What size photovoltaic panel (watts and volts) and what size inverter would be used to power a 100 watt 120 volt AC appliance (no motor involved). I only need it running when the sun is out, I don't want a battery backup. Will the inverter start the appliance when enough watts from the sun is available or do I need a volt/watt/amp sensor to turn on a switch/relay?

Register to Reply
Pathfinder Tags: inverter photovoltaic
User-tagged by 2 users
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15620
Good Answers: 986
#1

Re: Photovoltaics and Inverter

11/27/2017 2:12 PM

I would not bother at all with an inverter. I would bypass the AC/DC power supply in this motorless AC appliance. For fun I would design a boost/buck DC-DC converter between the photovoltaics and the load. The converter would be capable of driving the load from the light level reaching the photovoltaics an hour after sunrise. (I always wanted to use what I learned in that class.) To size the photovoltaic array will require some idea of how much sunlight you get wherever you are and what folliage or other shading complications you have.

In short, you don't give us enough information to provide even a WAG.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Photovoltaics and Inverter

11/27/2017 2:45 PM

What sort of appliance is it?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Mar 2011
Posts: 17
#3
In reply to #2

Re: Photovoltaics and Inverter

11/27/2017 4:32 PM

the appliance is a thermoelectric aquarium cooler probably DC but it specs a 120 v ac plug. redfords comments are probably good, just go dc and it will work when the sun comes up? I do have a DC pump in the system, needs to be pumping before the cooler turns on?

Register to Reply
3
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#5
In reply to #3

Re: Photovoltaics and Inverter

11/27/2017 9:31 PM

That's redfred. What's the story about an aquarium cooler, I've only experienced aquarium heaters?

Anyway, whether heating or cooling, a sensible goal is to achieve the desired amount of heat transfer during the day, with an integrated total, rather than all at once during the peak noontime sun. And rely on the tank water's thermal mass to get you through the day and night.

Below are 5-minute data points from my solar roof, over 9 successive days. Some are good solar days, others are disasters, like the cloudy 'yellow-squares' day.

Is yours a mission-critical task with no alternate power source? You have to be prepared for those low or nearly-zero-output solar days.

The above plot is at the annual optimum time, in mid-spring. Below, here's a sunny day in mid winter:

Note how the solar power fails to get above 6kW, and drops precipitously after 1pm, killing the normal symmetrical daytime curve. That's because mid-Dec has a low winter sun, which goes behind pine trees some 400-feet away. Only 24kWh produced in this full-sun winter day, compared to 62kWh in the spring time peak.

Some have suggested adding battery capability to your system, these curves help to show why you may need this.

__________________
Thanks, Win
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15620
Good Answers: 986
#6
In reply to #3

Re: Photovoltaics and Inverter

11/27/2017 10:45 PM

An aquarium cooler you say. This implies two helpful ideas to me.

First, you live in a predominantly warm climate where seasonal changes in sunlight will be minimal. This simplifies some of the calculations. It does unfortunately imply that vegetation shading might become a future problem.

Second, the thermal energy source you wish to remove from this aquarium predominantly comes from the sun you wish to also power your cooling system. Thus more light produces more aquarium heating and more photo-voltaic (PV) power simultaneously. I doubt most of the solar heating transfer happens from direct sunlight absorption by the water so some lag in the heating transfer will occur. PV energy will probably have to be stored in some fashion to continue cooling as other objects (rocks, sand, fish) continue to dump heat into the water. A rechargeable battery does immediately come to mind but daily charging and discharging implies high cycle counts. Lithium ion batteries have a 500-2000 cycle count range, thus a 1.5 to 5 year lifetime for a battery may be a problem. I wonder if an ultra-capacitor might fit this bill?

It's fun to extrapolate from minimal information. It's rarely accurate but it sure is fun.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
3
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9939
Good Answers: 1148
#4

Re: Photovoltaics and Inverter

11/27/2017 5:50 PM

100 watts at 120 volts is a resistor of value 14400/100 or 144 ohms. To find the amount of power delivered to a resistive load, you need to consider the load and source using load lines and the voltage and current characteristics of the source.

A photovoltaic device produces almost constant voltage but the current produced is proportional to illumination. To see the relationship, see this calculator.

http://www.pveducation.org/pvcdrom/effect-of-light-intensity

An example load line vs photovoltaic output is shown below:

https://www.mouser.in/applications/sophisticated-management-solar-energy/

So with your resistive load, the output voltage will vary directly proportional to illumination.

Solar illumination varies through the day, mainly because of absorption in the atmosphere (see Beer's law).

https://en.wikipedia.org/wiki/Beer%E2%80%93Lambert_law

https://www.cat.com/en_GB/articles/white-paper-hybrid-microgrids-the-time-is-now.html

Assuming your "appliance" can accept up to 120 volts, the voltage you can expect during any other time of the day if you connect it directly to the solar panel would follow the plot above, scaled for a maximum of 120 volts.

So if you want it to work all day and not just at noon, you need some kind of voltage regulator and a large enough array to produce enough power in as early in the morning and as late in the afternoon as you wish it to operate and limit the power at midday. The sun furnishes about 1000 W per square meter (at midday), but with the efficiency of solar cells you can expect about 150 W per square meter.

The daily variation is one reason to use batteries. A smaller solar panel could be used to provide average power for the day, and the solar panel output could still be used to switch on your appliance when the sun is out.

Register to Reply Good Answer (Score 3)
2
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#8
In reply to #4

Re: Photovoltaics and Inverter

11/28/2017 4:08 AM

GA to Rixter for a very comprehensive answer.

My thoughts for the OP

To make this work effectively you really need to consider a battery both as a buffer for the incoming solar energy and for times of low insolation.

A 100 watt resistive load is going to draw around 8 amps at 12.5v or around 10 amps if driven via an inverter.

A 200 watt inverter would be quite adequate for the job, and a minimum 100 Ah battery would give you reliability of supply on all but the worst of overcast days without dipping below 50% SOC.

You may be able to get away with a cheaper modified wave inverter rather than a pure sine wave type, but be aware that some power packs (as I assume from your comment in #3 this device uses) do not work well with modified wave supplies.

Taking an industry standard 5 peak sun hours per day, and also allowing that you may need less cooling on colder days and outside of PSH times, you could expect to use roughly 1000Wh per 8 hr day. To replace this power you would require a minimum 300 watts of photovoltaics in an unshaded location facing the Equator and preferably pitched at latitude angle.

A regulator would be essential and I would suggest that you use an MPPT type in preference to a series or PWM type as it will provide a higher charging current for the same wattage PV array and it will allow use of a higher voltage array to both limit voltage drop and provide better performance at shoulder sun times when a series regulator would be limiting input due to impedance mismatch pulling the instantaneous I/V point right off the knee.

While an MPPT regulator would run the device without the battery, you will find that operation on all but clear days will be sporadic, and possibly non existent on highly overcast days - this may suit your purposes as you may need no cooling during those periods.

If using a 12v battery setup then PVs should be 24v minimum feeding an MPPT regulator with output voltage sized for the battery being used. The regulator should be positioned close to the battery to limit line losses.

If not using a battery, then you would be better to stick to a PV array of the same nominal voltage as the inverter input. Likewise if using a PWM regulator, the PV nominal voltage must be the same as the battery or inverter.

You would need a relay to turn the system on and off, and this could be achieved with the relay coil connected directly across the PV array with a delayed off feature to cater for clouds etc.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#9
In reply to #8

Re: Photovoltaics and Inverter

11/28/2017 7:57 AM

The <...relay coil connected directly across the PV array with a delayed off feature to cater for clouds...> would need a battery to sustain the relay and run the timer until it expires. Otherwise it is the clouds that determine what is happening...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#11
In reply to #9

Re: Photovoltaics and Inverter

11/28/2017 5:03 PM

The PV voltage doesn't fall much when insolation is not optimum, it's the current that drops right off (Rixter's 2nd statement also makes that point), but the relay draws little enough current that it would remain energised while there is daylight available.

The point of my comment - which I unfortunately didn't make very clearly - was that the delay off feature would maintain the appliance from the battery (which I did recommend to be used) while insolation is low, but that by having a delay off feature, it will turn off after a set period of lack of illumination.

I think my other comment adequately covers your correct point of the clouds controlling the cooling if no battery is used "While an MPPT regulator would run the device without the battery, you will find that operation on all but clear days will be sporadic, and possibly non existent on highly overcast days - this may suit your purposes as you may need no cooling during those periods."

As an aside, I use a small pcb relay connected directly across a nominal 12v PV array to run a cooling fan for a larger relay that controls input from those panels. The fan, which is powered from a battery, runs continuously during daylight hours which is when the relay requires cooling. When the PV current drops below about 20mA, the PCB relay drops out and the fan stops. The pick up and release voltages of the relay are about 7.5 and 5v respectively, and that is easily maintained by the array even in low light conditions.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#14
In reply to #4

Re: Photovoltaics and Inverter

12/07/2017 12:30 PM

Well stated. There are some other GA's here as well.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33399
Good Answers: 1817
#7

Re: Photovoltaics and Inverter

11/28/2017 12:26 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5833
Good Answers: 322
#10
In reply to #7

Re: Photovoltaics and Inverter

11/28/2017 2:02 PM

Add one of these:-

https://www.ebay.com/p/Thermoelectric-Peltier-Refrigeration-Cooling-System-Kit-Cooler-Double-Fan-120w/2112254968?iid=292198181249

to SEs solar panel and you're almost done. You just need some copper piping which draws water out of the top of the tank an injects it back into the bottom: let convection replace the pump.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru

Join Date: Apr 2011
Posts: 8010
Good Answers: 286
#12

Re: Photovoltaics and Inverter

11/28/2017 5:58 PM

Whats the temperature and humidity like in your location? How big is the tank? What temperature reduction are you attempting?

TEC/Peltier coolers are on the inefficient end of the various cooling technologies available. Depending on your local conditions and what you are attempting, using a small vapor compression system (reclaimed from refrigerator?)or possibly indirect evaporative cooling might be worth consideration.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#13

Re: Photovoltaics and Inverter

12/07/2017 12:27 PM

Use switches/relays to control this load. It makes sense to do so.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brian nuclear (1); James Stewart (2); PWSlack (1); Randall (1); redfred (2); Rixter (1); SolarEagle (1); spades (2); Tornado (1); truth is not a compromise (1); Winfield Hill (1)

Previous in Forum: Fence Requirement For The Oil-Filled Power Transformers   Next in Forum: Isolator Switch

Advertisement