Star Delta Starter

01/20/2017 3:35 AM

Star Delta Starter uses contactors for reduced voltage starting of cage motors. I have seen this starter for low voltage (400v) motors but not for medium voltage (say 11kv) motors starting. Why? Medium voltage vacuum contactors are available from different manufacturers so it should not be difficult to do star delta in medium voltage. Also how is V/f relation kept constant in star delta because starting voltage is reduced but frequency is constant.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: star delta starter

01/20/2017 3:37 AM

Hint: has it got anything do with the power available within the circuit, voltage drop, and the circuit's resilience to motors starting on it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#2
In reply to #1

Re: star delta starter

01/20/2017 3:40 AM

u giving me or asking hint?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: star delta starter

01/20/2017 3:46 AM

Er, what part of the <...?...> is difficult to understand, please?

Think it through.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#4
In reply to #3

Re: star delta starter

01/20/2017 3:54 AM

non english speaker here dear thats why asked "intent" of "?".

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: star delta starter

01/20/2017 3:55 AM

Starting current is already pretty low on MV/HV motors. (And, can you just imagine how big a Y-Δ MV/HV starter would be?)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: star delta starter

01/20/2017 3:56 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#7
In reply to #5

Re: star delta starter

01/20/2017 4:02 AM

i saw a 4MW ,11KV compressor motor being started across the line. the whole 11KV busbar tripped on undervoltage. the guys then changed tapping of the 220/11KV transformer that fed the 11KV substation to bring voltage to 11.5KV. so starting current is not that low if equipment is large

Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#16
In reply to #7

Re: star delta starter

02/09/2017 12:03 AM

4 MW motor at 11KV starting across the line are not applicable as the starting current are too high. Basically for these 4MW motor at 11KV, we use liquid starters to start. Motor below 400KW at 11 KV are aceptable to start across the line as the starting current are low.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#12
In reply to #5

Re: star delta starter

01/21/2017 4:42 AM

yes , big cabinets reserved for four contactors for close transition will make star-delta very difficult and noneconomical.agreed

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: star delta starter

01/20/2017 10:50 AM

Star (wye) - delta starting is basically a scam to begin with. It works to a much lesser degree than most people realize and adds more problems than it solves. But it will technically satisfy requirements for reduced voltage starting because we collectively agree to ignore the evidence to the contrary and the negative consequences when used on low voltage motors, because people want a cheap solution. That's all it really offers compared to all alternatives.

Once you get into the world of MV motors, you have entered the realm of critical path machinery; meaning that which, it not functioning, generally means your entire operation shuts down and the economic risks to the company or entity border on catastrophic. So the little ignored details in LV systems such as severe torque spikes on transition, voltage dips because the transition current spike is equal to or greater than Across-the-Line starting current anyway, the rapid destruction of contacts in the contactors and the extreme mechanical stresses imparted onto the test of the drive train components, all add up to allow real engineers to take precedence over cost cutting bean counters.

If you need to truly reduce starting current and/or stating torque on a MV motor, use a solid state soft starter. It likely will cost you the same at MV compared to a star-delta starter anyway.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#9
In reply to #8

Re: star delta starter

01/20/2017 12:01 PM

soft starter also does not maintain V/f=K ,i think. only option left is VFD.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#13
In reply to #9

Re: star delta starter

01/21/2017 5:45 AM

You should understand the V/f control is only used because the frequency is variable.

On a variable speed drive, if volts were not reduced in proportion to Hz, the motor would be overfluxed - saturation, high current, strain on electronics.

If volts not increased with Hz, torque at 150% speed would fall to 100/150 rated - constant power behaviour.

A usefull "rule" is that for transfos at a constant frequency "the primary voltage determines the magnetic flux". Also, for a given inductance, current is proportional to frequency and flux is proportional to current.

With generators bolted to main step-up or unit auxiliary transformers, transfo overfluxing would occur below normal speed if V/Hz control was not applied. This causes mighty humming, mechanical vibration stress in transfo, tripping of differential relays and transient voltages going in/out of saturation. Note that on big generators, excitation comes on/off at about half speed with correct V/Hz ratio then, and at higher speeds.

Star/Delta starters do not vary frequency so V/Hz is not "in the picture".

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10

Re: Star Delta Starter

01/20/2017 6:02 PM

Maintaining the V/Hz ratio is what a VFD does to MAINTAIN torque in the system.

Reduced Voltage Starting does change the V/Hz ratio, which reduces the torque, which is one of the REASONS to use it. That's why you cannot do it for long though.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#11
In reply to #10

Re: Star Delta Starter

01/21/2017 4:39 AM

normally in industry, when motor is started on reduce voltage , the low starting torque is handled by closing discharge valve of centrifugal pump,damper of air handling unit etc so that mechanical starting load imposed on motor shaft is low enough to prevent motor stalling.

Register to Reply
Associate

Join Date: May 2007
Location: Serbia
Posts: 44
Good Answers: 4
#14

Re: Star Delta Starter

01/21/2017 7:07 AM

We have at our factory five 2/ 0,5 MW 6kV motor for fan operation which has 3 switches to achieve pole scheme Y / YY .Last 30 years system for starting and motor works well and recent idea about their replacement with soft starter we refused .

Perhaps the problem is that they are really rare , bearing in mind that the higher consumption of copper for making windings and a small low cos φ at low speed .

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#15
In reply to #14

Re: Star Delta Starter

01/21/2017 7:39 PM

Your Y-YY situation is different, that's a 2 speed motor. You likely always start it in low speed but that's not the same as a Y-delta start scheme.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); coolyaar (6); JRaef (3); Panta SD (1); PWSlack (3); Simon Wan (1); Tornado (1)

Previous in Forum: Motor Housing vs DIN 1.4470   Next in Forum: Generator Power Factor

Advertisement