Amp Capacity of Extension Cords

01/17/2018 3:29 PM

Extension cords list the maximum length of cord based on the size of wire used and the current draw. Is house wiring taken into account? There can be 50' or more house wiring between the receptacle and the power panel. To state it a different way, will an extension cord of say #14 wire be able to carry more current when plugged in close to the power panel than 50' away from the panel?

__________________
Mr.Ron from South Ms.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#1

Re: Amp capacity of extension cords

01/17/2018 3:48 PM

14 gauge wire, when used for house wiring, is rated for 15 amps. The wiring will be connected to a breaker of no more than 15 amps rating.

If your house is wired correctly, that extension cord will get a maximum of 15 amps running through it.

Where it is plugged in to the circuit is irrelevant, once that branch exceeds 15 amps, the breaker will trip, shutting off power.

Or to put it another way, you are asking hypotheticals when the example given is already laden with practical limits, thus rendering an answer on the hypotheticals moot.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#2

Re: Amp capacity of extension cords

01/17/2018 3:49 PM

I think the ampacity of the extension cord is what is labeled on it.

Practical common sense states that there might be a little bit of volt sag if the wiring run from breaker panel to outlet is rather long compared to the shorter run outlet, yes.

The answer is Yes, but not by much.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
3
Guru
Engineering Fields - Electrical Engineering - Hmmm...

Join Date: Jul 2010
Location: Maryland
Posts: 567
Good Answers: 29
#3

Re: Amp capacity of extension cords

01/17/2018 3:59 PM

The worry with an extension cord is not the current that it can carry, but the voltage drop when it carries that current. The length of a cord does not affect the current carrying capability. 14AWG is typically used to carry up to 15 amps.

What will really determine the viability of a 14 AWG extension cord is the equipment that is used at the load end. If, when drawing 14 amps, the voltage drop is below the equipment's rated supply voltage then it may cause problems. Will your motor overheat with too low line voltage? Will your UPS trip if the line voltage drops too low? Can it cause damage to the device you are powering?

For the most part incandescent lamps don't care. Some electronic devices may not work well (a UPS is a great example), but things like phone chargers will work just fine. The surge current to start a motor may cause enough voltage drop that the motor may not start.

Register to Reply Good Answer (Score 3)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#4
In reply to #3

Re: Amp capacity of extension cords

01/17/2018 4:07 PM

Very useful information.

In my home shop, I have a fractional horsepower lathe motor, a chop saw, a table saw, air compressor, drill press, and a host of other small loads that more or less get one-at-a-time operation by me. Not a problem, at least the lathe motor does not overheat, and it runs longer than the others. All of this on a 14 gauge 100' extension cord from a wall outlet (20 A) on the back of the house.

The real problem was when I tried running my air conditioner out there. Oops! She gets the cord hot, runs hot, then shuts down (without burning down my work shed).

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#10
In reply to #4

Re: Amp capacity of extension cords

01/17/2018 6:09 PM

Maybe there's a reason the A/C unit comes with a 4' pigtail that is 10 Ga AWG?

If you get a chance, cut that 100 footer into a bunch of 15 footers (or so) and get yourself some replacement cord ends from some hardware store... remember this guy?

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#20
In reply to #10

Re: Amp capacity of extension cords

01/18/2018 11:15 AM

First of all, this is a "window" unit A/C. It has a typical three contact plug that normally gets plugged into a wall outlet (one that is rated for the amp draw of the A/C, hopefully), and you are not going to get me to mess up a perfectly good 100 footer to satisfy someone else's crazy ideas.

I will eventually get my shop wired properly, maybe. Maybe with its own meter loop.

It is really a tiny little shop building, more of a wooden storage unit. It would make a splendid fire, if I ever went completely stupid.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#21
In reply to #20

Re: Amp capacity of extension cords

01/18/2018 11:32 AM

"It is really a tiny little shop building, more of a wooden storage unit. It would make a splendid fire, if I ever went completely stupid."

For some reason I'm reminded of a story about Ozzy Osbourne. Apparently, one time when he returned home from a concert tour, he was really drunk/stoned/high/some combination of the above, and after he got home late at night, he went out back and set fire to his chicken coop. A neighbor came by, due to the unexpected bonfire, and when he laid eyes on the scene, all the neighbor had to say was, in traditional British deadpan, "So, I see you're back from the Americas."

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Amp capacity of extension cords

01/17/2018 4:08 PM

There's extension cords, and then there's extension cords.

Bottom line is how many AMPS are you trying to pull/push through that particular cord.

A light bulb and a Skil saw will put vastly different loads on the service cord.

It's no different than trying to push 5 GPM through a 1/2" water pipe and trying to push 50 GPM through that same pipe. It'll take a LOT more power to push 50 GPM through it.

Here's a handy guide:

How to Select the Right Electrical Extension Cord - The Spruce

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: Amp capacity of extension cords

01/17/2018 4:16 PM

There is definitely a voltage drop depending on length of run....as the voltage goes down the amperage goes up...the wattage demand of your device is what determines voltage amperage demand.......here is a calculator

http://www.southwire.com/support/voltage-drop-calculator.htm

http://www.ecmweb.com/code-basics/dont-let-voltage-drop-get-your-system-down

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
3
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#11
In reply to #6

Re: Amp capacity of extension cords

01/17/2018 6:14 PM

"as the voltage goes down the amperage goes up...the wattage demand of your device is what determines voltage amperage demand"..

That depends on the device -

Ohm's Law states that Amps = Volts/Resistance. This means that if you apply a specific voltage across a specific resistance then you will get a specific current flow. ie. for a purely resistive load, a 120v supply across a 144 Ohm resistance will produce a current flow of 0.833 amps This implies that if you reduce that voltage then the current will also decrease, 115v/144Ω = 0.799A

Ohm's law also states that Watts = Volts x Amps, so 120v x 0.833a = 100w.

Watts is not a constant here, it is entirely dependent on the voltage and resistance of the circuit, so if Volts decrease, then so will Amps and Watts - a "brownout" is a perfect example of this where a reduction in voltage causes your lights to dim, they don't just draw more current to produce the same original light output/wattage. Your 100w globe at 120v becomes a 90w globe at 115v.

A reactive load is different, motors will generally attempt to draw more current to compensate and thus may overheat, many commutator type motors such as in hand power tools etc may just run slower with no ill effects.

Regulated power supplies attempt to maintain their output voltage by increasing their input current draw until the voltage decreases beyond their capability to compensate.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#23
In reply to #11

Re: Amp capacity of extension cords

01/18/2018 12:27 PM

Yes , but wattage or current demand of the device will determine what the relationship between amperage and voltage will be, whether you are meeting that demand or not is the issue...but good clarification for general purposes....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7

Re: Amp capacity of extension cords

01/17/2018 4:34 PM

To answer both your original question and the re-phrased one... No.

If your house is wired to code, the code takes into account the maximum permitted voltage drop in the circuit based on the amp rating of the circuit in question. So, you can ignore the wiring between the receptacle you plug your extension cord into and the source of power for that receptacle. If to code of course.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#8
In reply to #7

Re: Amp capacity of extension cords

01/17/2018 4:42 PM

In other words, the source is still a Thevenin source, i.e. a potential source with a series resistor, but when wired to code, one may neglect this tiny amount of resistance.

If Rs << Rc (the cord resistance), all the voltage drop up to the load will be on the extension cord.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#9
In reply to #8

Re: Amp capacity of extension cords

01/17/2018 4:49 PM

Yes, but no. The code has limits on the length of wire used to deliver a certain current to a receptacle or a load, this is based on the wire size. If you go beyond the maximum permitted circuit length (this includes both to and from the load by the way) for a given current and wire size combination, you need to increase the wire size to be back in compliance with the code.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#19
In reply to #9

Re: Amp capacity of extension cords

01/18/2018 11:09 AM

I got that, but I was attempting to explain why the danged code is the danged code, and why it is written that way. It is because higher wire gauge numbers have less conductor in them, and therefore have more net resistance per linear distance.

When calculating distance, you are certainly correct on all accounts, by saying, take the distance and double it, and if that is within the length specified for run of that gauge at that load, then you do not have to increase wire gauge on that run. If, however, the double length exceeds the allowable, then code would be violated if one did not increase the wire gauge to the next size that meets the standard.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#12

Re: Amp capacity of extension cords

01/17/2018 10:13 PM

Yes, depending on the length of the cable.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#13

Re: Amp capacity of extension cords

01/17/2018 10:56 PM

The current carrying capacity of a conductor is limited by its maximum allowable temperature rise and/or the maximum tolerable voltage drop of the load equipment.

All other things being equal, the shorter the distance to the CPD (Circuit Protective Device), the lower the voltage drop at the load. For example, if you have 50' of #14 in the wall and plug in a 50' #14 extension cord, then depending upon the load current, if the voltage at the wall may is just acceptable, then the voltage at the end of the extension cord will not be.

Substituting a 50' #12 cord set will not increase the current carrying capacity of the circuit, but it will result in a slightly higher (but still unacceptable) voltage at the load.

Things get really dicey when there are a number of daisy chained outlets between the CPD and the outlet where the extension is plugged in, since any poorly made up intermediate connections can be a source of increased voltage drop. Even worse, where #12 wiring is protected by a 20Amp breaker, the time-current characteristics of the breaker will allow enough current through the #14 extension cord to raise its temperature to 250F in approximately 90seconds, long before the breaker would trip.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#14

Re: Amp capacity of extension cords

01/18/2018 2:24 AM

I think a lot of stuff involving appliance and extension cords just gets fudged in many places. For instance, in the USA, most 120 volt outlets are 15A or 20A. But nothing physically stops you from plugging a 16AWG extension cord (good for maybe 10 to 15A) into a 15 or 20A outlet.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #14

Re: Amp capacity of extension cords

01/18/2018 2:44 AM

<...gets fudged...> That highlights the beauty of the UK system, where there is a fused plug. To protect a cable of smaller cross-section, one merely fits a smaller-rating fuse, say a 3A instead of a 13A. Upstream of the socket, the house wiring, if it were a 2.5mm2 ring-main, is usually protected by a 30A fuse or a 32A breaker, according to the date the installation took place.

Fitting the wrong fuse is always the risk.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16
In reply to #15

Re: Amp capacity of extension cords

01/18/2018 2:56 AM

Agreed. In that respect, I think the British system is better.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#17

Re: Amp capacity of extension cords

01/18/2018 5:16 AM

This is OT with respect to your post, but on the topic of extension cords, and important, so I won't mark it OT.

When using an extension cord of the type that is stored wound onto a drum, always ensure it's fully extended (i.e. off the drum) when in use. I ignored this rule once, in my youth, and have known several other people ignore it since. The result (for any appreciable load) is a nasty smell, usually some smoke, and a burnt-out cord.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #17

Re: Amp capacity of extension cords

01/18/2018 7:45 AM

Quite. No-one likes nasty smells.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#22
In reply to #17

Re: Amp capacity of extension cords

01/18/2018 11:36 AM

No project is entirely fulfilled until one lets the smoke out of it.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adreasler (2); Doorman (1); James Stewart (6); JohnDG (1); Lo_Volt (1); lyn (1); North of 60 (2); PWSlack (2); RAMConsult (1); SolarEagle (2); spades (1); Tornado (2); WJMFIRE (1)

Previous in Forum: Fully Controlled Rectifier Firing Mode   Next in Forum: Lightning Protection for Water Steel Tanks and Zone of Protection

Advertisement