Anonymous Poster #1

Synchronized Power Plant to Grid Station

05/20/2017 2:15 PM

Hi,

I want to know if there is 132kv line from power plant (combine cycle gas fired ) and its Grid station to the power purchaser grid station 132kv 50hz (GIS) and i am going to synch adding power plant to the system, so

1.first I get backfeed through line from power purchaser gird station GIS to the power plant grid station.

2.Then energized the 132kv side of step up 132kv/11kv transformer in grid station (power plant side) the to energize the MV 11KV bus then generators synchronized with that voltage and frequency.

3.After phase sequence and frequency matched

4.then increased the prim mover to increases the frequency (50.1 hz ) to transfer the power to the power purchaser right ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: synchronized power plant to grid station

05/20/2017 4:33 PM

Sure, why not?

Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#2

Re: synchronized power plant to grid station

05/21/2017 12:07 AM

Crank that sucker up to 55 Hz and show that mutha who's boss.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: synchronized power plant to grid station

05/21/2017 12:31 AM

That'll bring it to its knees in short order.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#4
In reply to #3

Re: synchronized power plant to grid station

05/21/2017 12:46 AM

You know that, and I know that, but if he doesn't know that, he shouldn't even be in a position to try.

Anyone foolish enough to come to an anonymous public forum for advice on how to run a bloody power plant deserves whatever answers he gets.

Reply
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#5

Re: synchronized power plant to grid station

05/21/2017 1:50 AM

It would be nice if we knew what the question asker's native language was, then we could back feed that through Google's Universal translator and see what he was really asking. Then the engineers here could help him.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Synchronized Power Plant to Grid Station

05/21/2017 2:54 PM

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Synchronized Power Plant to Grid Station

05/21/2017 4:00 PM

Just..no..don't do this. Consult a qualified professional immediately for assistance before doing anything. Seriously.

I shouldn't have to say this but on the off chance this is not a joke or a troll, running a power plant is a very serious affair and must be handled by trained professionals.

__________________
jack of all trades
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: Synchronized Power Plant to Grid Station

05/22/2017 7:12 AM

Comment about your numbers....

1 Correct.

2 When 11kV bus available, 11 kV/400V and 11kV/?? volt transformers must be connected to provide auxiliary power for prime mover, generator and site. Only then can genset be started and synchronized.

3 The phase sequence cannot be matched except by correct connection of busbars or cables to switchgear. Once built, prime movers only turn in one direction but generators theoretically can turn either way to change sequence. Once voltage and frequency are matched [usually 2% voltage & 0.1 Hz difference are acceptable] 11 kV breaker must be closed at right [in phase] moment in "slip cycle" using phase indicators and manual close or [usually] automatic synchronizer unit ASU.

4 Once connected, individual generators on a Grid usually have negligible effect on frequency. About 750 MW is required to change frequency of 25000 MW 50 Hz Grid by 1 Hz. Increasing the prime mover power driving generator will increase power delivered to Grid without change of frequency.

Reply
Anonymous Poster #1
#10
In reply to #8

Re: Synchronized Power Plant to Grid Station

06/05/2017 1:42 PM

thanks for the brief reply,

if we increase the primover to meet the load put on the genrators from the system which we connect then the frequency change and may be increased then the system frequency ?

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#11
In reply to #10

Re: Synchronized Power Plant to Grid Station

06/05/2017 2:00 PM

It sounds like you, anonymous grasshopper #1, may need to study on the topic a bit more before we can place the controls into your hands.

Please revert back to square one at HR, and they will provide you with a map to your next learning station.

Adding a "slave" unit onto the grid "master", does not change the frequency, although if things are misaligned as badly as you seem to intimate, there could be a sudden release of excess smoke contained within the wires and connections.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#12
In reply to #10

Re: Synchronized Power Plant to Grid Station

06/06/2017 6:05 AM

You are right to question my item 4!

Much power supply theory simplifies by assuming Grid frequency is fixed and synchronous generator theory shows that increasing prime mover power does increase electrical power delivered to Grid with fixed frequency.

Systems with a small number of generators always need a control system [originally an operator with hand controls] which keeps frequency at near 50 or 60 Hz and spreads load around generators for best operating cost.

I refer you to http://www.gridwatch.templar.co.uk.

This is a time display of UK Grid. You will find that Grid frequency varies over day within operating limits of 50 +/- 0.2 Hz with considerable load variation. Frequency change plays its part in coping with unpredictable load changes.

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#9

Re: Synchronized Power Plant to Grid Station

05/22/2017 11:27 AM

It does not have to be 50.1, but it needs to be advancing phase just slightly, so that once the indicator arm reaches TDC, and the phase lamps dim to zero, the synd lever is activated at just that moment and no other. At that point, since the voltage was previously lined up, and now the phases are aligned and in sync, and the systems are physically attached, you need to increase load on your prime mover, and ensure that your generator does not end up in motorized mode. You will need to adjust VARS to maintain the specified power factor on your output load.

__________________
If it ain't broke, don't fix it. Just build a better one.