Anonymous Poster #1

Selection of Upstream Breakers

01/14/2017 10:08 AM

Hi,

Say, a circuit has 8 branches. The sum of currents in all of them is 18.04 amps.

Now, max size of branch circuit MCB is 16 amps. (others are 6 amps MCB).

What will be the size of upstream of 8 branch MCBs?

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: selection of upstream breakers.

01/14/2017 10:27 AM

It depends on local regulations, especially on how diversity may be used in load calculations.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: selection of Upstream Breakers.

01/14/2017 11:12 AM

NFPA 70e

Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#3

Re: selection of Upstream Breakers.

01/14/2017 12:14 PM

Total average load plus 20 - 25% rounding off the nearest common since breaker that fits in that range.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: selection of Upstream Breakers.

01/14/2017 12:30 PM

You don't really have any choice, all electrical installations are governed by the electrical codes....consult your local codes....

https://www.fs.fed.us/database/acad/elec/greenbook/3_basicdesigns.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#5

Re: selection of Upstream Breakers.

01/14/2017 2:35 PM

Is this a homework question? 18.04 amps sounds a little precise (truly, 18 amps + 40 milliamps? In a power distribution circuit?) given the ordinary realities of varying mains voltage and so forth, and so sounds a bit on the academic side to me. Just curious.

If it is a homework question, what do your lesson's study materials tell you?

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: selection of Upstream Breakers.

01/14/2017 3:20 PM

It only gets worse.

Electrical Panels Rating

Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#8
In reply to #7

Re: selection of Upstream Breakers.

01/14/2017 3:27 PM

It does rather seem someone is a bit in over their head, yes?

Is it too late to suggest a career change?

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: selection of Upstream Breakers.

01/14/2017 4:00 PM

Be careful.

One of my faults is telling the truth when a poster demonstrates a complete lack of competence in a subject, especially when discussing something with a high potential for lethality, like electricity.

I've been accused of being a meanie for giving someone truthful advice that they are in way over their heads.

I wouldn't give a blind man a loaded gun and invite him to shoot it.

Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#10
In reply to #9

Re: selection of Upstream Breakers.

01/14/2017 4:17 PM

Yes, I know, but I think at this stage the greatest risk the OP currently faces is a paper cut. I have this hunch he's a student who's not studying his lessons thoroughly enough to pass his sparky exam.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #10

Re: selection of Upstream Breakers.

01/14/2017 4:39 PM

His dog ate his code book.

I weep for our future.

Incompetence seems to be in vogue these days.

Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#12
In reply to #11

Re: selection of Upstream Breakers.

01/14/2017 4:52 PM

Most students I've encountered (and I've encountered quite a few, trust me) are pretty incompetent. Probably why they're students. At least we can give them credit for attempting to remedy the situation by attending school. Unfortunately for some, merely attending classes doesn't seem to have much effect. They also have to study, a foreign concept to some. Our OP sounds like he may fall into this latter category. My advice to him is log off this forum and get his nose back into the books. At the very least this will remove him from live circuits.

If he'd said 18 amps, I would be concerned, but he said 18.04 amps. He's either designing a space probe's power distribution bus where every milliamp counts (highly unlikely methinks) - or he's in school and this a homework problem.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: selection of Upstream Breakers.

01/14/2017 3:17 PM

It depends not upon the loads connected, rather upon the cables connected, about which the forum has been told exactly nothing. After all, the circuit protective device is only there to protect the cables.

British Standard 7671 gives full protocols for this sort of assessment and to post further on the topic here is abstruse. If in doubt, consult a qualified Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Associate

Join Date: Mar 2014
Location: Mumbai, India
Posts: 25
#13

Re: Selection of Upstream Breakers

03/07/2017 4:57 AM

I feel if sum of all currents is 18.04Amps, then to have close overload protection main incomer must be 20Amps. However as I can see, that the selection of outgoing MCBs is on much higher side which needs to be rectified to have close protection. Today MCBs are also available in 0.5A, 1A, 2A, 3A, 4A, 6A. It is recommended to use those depending on max load on each outgoing. Thanks.