Power Consumption

08/15/2007 5:33 PM

The questions was posed to me on how much power are we wasting by not shutting off the motors in a room when they are not being used. I couldn't find the formulas that I needed to use, and didn't find them in my head. So I need some assistance. Here are the factors:

Warehouse with approx. 50 motors running conveyors

Motors average 1 1/2 hp; 460V 3 phase 60 hz; 2.33 amps

Loaded approx. 10 hours per day (off and on for 16 hours)

running 24hrs per day. (they just won't shut them off when they aren't needed or they go home)

That and they won't shut the lights off either.

__________________
Home is where the heart is!
Register to Reply
Pathfinder Tags: motors power consumption
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Aug 2007
Posts: 1
#1

Re: Power Consumption

08/15/2007 11:38 PM

Ref your query, I think that you don't need a formula, you will need an instruments like Fluke-1735 Power Logger (or similar) to take all the informatiom from the motors.

Cordially yours, Arturo

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Power Consumption

08/16/2007 3:55 AM

It looks like there is an opportunity for improving the bottom line of this organisation. If corporate nagging techniques don't work, consider investing in time-switches and room occupancy sensors, assuming the organisation pays for electricity by the kWh?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#3

Re: Power Consumption

08/16/2007 9:10 AM

Well, let's see. You're people are definitely wasting power, that's for sure.

If you're warehouse happened to be located in my factory, our boss would blow his top and put a grenade in each of the people's pants and threaten to pull the pin if everyone doesn't shape up.

All that and he won't even stop to ask how much power is being wasted. All he cares about is that power IS being wasted and he doesn't care how much.

So...don't ask how much, just stop the waste.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Commentator

Join Date: Jun 2007
Location: Colorado, USA
Posts: 91
Good Answers: 1
#4
In reply to #3

Re: Power Consumption

08/16/2007 3:46 PM

Before El Gato Del puts his two cents in, when I had a few minutes I searched the site and found where this had been discussed before and found the formula that I needed. And I passed that on to those concerned, and hopefully they put a few hand grenades down some shorts and pull the pins.

Thanks guys!

Jon

__________________
Home is where the heart is!
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#5
In reply to #4

Re: Power Consumption

08/16/2007 11:45 PM

Consider adding some proximity switches & or photo beams so the conveyors don't run when empty, a few timers to complete run out would limit the complexity of such a set up

Register to Reply
Participant

Join Date: Aug 2007
Posts: 1
#7
In reply to #3

Re: Power Consumption and proper word usage

08/17/2007 2:09 AM

I am an engineering type, so you can imagine how much I must be irritated by this misuse of language to offer this critique. i.e.

"You're people are...." You're is contraction for you are, the context of this phrase requires a possessive pronoun which would make the phrase 'your people... The poster misused this pronoun twice in his post.

You're people are definitely wasting power,.....
If you're warehouse happened to be located in my factory,.....

Register to Reply Off Topic (Score 6)
Anonymous Poster
#9
In reply to #7

Re: Power Consumption and proper word usage

08/17/2007 3:56 AM

are, the

The above punctuation mark should be a semicolon, not a comma.

Register to Reply Off Topic (Score 7)
Anonymous Poster
#13
In reply to #9

Re: Power Consumption and proper word usage

08/17/2007 7:27 PM

corrected

10q

Register to Reply Off Topic (Score 5)
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#14
In reply to #7

Re: Power Consumption and proper word usage

08/18/2007 9:19 AM

Great catch! You're right and I was wrong (I used it right this time eh?).

No excuses offered. It was a slip of the fingers (which is connected to the spinal column, which leads to the brain, etc.).

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Power Consumption

08/17/2007 12:27 AM

First off, technically the answer to your question would be "100%"!

If you are running motors that are not being used and don't need to run, the wasted power is 100% of the consumed power. I know that's probably not what you meant to ask, I was just being persnickety.

But if you don't have a way of actually measuring the unloaded power, you can guesstimate it fairly well by using 30% of the FLA. Most small AC motors will pull about 20% FLA when completely unloaded, but in your case you need to add some friction load just to move conveyor belts, so another 10% should cover it (unless you have some kind of unusual belting). In addition, your power factor will be really low, probably in the .3 range, when unloaded. So your kW would be 1.732 x (FLA x .30) x V x pf / 1000 = kW. So in your case, you have 1.732 x 2.33A x .3 x 480V x .3 / 1000 = approx. .174kW per motor, x 50 motors = 8.72kW of wasted power. If you want to know the ENERGY wasted, take the kW x the unnecessary running hours. So if they are left running overnight for 8 hours a day, that's 70kWh per day, x 20 days per month, that's 1400kWh / month. If you pay 15 cents per kWh like we do here in California, that's $210 per month.

An easier solution than occupancy sensors or load sensors on each conveyor may be to put a power (kW) monitor on the power feeder to all the equipment in that room (assuming it's that simple) and look at the normal running kW. When the kW drops below that for a set time, say 30 minutes, shut it all down. Siemens makes a unit that would do that called a Simocode. You would need some sort of a device to kill power though such as a contactor or a circuit breaker with a shunt trip. Either that or use a master control relay wired to each of the motor starters so that it shuts each one off.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Jun 2007
Posts: 11
#10
In reply to #6

Re: Power Consumption

08/17/2007 1:40 PM

Thanks for providing a helpful, direct answer to the original poster. IMHO, too many of the replies I see here are unprofessioanl rants that reflect poorly on engineering in general.

Register to Reply
Commentator

Join Date: Jun 2007
Location: Colorado, USA
Posts: 91
Good Answers: 1
#12
In reply to #10

Re: Power Consumption

08/17/2007 3:19 PM

Thanks for the input.

Talked to my supervisor and since the starters and contactors for the motors are in the cabinet with the PLC equipment, it will be easy to hook them in. Since it is the older, un-renovated part of the plant, we would have to run photo eyes to the conveyors and program in sleep timers to shut them off. We already have the power monitoring equipment, and that is where I got the power factor for my calculations after I found the proper formula.

So it looks like I will gain a new project to spend some money to save some money.

__________________
Home is where the heart is!
Register to Reply
Active Contributor

Join Date: Oct 2006
Posts: 11
#8

Re: Power Consumption

08/17/2007 3:38 AM

As a heads up,you may want to look at what it takes to start back up. Some systems are left in operation because the power is cheaper than re-commissioning the equipment on a daily basis. Unless you have commissioned the system I would do some research before you shut down, the restart sequence could be more complicated than you realize. I assume your goal is to save the company money, also ask how much money it costs if the conveyor system doesn't operate for one day. There will be a day that a motor fails on starting. It would suprise me if the conveyors in your plant are running continuosly simply because nobody has thought of turning them off.

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#11

Re: Power Consumption

08/17/2007 1:41 PM

there are 2 ways you can cut down Waste and hence profit yourCo and/or yourself.

  1. When running ,add automatically a 3Phase Capacitor of appropriate µF across 3 phases. Will now show P.F ~1.0 for each running motor.And line current is a known Low! Say Iidle1
  2. Sensor can be set to MONITOR If that running motor stays at Iidle1 FOR>15 seconds . And hence to automatically Switch Off