Load Balance Problem

01/19/2017 8:21 AM

Hi,

I am designing an electrical system with 8 branches of loads and only last branch among them has three phase load of 1 H.P. motor. Here is the summary:

(1) Sum of all single phase (single phase load) currents: 17.43 amps

(2) For three phase motor of 1 HP, line current = 0.60 amps.

As three phase motor is a three phase load, in all R,Y,B phases a line current of 0.60 amps will flow. So, 0.6 amps shall be added in all R, Y and B.

(3) No 1 single phase current is:

0.73 (lamp, fan) +1.04 (computer) +0.87 (freeze)+1.14 (lamp, fan)+1.39 (lamp, fan, tv) +4.43 (geyser) +7.83 (air conditioning) = 17.43 Amps.

(4) R phase = 0.6+7.83 = 8.43 amps.

Y phase = 0.6+4.43 = 5.03 amps.

B phase = 0.6+1.39+1.14+0.87+1.04+0.73 = 5.77 amps.

(5) How to go for load balancing? As I understand, vector sum of currents Ir,Iy and Ib should be zero. But here, sum of R, Y and B phases has a considerable value to return from neutral.

Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Load Balance Problem

01/19/2017 9:02 AM

Eh? Simply move the single phase loads around until the totals are around 12A per phase, or as near as possible to that figure.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#2
In reply to #1

Re: Load Balance Problem

01/19/2017 9:15 AM

How you reached to the conclusion of 12 amps per phase?

Regards,

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Load Balance Problem

01/19/2017 10:18 AM

This is primary-school arithmetic. Invitation declined.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 9)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: Load Balance Problem

01/19/2017 11:07 AM

The distribution of loads to R, Y, B you suggest is OK as a "balance".

Ideal balance is rarely obtained - in any case, loads usually go on/off at various times outside the designer's control e.g. freezer and air-conditioning will go on/off according to ambient temperature and other loads according to wish of user.

"vector sum of currents Ir,Iy and Ib should be zero" if the three currents form a symmetrical triangle or Y e.g. Ir = Iy = Ib with angles 0, 120, 240 degrees respectively. Even if the currents are equal, they must have same power factor when fed from a symmetrical 3 phase voltage.

This is rarely achieved practically in final circuits with single phase loads, but a design for balance minimises neutral current, losses, volt drop and overloading of an individual phase.

Because supply distributers connect up homes etc in succession along a street as single phase supplies, R-Y-B-R-Y-B-...., the phase loads average out to a better symmetry at the local transformer.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5
In reply to #4

Re: Load Balance Problem

01/19/2017 11:34 AM

This is import to one phase in a real building over one day, loads are central heating pump, fridge ~ 2 amp, freeezer ~ 5 amp, lights ~ 0-8 amp and solar power generation (the fuzzy bits, logging cannot show power direction). Vertical amps, horizontal seconds 0 - 90000.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#6

Re: Load Balance Problem

01/19/2017 11:48 AM

Why do you feel you need to have such a small total load balanced across three phases?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #6

Re: Load Balance Problem

01/20/2017 2:58 AM

Pity there isn't a Good Question button.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#7

Re: Load Balance Problem

01/19/2017 3:48 PM

Sum Ting Wong offers a better solution where the branches actually add up.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#8

Re: Load Balance Problem

01/19/2017 10:24 PM

Your goals are laudable, however, practical impact is non existent. You could put all of those loads on one leg, and neither you or the utility will have a care in the world.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Power-User

Join Date: Sep 2016
Location: SPAIN
Posts: 233
Good Answers: 13
#9

Re: Load Balance Problem

01/20/2017 1:26 AM

I do not know if this is a concept issue, but what exactly are you talking about?

Amps is for instant value, Amps DC for average value, and Amps rms is for squered averaged value.

Considering your tools, you are adding rms values as if they were apples. Are you sure that no load has a phase shifted current?

Anyway, for balancing the loads you can literally "balance the loads" as my fellows suggested, or you can install a 3 phase transformer and expect the magnetic flux to do its job. However, it should be ibvious that this last solution will be expensive.