agree, JRaef. I also prefer to keep electronic component's temperatures low to ensure long life. It is clear the the OP is referring to panel aircons as per your answer, not room aircons as others may have thought. And the effect of local ventilation "dead spots" has been brought home to me - expensively, I may add!

Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Temperature Setting of Panel Air Conditioners

10/03/2016 2:15 AM

The addition of an air conditioner to a room full of electronics is no guarantee that there will be adequate cooling for the equipment unless there is some form of thermal analysis to determine how and where to direct air flow around and through the enclosure.

A simple thermostat will only provide the average temperature of the return/supply air without any regard for the actual temperature/heat-load of any particular piece of equipment. It is quite possible overheat a subassembly located in a stagnant air pocket while cooling the supply air to some arbitrary setpoint.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #8

Re: Temperature Setting of Panel Air Conditioners

10/03/2016 6:23 AM

There's a can of worms.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#11

Re: Temperature Setting of Panel Air Conditioners

10/03/2016 12:19 PM

Check the wiring junctions inside every panel and adjust the thermostats until the desired temperatures are reached.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#12

Re: Temperature Setting of Panel Air Conditioners

10/03/2016 12:21 PM

Air conditioning is for comfort control, so the best thing to do is ask the people who are working there.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 3)
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#13
In reply to #12

Re: Temperature Setting of Panel Air Conditioners

10/03/2016 5:46 PM

From the OP: "We have installed panel ACs with all field panels of machines having PLCs and drives."

This isn't for the comfort of people, it's to keep silicon from going "PFFT (that is the sound the magic smoke makes as it escapes)"!

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14
In reply to #13

Re: Temperature Setting of Panel Air Conditioners

10/03/2016 6:30 PM

My way of telling people to think about this, especially for anything electronic, is a simple formula:

Heat2 x Time = Failure.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#15
In reply to #14

Re: Temperature Setting of Panel Air Conditioners

10/03/2016 7:01 PM

Yep. Even if you don't exceed the temperature spec, it will shorten the life.

Besides, most VFDs and PLCs have some type of LCD screen for an operator interface, and the temperature spec on those is usually considerably lower.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#16

Re: Temperature Setting of Panel Air Conditioners

10/05/2016 3:40 PM

Why aren't you talking to the panel manufacturers, then?

__________________
Good moaning!
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#17
In reply to #16

Re: Temperature Setting of Panel Air Conditioners

10/08/2016 11:09 PM

As we have recently installed new BOBST Martin flexo graphic printing machine on which the set point temperature of all cabinet ACs is 40C, I have talked with OEM and according to them, temperature must not set below 40C because the electronic items can be work up to 55C. This is strange for me because there are Lenze servo drives, Siemens PLC field I/O cards and other electronic items are in the panels and according to the discussion made in this thread, cabinet temperature should be maintain within 30C.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#18
In reply to #17

Re: Temperature Setting of Panel Air Conditioners

10/10/2016 6:27 PM

Printing....

I seem to remember about Benjamin Franklin thinking printing was a good job because they had to heat the works in winter else the ink would not flow. Which is to say that printing gear may like a high temperature.

But why cook the electronics because another part of the system has high temperature requirements? I endorse the replies pointing out that electronics failure rate is increased at 40'C vs 30'C -double the failure rate is a "rule of thumb".

It may be that the A/C cuts in/out alternately letting the equipment heat up with natural circulation, then blasting it with fan driven cold air.

Temperature cycling is worse for equipment than a steady or slowly changing high temperature - maybe the supplier has found it is best only to use the A/C when it gets really hot.

This suggests to me a sub-optimum A/C system - would it not be better to have variable speed compressor and fans to achieve a stable equipment temperature rather than a bang-bang control?

I would quiz the OEM closely on why he recommends such a high setting.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#19
In reply to #18

Re: Temperature Setting of Panel Air Conditioners

10/15/2016 10:23 PM

At BOBST machine, we have all RETAL brand ACs with 40C set point temperature pre-set by OEM.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#20
In reply to #19

Re: Temperature Setting of Panel Air Conditioners

10/16/2016 2:32 PM

That's RITTAL!

I would suppose the 40'C is the delivery temperature into the enclosure (at bottom) from these "front panel" coolers. The temperature of the highest mounted electronics in the cabinet may be well over 40'C.

As has been mentioned, just blowing air around may actually create a "dead spot" which gets little inflow of cooling air to some equipment - may be worse than natural convection.

RITTAL have fan thermostats - electromechanical on/off control like a room thermostat and optional temperature dependent variable speed fan control. What do you have??

Cooling units have a capacity that depends on temperature differential, say you have Δt = 45 - 40 = 5'C that requires smaller capacity than Δt = 45 - 30 = 15'C.

But equipment is even more sensitive to humidity, usually 90% max, the term non-condensing is probably in specs of equipment inside your panel. If you cool 45'C, 80% relative humidity [R.H.] air to 40'C you have 100% R.H. and condensation! (I took a New Delhi climate as example). It may be this which dictates the high 40'C setting.

If your panels are well sealed, entry of external air should be slow. A good A/C unit has part of the cold matrix well below mean exit temperature - this will condense out the humidity in a closed volume and drain it out so the internal humidity at 40'C is reduced. From 100% RH to 80% RH at 40'C requires removing about 10g water per kg of air - that requires the air to be cooled to 35'C to condense it.

So if you wish to check the ambient of a vital equipment within the enclosure, you need to check its temperature (preferably on a critical heatsink or component) as well as local humidity where cold air goes from A/C into the panel.

I hope this helps.

67model

Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); Crabtree (1); gideon (1); JRaef (2); Kilowatt0 (2); lyn (2); PWSlack (1); RAMConsult (1); Signode (2); SolarEagle (1); tcmtech (1); Tornado (4)

Previous in Forum: Grid Islanding, Load Shading & Load Shedding   Next in Forum: In Search of Updated Electronic-Electrical Portable Workshop Tool(s).

Advertisement