220V Air Conditioner: How Far of a Run?

08/19/2007 2:31 PM

I need to connect a 220v / 25000 btu Air Conditioner with a 30" / 3 prong wire to a generator outlet, 220v circuit.

I am not sure what the amps are for the AC. One side of the plug has horizontal flat blade, one vertical flat blade and one round (ground) prong.

  1. How far can I run a 12/3 wire ?
  2. How far could I run a 10/3 wire?
  3. What do I do with the nuetral wire connection on the 4 prong male plug that goes into the generator?

The generator has a 4 space opening and has written in the manual " REMA 14 30."

Thank you.

__________________
There is no recall from extinction.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#1

Re: 220volt How far of a run

08/19/2007 3:09 PM

It sounds like you need to get hold of a professional engineer or technician to help you....

Something like this and with your possible lack of understanding could be dangerous to advise on...

Best to get local professional advice methinks...

John.

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#2

Re: 220volt How far of a run

08/19/2007 3:16 PM

I'd have thought it would have a wattage or current rating on it somewhere? Without that you are in the realms of guesswork...and if you are not confident/competent to measure the current consumption yourself, I'd take Electroman's advice.

Current CE regs in Europe state any electrical equipment must have voltage/wattage(or current) frequency etc clearly labelled.... surely it's similar over there?

Maybe have a look at the fuse rating that will give a clue... but not conclusive...

Good luck

Del.

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Active Contributor

Join Date: May 2007
Posts: 11
#3

Re: 220volt How far of a run

08/20/2007 3:01 AM

netmaker,

You have incomplete data, however we can only assume.The 25000 btu should be 25000 btu/hr which roughly equals 2 hp ac unit with an ampere rating of about 12A. It can be fed by a 220v ,1 ph, 60hz source. The 30"/3 prong probably refers to the length of the cord and the plug configuration attached to the ac unit.

if your load(acu) is located not too far say, less than 50 feet, then 3/c- #12 AWG THWN/THHN, or THW insulation would be sufficient to compensate the drop in voltage.The 3c - #10AWG can go even as far as 100 feet.

i would also assume that your generator is the portable type with a 4 prong male plug attached to it. i suggest that you contact a registered electrician to perform your wiring connections.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#4

Re: 220volt How far of a run

08/20/2007 7:52 AM

We'll start with this. If your plug has one horizontal blade and one vertical blade and one round (ground) blade, your electrical connector is rated 20 amps.

__________________
Eschew obfuscation.
Register to Reply
Power-User
Safety - ESD - RF Manufacturing ESD Installer

Join Date: Nov 2005
Location: Princess Anne, Maryland USA
Posts: 184
#5

Re: 220volt How far of a run

08/20/2007 8:35 AM

The Neutralis not used in this application. The ground must be hooked up.

__________________
“The problems we face cannot be solved with the same level of thinking we had when they were created” Albert Einstein
Register to Reply
Power-User
Safety - ESD - RF Manufacturing ESD Installer

Join Date: Nov 2005
Location: Princess Anne, Maryland USA
Posts: 184
#6
In reply to #5

Re: 220volt How far of a run

08/20/2007 9:15 AM

To elaborate on my answer; Since the AC unit has a three prong plug, The ground (round or Semi round prong) is an equipment ground only. It is not a current carrying conductor, except in fault conditions. Therefore it is not required to be an insulated conductor. You can actually use 12/2 or 10/2 NMB, or UF Cable. (12/3, or 10/3 SJ, or SO Type Cable.) My point is you only need 3 conductors. If 4 conductor wire is used the ground from the device must be bonded with the box in the event a metallic box is used. The insulated (white ) neutral should be capped off. (unused.)

If a female plug end is used I would recommend only using three conductor cable anyway.

__________________
“The problems we face cannot be solved with the same level of thinking we had when they were created” Albert Einstein
Register to Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#7

Re: 220V Air Conditioner: How Far of a Run?

08/20/2007 9:27 AM

Can you get nameplate data off your AC? Or a model number? If so, the FLA should be on the nameplate or maybe it can be found on the internet. With that info, I can give maximum distance that your wire length is to be to provide voltage to your AC allowing for voltage drop.

__________________
Eschew obfuscation.
Register to Reply
Guru

Join Date: Mar 2007
Location: Cajun Country , USA
Posts: 1498
Good Answers: 23
#8

Re: 220V Air Conditioner: How Far of a Run?

08/20/2007 5:46 PM

Hello All,

I have found that the AC is 20 AMP 220/v .

I have a 4 prong lock type MALE connector to fit the 6500watt gen set. It has a 250v 20 amp breaker built in.

I was told to use a 12/3 or a 10/2 wire.

I need to get to the AC plug , which when passed through a hole in the window and is 30" long. The gen set will sit outside and will be require no more than 15' of wire to make the connection.

I found out from the instructions in the packet how to disgard the 4th wire on the male 4 prong plug.

The female plug is 3 wire.

All I need to know now is:

Can I span 15' with 12/3 or do I need a 10/2 or 10/3.

Thank you all.

__________________
There is no recall from extinction.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: Cajun Country , USA
Posts: 1498
Good Answers: 23
#9

Re: 220V Air Conditioner: How Far of a Run?

08/20/2007 5:53 PM

To All,

I found I have a 20 amp, 220v AC unit.

I also know what to do with either a 10/2, 10/3 or 12/3 wire to make the connection to the Generator set ( how to wire the male and female plugs).

Now, all I need to know is;

which of these wires can I run 15' to complete the connection: 10/2, 10/3 or 12/3

Thank you. netmaker

__________________
There is no recall from extinction.
Register to Reply
Power-User
Safety - ESD - RF Manufacturing ESD Installer

Join Date: Nov 2005
Location: Princess Anne, Maryland USA
Posts: 184
#10
In reply to #9

Re: 220V Air Conditioner: How Far of a Run?

08/21/2007 6:03 AM

12/3 is all that is required. (20 amp)

__________________
“The problems we face cannot be solved with the same level of thinking we had when they were created” Albert Einstein
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: Cajun Country , USA
Posts: 1498
Good Answers: 23
#11

Re: 220V Air Conditioner: How Far of a Run?

08/21/2007 8:47 AM

12/3 it is.

Connections made and gen set runs everything as expected..........

........now we are ready again for whatever the season brings us, which I hope is no more than a rain squall!

Thanks to all.

netmaker

__________________
There is no recall from extinction.
Register to Reply
Anonymous Poster
#12

Re: Air Conditioner: How Far of a Run?

08/23/2007 10:44 AM

Please NOTE; In the USA the cord cap that you described is a 110-120 vac plug. Not a 208-220vac plug. If both blades were horizontal then it would be a 208-220vac plug.

One side of the plug has horizontal flat blade Just makes it a 20amp cord cap. This is to prevent you from inserting it into a 110-120vac 15 amp receptacle and overloading the circuit.

one vertical flat blade 110-120vac

and one round (ground) prong

If the run is in conduit I would pull the extra ungrounded conductor out, be sure to bond all of the metallic portions (including any switches and receptacles) of the raceways, boxes, and devices with the ground wire (green).

If cost is not an issue I would use #10 wire as it has a less resistance and a better ability to dissipate heat (but #12 will suffice).

The ungrounded conductor (the wire coming off of the breaker) hooks up to the brass color screw. The white conductor (by code if smaller than #6 must be white or gray) goes to the white screw, even though the neutral is known as the grounded conductor it should not be hooked up to ground at any point in the circuit, but should go to the panel neutral bus bar (at the panel box where the service first enters the house the neutral bus bar will be bonded to ground) . If you only have one Panel Box then you may just have one common bus-bar (with white, green, or bare conductors on them).

BTW; I am an electrical inspector for a larger county in California (so thats what I would expect to see).

As far as length of run if you are going less than a hundred feet the voltage drop would be insignificant.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

addun (1); Anonymous Poster (1); Electroman (1); jowens (3); Kyoto (2); netmaker (3); user-deleted-1105 (1)

Previous in Forum: bus bar ratings   Next in Forum: SOT Markings

Advertisement