Signal Isolator

04/11/2017 1:10 AM

Hello Everyone, i wanted to know what is signal Isolator and why it is used in between transmitter and AI card of PLC??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#1

Re: Signal isolator

04/11/2017 1:42 AM

To eliminate ground loops.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Signal isolator

04/11/2017 6:02 AM

On the "as built" issue drawing of the circuit will be the names of the individuals who designed and commissioned it. Surely a word in these individuals' ears is the best place to start? After all, the drawing cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#3

Re: Signal isolator

04/11/2017 10:00 AM

The clue is in the name...
It isolates the signals from unwanted voltage levels. Something like an opto isolator allows you to have some sort of sensor on (say) a high voltage circuit providing a signal into a 5v logic circuit. the signal being transmitted optically across a gap in the integrated circuit to provide electrical isolation.

Mind, I may be barking up the wrong tree as I have no idea what your appliction is or what an AI card is... artificial intelligence? Alien Invasion? Artificial Insemination?
Ah! Me sir me sir I know... is it analogue input?
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
2
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#4
In reply to #3

Re: Signal isolator

04/11/2017 10:25 AM

It surely bears no resemblance to draw testing.

Depending on what the "noise" in the environment is, this could be a band pass filter. Or, as you stated, it could be an optoisolator to separate signal from a very high voltage offset from the low values tolerated by either logic or an analog input.

For all we know from information supplied in the initial post, this could be nothing more than a shield of woven wire around the analog signal wire and its common ground wire.

just one example, that provides galvanic isolation in this instance.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#6
In reply to #3

Re: Signal isolator

04/12/2017 8:08 AM

PLC's have AI, AO, DI, DO, and some others lesser used cards. Analog Input, Analog Output, Digital or Discrete Input and of course Output. Standard acronyms in the control world.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#8
In reply to #6

Re: Signal isolator

04/12/2017 8:39 AM

D'uh... but not everyone is in "The control world"
Grrrr hisss ftzzzzzz

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#9
In reply to #8

Re: Signal isolator

04/12/2017 8:51 AM

That's why I gave you an explanation. The OP assumed we were in his "world". I just happen to be there too. We don't think when we speak of PLC cards - we just use the terminology we use everyday.

Be careful with that grrrr and hissss - that avatar is "Nittany" and you don't want to excite her - she takes aggressive cats out of the yard every time they enter. She will try to go right through our sliding door to the deck if one gets up on the deck. She even holds her own against 30 pound dogs.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#10
In reply to #9

Re: Signal isolator

04/12/2017 12:23 PM

Our current cat Emily is a bit poorly, she had an accident, her tail doesn't work any more, her bladder control isn't fully back to normal and she has some lumbar irritation which is making her bit at her back. It's a work in progress, but she's happy in herself.
She was missing for 3 days, but dragged herself home.
Prob' going to have her tail amputated next week
Del

PS. I was a tad confused by your statement:-

"It surely bears no resemblance to draw testing." which meant absolutely nothing to me... I recognise each word, but the only draw testing I'm familiar with relates to longbows

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#11
In reply to #10

Re: Signal isolator

04/12/2017 2:24 PM

That is because I knew about your bow testing rig. Your draw tests. The only signal that matters is the draw, not the twang, or if it breaks, the thunk sound.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#13
In reply to #11

Re: Signal isolator

04/12/2017 3:08 PM

Ah! That explains it... you are ahead of me
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#12
In reply to #10

Re: Signal isolator

04/12/2017 2:50 PM

That is a quite a bit like the old stray my mother took in while I was in college. He'd go out for a week and come back all beat up. He'd stay until he healed well enough to go again. He had partial ears, from fights, his face was always covered in scars, and his tail drooped a bit, but he soldiered on to about 13 years old. Best incident was the broken leg when he was gone over 2 weeks. We had to have the Vet. break it and reset it. It extended the full length of the hind leg and beyond a bit. One of us stayed with him day and night to pick him up to go relieve himself, as he could barely hobble around on the cast and despite our allowing him to stay in the house, he was still an outdoors cat, so that is where he went - no litter box. Didn't dare let him out by himself, or he would have tried to go hunting on that cast.

The things we do for our beloved little friends......

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Feb 2017
Posts: 69
Good Answers: 4
#5

Re: Signal Isolator

04/11/2017 11:00 PM

Without a signal isolator, you could end up accidentally feeding in a high voltage into your computer / PLC, which could damage it.

Even an incoming signal level is only, say 3.3V, you don't know what it is referenced to!

For example, the "ground" or zero volt level might be at a different potential between your computer's motherboard and the other device that is sending or receiving a signal.

You could have a 100V difference or more between the main DC ground of your computer and the other device.

Without a signal isolator, you could blow up your computer!

For example, Ethernet interfaces are magnetically isolated. Each wire pair is connected to small transformers on both ends ("magnetics"). This, by the way allows for transmitting power in Ethernet cables (PoE).

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#7

Re: Signal Isolator

04/12/2017 8:23 AM

In my 25 years of building/installing control panels on process skids, it has been my experience that they are there for something to do during system testing. EVERY one that was requested by a customer, or installed in a customer provided panel, are sitting in a box in my largest desk drawer. We removed them all during final testing of the system, at the customer's request. Now I'm sure there are times they function properly and are required, but so far, I've not encountered that.

The exception would be intrinsically safe barriers which would technically fall into this category as well as the discussed noise filters. Those must remain to keep voltage/current in a circuit below the level needed for arcing in a hazardous atmosphere application.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#14
In reply to #7

Re: Signal Isolator

04/12/2017 3:49 PM

Very interesting timing. The customer built panel we are testing on a process skid today, much to my surprise, had signal isolators on the analog signal to and from a motor mounted VFD. I totally missed that when going over the drawings to layout our wiring plan. These seem to function fine, and I can see why an engineer threw this in - a VFD is a very noisy item. I know this same panel has worked before without them, but it can't hurt to have them. Wiat - just got word that the analog circuits in question are not working - more on this later after I go do some circuit analysis.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Anonymous Poster #1
#15

Re: Signal Isolator

04/14/2017 6:57 AM
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard