Anonymous Poster #1

Ground Fault Protection in Corner Grounded Delta System

11/26/2016 5:31 AM

Suppose if "B" Phase winding of three phase motor is short circuited to earth, which is supplied by corner grounded delta transformer in which the "B" phase is grounded. How to identify the short circuit?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Ground fault protection in corner grounded delta system

11/26/2016 11:32 AM

An ordinary 3P RCD or GFCI will detect a fault and trip.

__________________
The reports of my death are greatly exaggerated.
Reply Good Answer (Score 2)
Anonymous Poster #1
#2

Re: Ground fault protection in corner grounded delta system

11/26/2016 12:56 PM

Hi Solar Eagle & Tonys,

I understand should a fault on "A" or "C" phases occur, the fault current flows through corner ground of the "B" Phase. But What happens if fault occurs on "B" phase. How the fault is identified, for example in solidly grounded systems current based fault detection is used and in ungrounded systems voltage based fault detection is applied. In this particular case how the fault is identified?

Reply
4
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3
In reply to #2

Re: Ground fault protection in corner grounded delta system

11/26/2016 4:01 PM

It can be done by residual current.....

If the A, B and C wires pass through a CT, then normally (ignoring leakage and capacitance currents) the currents sum to zero. However, for an earth fault, as shown, the earth current goes out through the CT but back via earth - so the earth current in the CT is not cancelled and current flows in the relay.

There are other ways to get same effect like separate windings for each current A, B, C.

Devices integrating a circuit breaker with this detection are called Residual Current Device (RCD) in Europe and Ground Fault Circuit Interruptor (GFCI) in USA.

In single phase domestic service RCBOs (overcurrent breakers with integral RCD) up to about 50 amps are used with sensitivity of 30 milliamp residual current in the circuit through the CT.

Commonly, this gives trip for >=30mA earth current (<10 mA even 5 mA is available), although it would not matter if the residual current were to another circuit not ground, which is why the RCD name is used.

Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #3

Re: Ground fault protection in corner grounded delta system

11/28/2016 6:25 AM

A break in conductor A, for example a fuse blowing, would require a trip on the basis of an earth fault, particularly if the fault circuit contained a human being in series with the supply. GA.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #7

Re: Ground fault protection in corner grounded delta system

11/30/2016 5:36 AM

Update: the A phase conductor as shown can be considered to be a neutral conductor. Most national standards will not permit the additional grounding/earthing of a neutral downstream of the distribution point as it leads to non-fault currents in the ground/earth. A residual current device in the supply leads will disconnect in the event of the ground/earth current exceeding its trip setting, as has been correctly suggested elsewhere in this thread. One would not expect a circuit protective device to be placed in the neutral conductor as, were it to open, phase voltages would appear downstream of it; for this reason such an installation falls outside the content of most national standards.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#8
In reply to #3

Re: Ground fault protection in corner grounded delta system

11/29/2016 2:46 AM

67model,

Thank you!

But still I'm unable to grasp. As you can see in the below picture, the B phase is grounded at the service entry too. With current flowing through B phase to the motor, why doesn't the current circulates between the grounds?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Ground fault protection in corner grounded delta system

11/29/2016 3:36 AM

By all means ground the outer casing of all field equipment that is not double-insulated.

It would be a mistake to ground the service conductor in the field, as to do so would ensure that operating current circulates via ground; such a situation would constitute a fault and the residual current equipment would operate to disconnect the supply.

Were such a connection to be made via a human being, and the residual current equipment were to be absent, it would not be reasonable to expect the human to survive the experience.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#11
In reply to #8

Re: Ground fault protection in corner grounded delta system

11/30/2016 5:52 AM

Your posted question was - how to protect motor by detecting "earth" fault! To protect motor pass three motor wires through CT at A.

To protect everything, pass 3 wires going into 3 pole isolator through CT at B.

Current will circulate between the grounds, if only because the load current through the ground/Bphase wire causes a volt drop, putting a voltage between the two grounds. One assumes earth fault protection (other than fuses/breaker) is not present upstream of incoming 3 pole isolator.

The motor windings are well insulated from its case, so only small leakage (mostly capacitance) currents will flow to the ground terminal of the motor casing.

Some street supply systems use cables with combined neutral & ground [maybe concentric with outer ground/neutral](and multiple grounds) up to the house incomer. At the house incomer, circuit protective conductors [CPC] from each outlet are connected to an "earth" ("ground") bar in the incoming distribution board/panel/box (DB) which is connected to earth/neutral at incoming cable end.

It would not matter if the DB was in a wooden "container" building sitting on top of a another wooden container. That's why our "wiring regulations" now write CPC except where it really is earth. The whole system including source generator could be on an insulated fibre-glass ship or aeroplane.

67model

Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#12
In reply to #8

Re: Ground fault protection in corner grounded delta system

11/30/2016 7:08 AM

Second attempt -further to my post #9.

I have realised what may be your misunderstanding. I did not draw my diagram properly to show the reality of "earth" for most equipment! It is actually a wire back to a terminal in the building incomer provided by the power supplier and usually called earth/ground. The wire's purpose is to make sure,as far as possible, a fuse blows if metal casings become live due to a fault. Typically, the consumer's earth is wired back to the earthed winding terminal at the transformer providing the supply.

Usually, nowadays, socket circuits are protected, additionally to provision of CPC "earth/ground" in socket, with RCD trip, because it is sensitive enough [30 milliamps] to protect most people who touch a live terminal (RCD mandatory provision started just for sockets for outdoor use, the damaged cable lying in a water puddle risk).

In some cases, for low cost, there may be no supplier's earth wire and building "ground" is a rod driven into the ground by the building. A single rod gives only 30 ohms earth resistance in typical good soil, which would not blow even a small fuse current rating.

In such cases the connection to the rod goes through the coil of a sensitive "earth leakage circuit breaker" ELCB which disconnects the consumer's supply. If you are in a dry location on a bed of sand the earth resistance is too high to work even this.

But if you have an RCD protection, then, within the building, it does not matter how good the earth rod is! This is why metal gas and water supply pipes are bonded to the earth terminal within building (outside buildings, plastic gas/water pipes are common now).

67model

Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #12

Re: Ground fault protection in corner grounded delta system

11/30/2016 7:35 AM

GA

On a TT-earthed system, the CPC is wired to a local earth rod, and this is the route for the fault current - until the residual current device opens the circuit to disconnect the fault, that is.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#14
In reply to #2

Re: Ground fault protection in corner grounded delta system

11/30/2016 1:24 PM

If you want to detect a neutral to earth fault, which is really what you're saying, you need an earth leak trip device, because a neutral to earth fault also needs disconnection before you hurt or kill somebody. A fuse will disconnect a phase to earth fault.

__________________
Good moaning!
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Ground Fault Protection in Corner Grounded Delta System

11/26/2016 4:08 PM

If phase B is intentionally corner-grounded, then contact from phase B to ground is not a ground fault.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: Ground Fault Protection in Corner Grounded Delta System

11/28/2016 6:19 AM

Ahem, it is if the circuit to ground contains a human being in series with the supply.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: Ground Fault Protection in Corner Grounded Delta System

11/27/2016 3:21 PM

Friend/AP#1,

I would expect an imbalance in the current flow. The flow through the "B" phase would partly go through the insulated wires to the motor and partly through the earth/ground path.

Picture a circuit having a fusible disconnect switch with fuses on the A & C phases and no fuse on the B phase; have the B phase properly grounded on the line side of this disconnect switch. This is the normal way in which this type of system is wired. From the disconnect switch have the three wires then go to a motor starter and from there to the motor. Because the B phase has shorted to ground at the motor, instead of all its current flowing through its wire, some uses the alternate ground path and returns to the service ahead of this fusible disconnect switch.

Hence, if you are using an IEC-style overload heater, which senses and reacts to current imbalance (and not just a current overload), this current imbalance may be enough to trip the overload. If the motor currents are within the nameplate rating of the motor, you may not recognize the grounded B phase as the reason for this trip.

A large number of electricians have not seen a corner-grounded 3-phase service and will assume it is a typical single-phase service. However, when they read the voltages between all three wires and find they are equal they will scratch their heads and (hopefully) ask someone to explain what is happening.

--JMM

Reply
Reply to Forum Thread 14 comments