good day people,
I am confront with a flow induced vibration problem in a cross flow tube bundle heat exchanger. (Air/Air)
Including is a brief explanation of the problem and history with some illustrations.
And what I am looking for are people that may had experience or are familiar with this phenomenon. Basically feedback to this fix or at least to reinforce that I am on the right track. (with suggestions)
Some of the criteria is the Air flow has to remain the same, with the fix being applied to the xchangers itself.
And with the pool of talent here at this point what I would like to avoid (but I much as it may interest me) is lectures on "Vorticity Shedding and/or Acoustic Resonance Mechanisms" or Numerical Procedure with how this bundle should have been design, because this is what we have to work with being this a small company, big or small it all has to do with economics, i.e. "bottom line".
Attached are the Illustrations, hope they are legible.:
fig. 1
TUBE BUNDLE BASIC DESIGN
TOLERANCES NOT APPLIED FOR
DESCRIPTIVE PURPOSED ONLY
fig. 2
PROPOSE SOLUTION BROUGHT TO ME.
I have reservations on this
being that this is not solving
the core problem of vibrations
fig. 3
MY PROPOSAL TO ADDRESS PROBLEM
(considering that the company has been
doing this for a number of years, even
though I felt uncomfortable, I can't
assume they tried this, they had and
they had see fig. 5) Installation of saddle
reinforcement strips to firm up tubes
and reduce the movement from vibration
and still leave room for thermal expansion
SEE FIG 4
fig. 4
INSTALLATION OF SADDLES
This would contain the tubes
in 2 axis leaving the 3rd axis
for expansion
fig. 5
COMPANY'S INITIAL FIX
They installed cross tube (tack welded).
And it work for approx. 6 weeks
And then the vibration started again.
I believe they were on the right track.
but this only firmed up the tube in
only one axis
Looking forward to your comments.

"Almost" Good Answers: