Anonymous Poster #1

Flow Meter

12/11/2017 3:18 AM

What causes a flow meter to run up to a maximum flow rate with pump start up and then reduce to zero, immediately while pump is still running and delivering flow of material physically into the tank in the plant.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Mr

12/11/2017 3:28 AM

A fault.

Go on:

  • Tell the forum what type of flowmeter it is!
  • Tell the forum its size, its age, its manufacturer!
  • Tell the forum about the nature and name of the <...material...>, its temperature and pressure!
  • Tell the forum about the ambient conditions!
  • Tell the forum about the pump, the key dimensions and features of the piping installation and the difference in elevation between the <...material...>'s start and end points!
  • Tell the forum about the way this equipment is operated!

Pretty-please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#2

Re: Mr

12/11/2017 5:21 AM

Sounds like it's measuring the differential flow (relative to previous reading) rather than actual flow.

In a way, a bit like trying to use a DC meter to measure AC current/voltage.

I suspect that the meter also indicates maximum negative flow rate when turn pump off.

Have fun resolving this.

__________________
Just an Engineer from the land down under.
Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Mr

12/11/2017 7:50 AM

Without knowing any more about it, my guess is that on startup, there is little resistance to the flow and maybe the steady state flow rate is low but not zero when back pressure builds up.

Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#4
In reply to #3

Re: Mr

12/11/2017 8:33 AM

So, that smiley face is to indicate you aren't actually serious, right?

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: Mr

12/11/2017 8:46 AM

<...Without knowing any more about it...smiley face...> What good would crying do, though (rhetorical question - NNTR)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#9
In reply to #4

Re: Mr

12/11/2017 10:26 AM

No, actually I was envisioning some sort of liquid filling empty pipes on startup ahead of some constriction downstream that limits the flow when the "product" reaches it. There was not much information provided in the original question, leaving a lot to the imagination.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10
In reply to #9

Re: Mr

12/11/2017 10:47 AM

I'm with you.

Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#12
In reply to #9

Re: Mr

12/11/2017 11:53 AM

Ah, okay. I can see where you are coming from. The meter would have to be poorly chosen or functioning improperly to read zero flow with the tank being filled at a rate not deviating enough from normal to be noteworthy.

If it wasn't filling the tank, any obstruction that acted like an overfill prevention valve with the pipe as the tank, could allow air to be pushed out initially and then stop flow. Simply have a fair amount of air caught in a long closed line would likely yield oscillation.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#5

Re: Mr

12/11/2017 8:44 AM

If this is a dp flow meter, initial maximum indication may be due to sudden increase in pressure reaching the first leg before the second and the inertia within the device.

The subsequent reduction to zero is because the flow meter is broken/in need of maintenance, or severely in need of calibration, or of insufficient resolution, or improperly installed, or not actually a flow meter after all.

Maybe this flow meter isn't even attached to the system you think it monitors. Perhaps the jump and return to zero is just coincidental with operation of a nearby system and has nothing to do with the fluid flow into the tank you reference.

We can't tell from this end. You have left us fairly blind.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7

Re: Mr

12/11/2017 9:16 AM

It's real. You forgot about the accumulator that's between the flow meter and the orifice (nozzle) that feeds the tank.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Mr

12/11/2017 9:19 AM

...and the closed valve upstream of the pump...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#13
In reply to #7

Re: Mr

12/11/2017 11:55 AM

Doesn't account for zero flow shortly after start.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11

Re: Mr

12/11/2017 11:31 AM

It would be indicative that you have a valve closed past the flowmeter location....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#14
In reply to #11

Re: Mr

12/11/2017 11:56 AM

Except the OP notes the tank is filling.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#15
In reply to #14

Re: Mr

12/11/2017 12:43 PM

The he's probably using the wrong type of flow meter for the application....

https://www.keyence.com/ss/products/process/flowknowledge/sources/trouble_02.jsp

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#16

Re: Mr

12/11/2017 4:56 PM

It broke.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#17

Re: Flow Meter

12/12/2017 12:37 AM

My guess is the feeder pipe is a different one than the one where the flowmeter is on.

Both are empty at start and then most of the flow goes through the other pipe.

__________________
Common Sense Dictates
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#18
In reply to #17

Re: Flow Meter

12/12/2017 2:12 AM

That doesn't make even the tiniest shred of sense.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Off Topic
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#20
In reply to #18

Re: Flow Meter

12/12/2017 7:05 AM

Now, that is your problem!

__________________
Common Sense Dictates
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#23
In reply to #20

Re: Flow Meter

12/12/2017 8:54 AM

No, the problem is that neither of you are communicating your thoughts well enough for the other to understand your concept.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#26
In reply to #23

Re: Flow Meter

12/12/2017 10:33 PM

Tornado thought I have no idea and I think he expressed that well enough! There is no real misunderstanding more a dislike!

__________________
Common Sense Dictates
Reply Off Topic (Score 5)
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#19

Re: Flow Meter

12/12/2017 4:49 AM

This is my guess ( it's probably wrong ) my guess is about as good as anyone's so what the fudge.

The pump is a two stage diaphragm, there is a faulty check valve before the pump. When the pump starts up, the pipe is full of fluid and the check valve is open, the gauge reads high. Then the check valve sticks closed, the viscosity of the fluid drops after the pump and flow still comes out of the pipe because the pump is still pumping on it's exit diaphragm, but the gauge drops to zero because this has been going on for so long the gauge is worn out and will only indicate full or nothing at all. When inlet side pressure finally builds up enough, the check valve opens, the gauge reads full, the viscosity in the line is high and flow continues out of the pipe. This process repeates itself over and over.

Remember this is just a guess and I'm probably wrong, again, as usual.

Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#21
In reply to #19

Re: Flow Meter

12/12/2017 7:08 AM

We do not know what is pumped and how and not even why, so any guess is good until we have more details!

__________________
Common Sense Dictates
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22
In reply to #21

Re: Flow Meter

12/12/2017 7:50 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#25
In reply to #19

Re: Flow Meter

12/12/2017 9:38 AM

pair o' ducks.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#24

Re: Flow Meter

12/12/2017 9:38 AM

Magnetic flow meter electrodes (inside the pipe) are going dry after start, pipe not full

Incorrectly operating pump contact, used to clamp magnetic flow meter output to zero when pump not running, usually used when air is likely in the meter body. If contact closes while running, meter output goes to zero.

Bad magnetic flow meter transmitter (the box with all of the electronics), or less likely open / un-grounded circuit on one of the excitation coils (wrapping the pipe).

Reply
Power-User

Join Date: May 2008
Posts: 136
Good Answers: 2
#27

Re: Flow Meter

12/13/2017 7:11 AM

I'd suggest some scenario which may be resulted in the problem you've described:

Most flow meters (or at least those I've come across) work according to a certain working pressure in a process, and when this pressure goes below that value, then the meter would become zero... That's why you need to check if there is a pressure relief valve(s) in your process being damaged or leaked out a severely ..

ـــــــــــــــــــــــــــــــــــــــــــــ

__________________
Just live and .. Learn!!
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#28
In reply to #27

Re: Flow Meter

12/13/2017 10:13 AM

It remains to be seen what type of flowmeter we are talking about. It could even be in the set-up of the meters electronic parameters (if electronic), where a low threshold was set too high, for example, with a magmeter.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#29
In reply to #28

Re: Flow Meter

12/14/2017 5:48 AM

Agree with you. Until we know the flowmeter operating principals we are all shooting blind.

Initial thought was floating earth with capacitive effect. Initial (change in) flow shows as reading but then steady state flow indicates zero/null. That's why I suggested OP to provide meter observations at pump stop, which I suspect would be a negative flow indication.

Anyway, it's their problem to solve. We can only hope that the collective responses here have been of some assistance to them.

__________________
Just an Engineer from the land down under.
Reply
Power-User

Join Date: May 2008
Posts: 136
Good Answers: 2
#30
In reply to #28

Re: Flow Meter

12/14/2017 7:08 AM

Yes,.. I suppose it as a variable area flowmeter which has a constant pressure drop,... and nevertheless,.. without more information from the OP, all we do is a kind of mere guessing!!

What I can say here that I experienced something similar to the OP's issue, and the the flowmeter was Krohne-made,.. We've found out that relief valve -directly past the feeding pump- is responsible for that problem..

__________________
Just live and .. Learn!!
Reply
Member

Join Date: Dec 2017
Posts: 7
#31

Re: Flow Meter

12/21/2017 5:39 PM

Perhaps the line is empty, when pump starts it's against zero head so the fluid travels rapidly to fill the pipe then the pump runs out of head or it meets a closed valve and the velocity drops to zero.

That's my guess for what it's worth

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#32

Re: Flow Meter

12/27/2017 4:55 PM

Is there a prize for getting the right answer?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#33
In reply to #32

Re: Flow Meter

12/27/2017 5:37 PM

Yes, every ESO failure will be sent to your door step.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Reply to Forum Thread 33 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ali18 (2); IdeaSmith (4); James Stewart (3); Just an Engineer (2); lyn (1); PWSlack (5); redfred (3); Rixter (2); Roy Matson (1); rwilliams (1); SolarEagle (2); tonyhemet (1); Tornado (1); truth is not a compromise (5)