Lightning Protection for Water Steel Tanks and Zone of Protection

01/18/2018 7:11 AM

We have steel water tank with 100m diameter and 23m height above the ground level. Also, we have two rooms 40m and 46m far from the steel tank. The inquiries are:

1- Should I make air terminal for lightning protection above the steel tank or itself protected as the steel sheet of tanks have thickness not less than 5mm and only bonded the tank bottom sheets to ground terminal.

2- Should I make lightning protection for those two concrete rooms (each 6m height and far from tank 40m, 46m respectively) or they locate in the protection zone of tank and don’t need lightning protection.

Thank for all in advance

Register to Reply
Pathfinder Tags: lightning
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: lightning protection for water steel tanks and zone of protection

01/18/2018 7:40 AM

The only way to answer the question is to review and apply the applicable standards for lightning protection in whatever location these structures are on the planet. The standard cannot be seen from here, and the location has been withheld from the forum for some reason that cannot be determined. The contents of the tank influence the outcome: the approach might differ if the tank were holding aviation spirit as opposed to water, for example.

The only way of protecting structures from lightning, in principle, is to give the lightning a preferable path that makes the lightning go nowhere near the structures. Typically, it is an earth electrode pointing up to the sky; in the UK, radio masts, mobile telephone masts and church spires are typically used in this way, giving a measure of protection to the other structures in the immediate vicinity. However the forum has nothing to go on about the location of anything suitable in the immediate area of the chosen structures.

Therefore any form of useful reply to the original question is going to be somewhat unlikely.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Lightning Protection for Water Steel Tanks and Zone of Protection

01/18/2018 11:41 AM

Click HERE

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#3

Re: Lightning Protection for Water Steel Tanks and Zone of Protection

01/18/2018 12:17 PM

Why not go full tilt, and protect above the tank with lightning rod, and copper rope.

Also protect the buildings, depending on what is worth anything to you.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#4

Re: Lightning Protection for Water Steel Tanks and Zone of Protection

01/18/2018 5:03 PM

My understanding is that air terminals provide roughly a 30 degree cone of protection around them. It seems that a 23 meter high air terminal will not provide much protection to structures about twice the distance away.

You will find a number of standards at the bottom of the Wikipedia page

https://en.wikipedia.org/wiki/Lightning_rod

Good luck with your quest.

Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#5

Re: Lightning Protection for Water Steel Tanks and Zone of Protection

01/19/2018 10:34 AM

As long as the tank is well grounded, it is plenty of protection for itself. No action should be needed. As to the rooms some distance away, same answer - If you are worried, sink ground rods along the connecting pipes and ground the pipes.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Lightning Protection for Water Steel Tanks and Zone of Protection

01/19/2018 11:26 AM

If you intend to follow NFPA 780/2012 Chapter 5 Protection for Miscellaneous Structures and Special Occupancies 5.4 Metal Towers and Tanks “shall require only bonding to grounding electrodes” if that have a metal thickness of 4.8 mm (3⁄16 in.) or greater shall require only connection to the lightning protection system by welding, brazing or plates having a surface contact area of not less than 5200 mm2 (8 in.2).

However, the other two structures are too far located –in my opinion. Following rolling sphere method, the horizontal protected distance has to be [in excel language]:

d=sqrt(h1*(2*R-h1))-sqrt(h2*(2*R-h2)) where:

d = horizontal protected distance (m or ft)

h1 = height of the higher roof (m or ft)[23 m]

R = rolling sphere striking distance radius (m or ft)

h2 = height of the lower roof (top of the object)(m or ft) [6 m]

R<=h1-h2[17 m]

d=1.63 m only.

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Lightning Protection for Water Steel Tanks and Zone of Protection

01/19/2018 3:04 PM

Sorry.The last sentence has to be:

R>=h1-h2

For a 2.9 kA lightning peak value R=10*2.9^0.65 =20 m

Then d=4.28 m.

__________________
Julius
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jan 2008
Posts: 3
#8

Re: Lightning Protection for Water Steel Tanks and Zone of Protection

01/25/2018 5:52 AM

Thanks to all for enriching the discussion

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: