Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/08/2016 2:35 PM

Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Starting CT Ratio 200/1 Amps.

How to calculate protection setting calculations for Thermal Overload for 895kW 11KV motor

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#1

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/08/2016 2:54 PM
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/08/2016 6:12 PM

Even easier...

1. Read motor nameplate for the FLA value

2. Read instructions for your specific OL protective device to see how you set it.

You cannot generically assume anything, each relay manufacturer has their own internal design philosophy. OL relays have a "pick-up point" at which the relay begins to respond to the motor OL condition. Depending on the regulations in different parts of the world, that pick-up point is going to be anywhere from 115% to 125% of the motor FLA. In addition, some relay mfrs expect YOU to factor in the pick-up point, others do it for you, meaning you set the relay AT the motor FLA. Without knowing what yours does, you cannot assume. Assuming is guessing, and on something that big, guessing wrong is going to be very expensive.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/08/2016 11:29 PM

For such high powered motors relay setting has to perfect.For this one has to study the motor characterstics like, Fulload current, starting current, acceleration time, time constant, no of starts , cold and hot withstand time etc.

Only with these information correct setting can be proposed.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #3

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/09/2016 2:06 PM

This assumes you have a relay that is capable of this level of programmability. The OP made no mention of what he/she has...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8
In reply to #7

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/09/2016 2:19 PM

Although he has not mentioned, such motor protection relay required for these type of high powered motors.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Off Topic
Participant

Join Date: Dec 2016
Posts: 2
#10
In reply to #3

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/11/2016 3:53 AM

Please find attached Motor Data Sheet, We are using Sepam 40 Motor Protection Relay, Please advice !!

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/08/2016 11:46 PM

Embedding a temperature sensor in the motor windings might be a good idea, too.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#5

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/09/2016 6:01 AM

A phone call to the motor manufacturer is overdue, if the information is not already contained within the data sheet for the particular motor. With regard to the latter, it cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/09/2016 9:32 AM

Try this.. go to your office, pick up the phone and call someone who knows what they are doing!

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/10/2016 1:09 AM

See-for instance:

IEEE 242/2001 ch.10.5 Medium-voltage motor protection

and

XM1 - Motor protection relay

file:///C:/Users/user/Downloads/proddocspdf_2_354.pdf

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11

Re: Thermal Overload Setting for 11kV Chiller Motors 895KW DOL Start CT Ratio 200/1

12/12/2016 12:27 AM

At first it is impossible to read the attached list.

If the stall time is 10 sec you have to check if the starting time it will be less.

You need the compressor inertia moment and to state if the start will be at no-load or not.

See ABB instructions how to appreciate the starting time.

See Sepam 40 instructions :

http://www.engineering.schneider-electric.se/Attachments/ed/use_main/sepam_40_user_manual.pdf.pdf

Try to contact Schneider Electric at your country.

__________________
Julius
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); brich (1); JRaef (2); lyn (1); PWSlack (1); ramvinod (2); Tornado (1); Zaheer SCAN (1)

Previous in Forum: Intermittent Faults - Definition   Next in Forum: Current Transformer Composite Error Determination

Advertisement