05/10/2017 9:27 AM

I have a three phase mains connection. An RCCB is installed after the electrical meter. The three phase wires are connected to on pole of the 2pole RCCB and neutral is connected to the 2nd pole. Will this arrangement work fine? If not, what problems will it cause?

Register to Reply
Pathfinder Tags: RCCB 2 pole three phase
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#1

Re: Three Phase wires in one pole of RCCB

05/10/2017 9:54 AM

You have three-phase power coming in.

You are connecting all three wires to a single pole.

That is called a SHORT CIRCUIT BETWEEN THE LIVE WIRES.

The first problem is that it will cause breakers to trip/fuses to blow upstream in the power grid, knocking out power for your neighbors.

The second problem is that anyone near the panel when this gets power could be KILLED.

The third problem is that this would get the person who wired it up FIRED for not knowing the basics of electrical wiring.

I would Strongly Recommend that you go back to school and learn about electrical wiring before you try working with electrical power.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#2

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 10:02 AM

1) If this is a test or homework question and you don't know the answer - and you don't know why you don't know the answer - tell your teacher he's wasting his time. Then go over to the registrar's office and change your major to something that does not involve large quantities of energy.

2) If this is a real installation that you're standing near, drop everything this very second and run like hell.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#4
In reply to #2

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 10:16 AM

Thank you, I wanted to use strong language like that, but the last time I did a 'what the he** are you thinking!?!' post to a question like this, it got deleted by the admins for being 'abusive.'

I guess I'm not allowed to yell at people for doing dangerous, self-destructive things. All I can do is fill out the 'observer' paperwork to help these people get the Darwin Awards they are so desperately trying to earn.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 445
#3

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 10:13 AM

Today's Darwin Award goes to...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 10:28 AM

"There was supposed to be an Earth shattering ka-boom".

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#23
In reply to #5

Re: Three Phase Wires in One Pole of RCCB

08/27/2024 11:25 AM

Worrying, isn't it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#6

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 10:30 AM

3. If this is a wiring job you did yourself, put down your tools, go over to the nearest precinct office, and turn yourself in to the police. You will be safer there - and so will everyone else.

Register to Reply
3
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#7

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 11:15 AM

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply Good Answer (Score 3)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33399
Good Answers: 1817
#8

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 11:31 AM

This will cause a massive cross phase short, an explosion will ensue destroying the breaker and damaging the equipment upstream...are you a terrorist?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#9

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 1:16 PM

A'll be jheeting my drawerS if you do that...

Register to Reply Off Topic (Score 5)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 3:34 PM

Perhaps you mean only one of the phases and the neutral is going through the 2 pole RCCB?

No this won't work. Have a look at your local electrical codes and standards for more details, or hire a qualified electrician to perform this work safely and legally.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33399
Good Answers: 1817
#11
In reply to #10

Re: Three Phase Wires in One Pole of RCCB

05/10/2017 6:48 PM

Yeah that makes a bit more sense, a three phase feed that he wants to separate into 3 single phase breakers....You still need a 3 phase main panel breaker....and 3 phase breakers to plug into the panel....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#19
In reply to #11

Re: Three Phase Wires in One Pole of RCCB

05/11/2017 9:05 AM

Warning... this diagram is missing a very important conductor.

It "does not" show a jumper between the bond ("ground") bus and the neutral bus. Without such a jumper in place, the system is depending upon a neutral to bond connection upstream of this panel board as there is no connection between the bonding system and the neutral at this panel board..

Given the possible impedance of such a connection, timely response of the overcurrent devices can not be assured.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#20
In reply to #19

Re: Three Phase Wires in One Pole of RCCB

05/11/2017 10:17 AM

Yes, that, and the neutral really only exists if the XFMR output is 3-phase WYE, not Delta. Seems like a very unusual arrangement, one doomed for failure of one kind or another, and not in code in US or Canada?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Power-User

Join Date: Sep 2013
Posts: 152
Good Answers: 2
#21
In reply to #19

Re: Three Phase Wires in One Pole of RCCB

05/30/2017 7:42 AM

Perhaps it's been done at the transformer.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#22
In reply to #21

Re: Three Phase Wires in One Pole of RCCB

05/30/2017 9:12 AM

A 120Y/208 volt three phase service is pretty much a North American thing. The connection between the bonding system and the neutral, to be code compliant, must be done at "both" spots.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#12

Re: Three Phase Wires in One Pole of RCCB

05/11/2017 1:06 AM

Its sound to me like , you are trying to use 2 pole RCD (single phase) in a three phase four wire system (3- hot ,1- neutral) by shorting three phase into single phase-Very bad idea . I hope you learnt about 3-phase fault.

Best solution is to buy a four pole RCD and complete the wiring. If you dont know hire someone to sort it out.

If it a home work question, click the link below or use Solar eagle's diagram.

http://www.electricalonline4u.com/2015/11/how-to-wire-4-pole-rcd-circuit-breaker.html

Register to Reply
Power-User

Join Date: Sep 2013
Posts: 152
Good Answers: 2
#13

Re: Three Phase Wires in One Pole of RCCB

05/11/2017 3:04 AM

Are you being serious? Or are you taking the P!SS?

Just take a moment and, think about what you are asking.

What would happen if you connected the 3 LIVE legs of a 3 phase supply together? Wait for it!

Are you sure it's a 3 phase supply?

Can you supply some pictures? I could with a good laugh.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#14

Re: Three Phase Wires in One Pole of RCCB

05/11/2017 3:05 AM

<...Will this arrangement work fine?...> No, it won't work at all.

<...what problems will it cause?...> When energised:

  • with good luck, the circuit protective device upstream will operate and disconnect the supply.
  • with bad luck there will be a lot of explaining to do to the Loss Adjuster from the building's fire insurance company after the building has burned down, assuming the individual doing the explanation did not die during that event.

That it is installed in the first place is a great curiosity:

  • Why would one need to ask on a global Engineering forum whether or not it would work if testing it at site would demonstrate this (rhetorical question - NNTR)?
  • Why did the individual installing it not demonstrate its action by carrying out such a test (rhetorical question - NNTR)?
  • Why is there no record of its having been tested that would obviate a need to ask these questions on a global Engineering forum (rhetorical question - NNTR)?

Disconnect the supply immediately. Engage a qualified electrician to install the correct RCCB for a 3-phase supply. Make sure that the test documentation for a correct installation is filed appropriately in case it is needed in the future.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor
Safety - Hazmat - New Member Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Dec 2009
Location: Kampala
Posts: 24
#15

Re: Three Phase Wires in One Pole of RCCB

05/11/2017 5:06 AM

What you should expect after energizing the system is a very loud bang and black ashes around.

__________________
"It doesn`t make sense to hire smart people and then tell them what to do, hire smart people so they can tell you what to do."--- Steve jobs.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#16
In reply to #15

Re: Three Phase Wires in One Pole of RCCB

05/11/2017 7:10 AM

<...black ashes...> But the post-2004 harmonised colours would be brown, black and grey <...ashes...> - prior to then they would be red, yellow and blue <...ashes...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#17

Re: Three Phase Wires in One Pole of RCCB

05/11/2017 7:18 AM

At a rough guess, I think our friend has a single phase supply of a three phase supply.

Like everyone else I can’t figure out the three phases in to one terminal of the RCD.

Is this thread associated with http://cr4.globalspec.com/thread/112418/RCCB-tripping-after-change-of-supply. if it is I would suggest our friend leaves things well alone and calls an electrician.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#18

Re: Three Phase Wires in One Pole of RCCB

05/11/2017 8:28 AM

BANG !

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adreasler (2); Andrew Westman (2); cuba_pete (1); DodgySolenoid (2); horace40 (1); jack of all trades (1); James Stewart (1); Kilowatt0 (1); luyombya (1); North of 60 (3); PWSlack (3); RAMConsult (1); SolarEagle (2); sriram1988 (1); TonyS (1)

Previous in Forum: Residential Wiring   Next in Forum: RCCB Tripping After Change of Supply

Advertisement