Can someone help me in deciding correctly the cable type and sizes required for the input and output of following welding machines:
  1. Submerged Arc Welding m/c: (Inverter based)
Rating: 55 kVA,
Current range: 60 – 1250 A,
Open circuit Voltage: 75 V
Full Load pf: 0.95
Duty cycle: 100%
  1. MIG Welding m/c: (Inverter based)
Rating: 17.2 – 22.5 kVA,
Current range: 340 – 400 A,
Open circuit Voltage: 18 – 54 V
Full Load pf: 0.95
Input Current: 35 A
  1. Welding Rectifier m/c:
Rating: 18.4 kVA,
Full Load pf: 0.95
Duty Cycle- 100%
Thanks
Pathfinder Tags: cable sizing Welding Machines
Re: Cable Type & Sizing Required For Welding Machines
08/11/2007 2:08 AM
55KVA or 22.5
3Φ or 1Φ?
fOR 3PH 55000=√3. EL..IL . cosΦ (=0.95) . Knowing EL - SAY 420V you get ILAmps.
Rule of Thumb for light insulation thickness in free air =1000 Amp/mm2 You get section in Aluminium
Likewise for1phase
08/11/2007 2:28 AM
Thanks for your reply.
All eqpts are 3 phase.
For 55 KVA, IL = approx. 75-80 Amps. This is OK. However, what is the reason for assuming pf = .95. Is it not true that pf is generally poor for welding machines?
Also, could u throw some more light on this thumb rule of 1000 Amps/mm2??? (1000 Amps??) (eg. 90 mm sq. cable is normally rated for around 130 Amps? then how come 1000 amps / mm sq?)
08/11/2007 12:54 PM
< =1000 Amp/mm2 >
0ops!! Meant 1000A/inch2 Or~ 1.5A /mm2