Exhaust fan sizing

08/29/2007 10:38 PM

Hi,

Need some help urgently. We have a room about the size of 15m (L) X 5m (W) X 3m (H) that runs a process which releases certain odour. We want to exhaust the air out of the room so that it is odourless in around 15 mins. How should I size the exhaust fans and ducting for this purpose?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Exhaust fan sizing

08/30/2007 5:39 AM

Consider also:

  • Containing the odour inside the process equipment
  • Venting the odour to the outside of the room using suitable ducting
  • Opening the windows
  • Demolishing the room walls.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2007
Location: The cigarette-stained drunkard living in the cardboard box outside Marks & Sparks delivery entrance, Eastgate Shopping Centre, Basildon.
Posts: 487
#2

Re: Exhaust fan sizing

08/30/2007 5:46 AM

Damn! Evicted again! I was getting used to dossing in there.

__________________
Essex jobs for Essex yobs! <Burp>.
Register to Reply
Power-User
Safety - Hazmat - Environmental, Safety & Health Manager Hobbies - Musician - Theremin (That about says it all...)

Join Date: May 2006
Posts: 289
Good Answers: 19
#3

Re: Exhaust fan sizing

08/30/2007 3:05 PM

When utilizing exhaust ventilation to remove odorous (non-hazardous) contaminants, it is always a good idea to have the exhaust fan's intake as close to the point of odor emanation as possible, ideally, enclosing the process itself inside of a "hood" (Think college chem class). Alternatively, if the process is taking place in a vessel or container, then a slotted intake should be configured, to increase the air velocity at the intake point, and improve capture efficiency. (A good reference manual is Industrial Ventilation: A Manual of Recommended Practice, by the ACGIH. )

Be aware, running general exhaust ventilation at 4 air changes per hour will be costly with respect to the energy required to "condition" the makeup air (that replaces the odorous air being exhausted.)

That being said, based upon your room dimensions, you are looking for an exhaust system that can move 900 M3/hour, or 15 M3/minute.

That's about 530 CFM (cubic feet per minute). In order to keep the velocity up, you will probably want to utilize ductwork < 8" in diameter.

Register to Reply
Participant

Join Date: Jul 2007
Location: Houston TX
Posts: 1
#5
In reply to #3

Re: Exhaust fan sizing

08/31/2007 9:20 AM

As a lab designer, I can tell you that 4 AC per hour will not remove an odor. Base minimum design is 6 AC / hr when all odor is captured in a hood. We regularly go as high as 12 AC/hr for certain circumstances.

Best practice is to contain the odor and use 100 FPM velocity across any opening in the enclosure.

This is a pretty complex design issue and should be addressed by a professional if the odor is offensive or hazardous.

RDMJR

__________________
Design/Build of Advanced Technology / Clean space / Precision temperature and humidity and Laboratory spaces
Register to Reply
Power-User
Safety - Hazmat - Environmental, Safety & Health Manager Hobbies - Musician - Theremin (That about says it all...)

Join Date: May 2006
Posts: 289
Good Answers: 19
#7
In reply to #5

Re: Exhaust fan sizing

08/31/2007 11:31 AM

"I can tell you that 4 AC per hour will not remove an odor."

That is a pretty strong blanket statement...

I believe that a few factors would need to be considered, such as the odor threshold of the substance in question, the volume of substance released, and its rate of release/evaporation/volatization.

By the way, 4 ACH is considered the "standard" when calculating exhaust ventilation requirements for safe asbestos removal, in accordance with US regulations.

Register to Reply
Power-User
Safety - ESD - RF Manufacturing ESD Installer

Join Date: Nov 2005
Location: Princess Anne, Maryland USA
Posts: 184
#8
In reply to #3

Re: Exhaust fan sizing

08/31/2007 3:09 PM

Don't forget to install an intake duct of at least the same diameter.

(Sorry I didn't read all the posts before I had to spout off.)

__________________
“The problems we face cannot be solved with the same level of thinking we had when they were created” Albert Einstein
Register to Reply
Power-User

Join Date: May 2007
Posts: 101
#4

Re: Exhaust fan sizing

08/31/2007 7:54 AM

Indeed, don't forget the make-up air! Without the make-up air a vacuum will be created in the room and you may not be able to open the door to the room. Make sure the suction side of the make-up air is not close to the discharge side of the exhaust fan.

Register to Reply
Associate
Safety - Hazmat - PHA / HAZOP Facilitator Engineering Fields - Chemical Engineering - Principal Engineer Engineering Fields - Piping Design Engineering - Chemical Process Engineer

Join Date: Mar 2006
Location: Billings, MT, USA
Posts: 54
#6
In reply to #4

Re: Exhaust fan sizing

08/31/2007 10:45 AM

All good points above, but you should also characterize the odor causing substance to see if it generally wants to go up or down (specific density relative to air).

I completed a similar design for a pesticide company recently and we used less than 2 air changes per hour, but we located all of the inlet ducts in a way that the source was well protected and local air velocities were high enough to keep the fumes in the air ducts. We also utilized heavy plastic curtains to enclose some of the equipment. The problem here was a filling operation where the chemical was filling plastic jugs, so we "enclosed" the filling stations with the plastic curtains.

The largest problem on that project was that it is located in Montana and the conditioned air had to be heated (a lot!) in the winter. The return air issue can be significant as someone else has already pointed out.

Stephan

__________________
Do what you will whilst harming none.
Register to Reply
Commentator

Join Date: Apr 2005
Location: Phoenix, AZ
Posts: 82
Good Answers: 3
#9

Re: Exhaust fan sizing

09/01/2007 1:21 AM

You have 225 cubic meters of air to displace. It all depends on what chemical you are using as to removing the smell. Is it oil based, water based, alcohol based, then you have to determine what residual volume you have left in the room, and then how much volume of air flowing over it will entrain it in the air stream. It is a simple question, but not a simple answer. Will you have to entrain water in your airflow to lift the offending chemical? Not an easy answer.

Register to Reply
Active Contributor

Join Date: Apr 2006
Posts: 13
#10

Re: Exhaust fan sizing

09/01/2007 6:08 AM

I don't know if you have hoods over the process you have mentioned. Hoods have different design criteria. Depending of what kind of exhaust system you have, the size of fan is dependent of the volume of air being exhausted. It also depends on whether the entire room is air conditioned or not. If it is air conditioned, it complicates the matter a little bit as you would not want to be exhausting conditioned air. This would be expensive. Consider a system like a kitchen hood exhaust. There is the exhaust and the make up air. The capture velocity is critical here, otherwise you won't be able to control the odor. There would be always odor migration to the other parts of the room or even outside of the room especially if the fresh air is greater that the exhaust air. Consider a negative pressure of around ten percent of exhaust air. For fan motor sizing, compute the pressure losses imposed by the system and size the motor adequately for the require air flow.