Previous in Forum: Circuit Breakers Question   Next in Forum: How to Identify 3 Phase Energy Meter Multiply Factor
Close
Close
Close
13 comments
Rating: Comments: Nested
Participant

Join Date: May 2012
Posts: 3

LC Filter for Three Phase & Single Phase Thyristor DC Converter

04/30/2017 2:22 AM

I am bit confused in selection of L & C values for a LC filter for my converter application. Mine was a two pulse & six pulse converter. I did apply formulae available but not sure about them...Any one pls help...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: LC filter for Three phase & single phase thyristor DC converter

04/30/2017 3:19 AM

Without so much as a single datum, how can anyone answer?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: May 2012
Posts: 3
#2

Re: LC filter for Three phase & single phase thyristor DC converter

04/30/2017 6:35 AM

My circuit was a battery charger of 24V DC output, 10A max; Input supply to the rectifier is fed from a 750VA 230/45V AC, 50Hz transformer. I want the ripple to be limited to 3%. The L value i have selected is 3.14mH & C value is 10000MFD. My doubt is up to what limit the L & C can be increased and what is their impact on the rectifier efficiency?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3
In reply to #2

Re: LC filter for Three phase & single phase thyristor DC converter

04/30/2017 10:44 AM

Use PSpice to simulate your circuitry.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#4
In reply to #2

Re: LC filter for Three phase & single phase thyristor DC converter

04/30/2017 2:57 PM
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#5
In reply to #4

Re: LC filter for Three phase & single phase thyristor DC converter

05/01/2017 6:16 AM

A model answer:

1. It stimulates the OP to reach his own conclusion

2. It does not abuse the OP for the vagueness of detail in the question.

3. It stimulates lurkers like myself to review broader questions. I knew already why ripple in an amplifier power supply was a bad thing and now I have found an explanation of why ripple in a battery charger may be a bad thing.

Thank you.

Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#8
In reply to #4

Re: LC filter for Three phase & single phase thyristor DC converter

05/01/2017 11:04 AM

just a reminder that dB is a generic relative term, and varies in its definition across the full spectrum of how it is applied. sometimes 20dB represent a factor of 10 increase (-20dB would be 1/10 of the original), whilst other times 20dB would be a factor of 100 increase, and -20dB would be 1% of the original.

The links are not clear which definition is being used, so we assume to power ratio definition so that -20dB will represent 1% of the original signal as ripple. The calculator gives a pretty good result based upon that definition, but who knows if in fact it is right?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #2

Re: LC filter for Three phase & single phase thyristor DC converter

05/02/2017 2:59 AM

The impedance of a battery under charge is so low that ripple elimination is mostly carried out by the battery itself!

The L and C can be increased without limit in terms of value, however with increasing value comes increasing size: in the end it is a judgement call - limitations of space inside the equipment enclosure can have a greater bearing on this decision than anything else.

A battery charger of that rating can usually be purchased at various automotive spares outlets (names withheld), so there is rarely any need to design.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#6

Re: LC Filter for Three Phase & Single Phase Thyristor DC Converter

05/01/2017 8:31 AM

Without any liability

The value for a smoothing capacitor is 2000 uF for each ampere current (rule of thumb). In your case you need a 10 000uF capacitor. But it all depends on the allowable ripple current.The voltage level for the capacitor is 45 X sqrt (2) x 1.2 (safety value) = minimum 76V.

Keep in mind to use a 1 phase transformer with a center tap and 2 diodes or if there is no center tap use 4 diodes (bridge rectifier).

A better solution, if you have 3 phase supply, is to use a 3 phase (separation) transformer and 6 diodes.

Another point of attention. Your output voltage must be 24V, if you use a transformer with a secondary voltage 45 Vac, the output voltage will be too high.

Register to Reply
Participant

Join Date: May 2012
Posts: 3
#7
In reply to #6

Re: LC Filter for Three Phase & Single Phase Thyristor DC Converter

05/01/2017 10:23 AM

Without any liability

The value for a smoothing capacitor is 2000 uF for each ampere current (rule of thumb). In your case you need a 10 000uF capacitor. But it all depends on the allowable ripple current.The voltage level for the capacitor is 45 X sqrt (2) x 1.2 (safety value) = minimum 76V.

Keep in mind to use a 1 phase transformer with a center tap and 2 diodes or if there is no center tap use 4 diodes (bridge rectifier).

A better solution, if you have 3 phase supply, is to use a 3 phase (separation) transformer and 6 diodes.

Another point of attention. Your output voltage must be 24V, if you use a transformer with a secondary voltage 45 Vac, the output voltage will be too high.

I intend to use single phase half controlled bridge rectifier with 2 SCRs & 2 Diodes. The output voltage is 2Vm/pi * Cos(alpha). The output voltage can be adjusted by firing the SCR is suitably.

If i use 10000uF capacitor what shall be my choke value?

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#9

Re: LC Filter for Three Phase & Single Phase Thyristor DC Converter

05/01/2017 4:20 PM

Without any liability

The smaller the fire angle is, the less energy you put in the capacitor, the bigger the capacitor and coil must be.

No idea what the minimum value will be for the coil, it also depends on the ripple current that is acceptable. But the higher the inductivity, the smoother the current will be. Higher inductivity means a bigger coil and more windings. Please use no air-coil, but coil with laminated steel core.

A secundairy from an old transformer is good. But the cupper wire diameter must be big enough to carry the 10A current. (rule of thumb = 3A per square mm cupper surface)

Using a variac is much easier, capacitor and coil can be smaller.

Why not using a SMPS (switched mode power supply), efficiency is much better, current is much smoother, price is probably less.

http://be.farnell.com/tdk-lambda/rws-300b-24/ac-dc-conv-1-o-p-24v-12-5a-300w/dp/2444007.

Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #9

Re: LC Filter for Three Phase & Single Phase Thyristor DC Converter

05/01/2017 4:36 PM

Interesting that you would go there. Those are great little power supplies, IMHO.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#11

Re: LC Filter for Three Phase & Single Phase Thyristor DC Converter

05/01/2017 5:19 PM

You want to get a copy of the paper titled, "Analysis of Rectifier Operation" by O.H. Schade. It was published in 1943. Yes, 74 years ago. Mr. Schade put a lot of work into those curves. Don't waste his efforts by ignoring them.

Here is a source for more knowledge:

http://www.powerelectronics.com/content/ac-rectifier-bulk-capacitor-selection-analysisspice

and here:

http://www.powerelectronics.com/power-management/analyzing-full-wave-rectifiers-capacitor-filters

Good luck with your quest.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: LC Filter for Three Phase & Single Phase Thyristor DC Converter

05/02/2017 3:22 AM

It is fascinating how many Engineers try to design power supplies when there is so much immediately available on the open market that saves one having to do the design.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Brave Sir Robin (1); James Stewart (2); phph001 (1); pssdeepak (2); PWSlack (2); RAMConsult (1); Rixter (1); rudy.leurs (2); Tornado (1)

Previous in Forum: Circuit Breakers Question   Next in Forum: How to Identify 3 Phase Energy Meter Multiply Factor

Advertisement