There is a differential pressure permissive that can inhibit a gas turbine/generator start-up if the differential is detected above a set limit in software.
The purpose of the dp switch logic is that if there is a substantial gas leak in the gas turbine engine compartment, that the dp will increase between that compartment and the generator compartment by x amount.
Does anyone here have an idea what that amount should be where there could be an ignition hazard inside the generator compartment?
The value set in our software is lower than low. It is so low, one can bump into the switch hard-mounted on the wall, and the vibration will engage the switch.
I am thinking this should never be lower than about 100 Pa (not kPa), or about 1 mbar. The switch sensing is calibrated in inches of water, and it is a small number. Our lead instrument tech thinks this number is so ridiculously low, that the thing should never allow an engine start. I concur.