3 Phase Utility Power Metering

05/24/2018 1:21 PM

I was asked by to look into our power bill why the KW being used seemed to be so high relative to our production level. So I built a meter map of all the meters in the plant and a diagram of where those distribution points are fed from and the downstream equipment being fed.

What I found was our main service from utility had only (2) CT's and (2) VT's on power pole. Our incoming power is 13.8KV and feeds 3 main transformers in our plant (2) 12.5MVA's and (1)5MVA transformer. Each of these units had a secondary meter on its load side. Then each distribution breaker also had a meter for loads it supplied.

If I start with meters on distribution breakers and add them all together and read these meters back up to the main that fed them I don't really have any internal issue they are typically within 1% of what the supply meter shows.

But when I add up the meters for the main transformers above and compare them to the utility bill the Utility Bill is almost always 350,000 - 450,000KW a month higher even after I even increase my meters by 3% for any Iron and I2R losses in the transformer even though I don't expect these to be greater than 1-1.5%

So considering the power company's metering is only looking at current on 2 lines and only using 2 PT's as well. I have been arguing with them about the way their metering is set up. We just had them install a new meter in series with new metering CT's and VT's this time on 3 phases / lines.

My question to you guys is how off could recorded power be if power company was using just 2 CT's and PT's? Even though we operate many 3 phase loads with largest loads being 3000HP Could they have been reading an imbalance leg with higher current thus calculating our power incorrectly by this magnitude.

The irritating part is I got contacted by them today their meter team for got to pull the CT shorts on new metering so I have to do another power outage for them.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: 3 Phase Utility Power Metering

05/24/2018 1:40 PM

It is possible to measure the total power on a 3 phase load with two wattmeters. Current is measured on two phases (e.g. A and B) and voltage is measured from these phases to the third phase (e.g. A to C and B to C). The total power is the sum of both wattmeters.

https://circuitglobe.com/two-wattmeter-method-of-power-measurement.html

Register to Reply Good Answer (Score 4)
Participant

Join Date: May 2018
Posts: 3
#2
In reply to #1

Re: 3 Phase Utility Power Metering

05/24/2018 2:16 PM

I don't disagree you can measure this way, but wouldn't this be accurate only if all 3 phases are balanced?

I just went and looked at a system meter on a rotary drum dryer at our plant. The entire process is down currently A Current 6 Amps, B Current 0 Amps, C Current 6 Amps. Voltage AB 477, BC 477, AC 477 PF .712 Lag. So while this system is off their is a large imbalance in the load mainly from lighting and small loads.

If power company is reading power on a 3 phase system and only has CT's on A and C Lines then this is going inaccurately report power. Since they are only using (2) CT's and reading the A and C current. Then they will be charging me almost 3 more KW per hour than I am actually using. if this system stayed down 24 hours with only lighting loads this would be 72KW per day being overbilled from just a small area of our plant.

We are a large factory, and we typically run 3 phase loads. But we have tons on non 3 phase loads as well, lighting, ac systems, computers, wall outlets etc. When your facility takes up 54 acres this could add up quite a bit. It would be nice to say over the years electrical peeps kept this as balanced as possible.. But to average guy adding a power panel to feed single phase loads I don't even think they consider this.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3
In reply to #2

Re: 3 Phase Utility Power Metering

05/24/2018 3:00 PM

I don't disagree you can measure this way, but wouldn't this be accurate only if all 3 phases are balanced?

No, they do not need to be balanced. Of course, there should be no neutral or some of the current has another way in and out.

"Two Wattmeter Method can be employed to measure the power in a 3 phase, three wire star or delta connected the balanced or unbalanced load."

https://circuitglobe.com/two-wattmeter-method-of-power-measurement.html

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#7
In reply to #2

Re: 3 Phase Utility Power Metering

05/24/2018 7:41 PM

Simple algebra proof of 2 Wattmeter method:

3 Wattmeter: P = V1I1 + V2I2 + V3I3

For a no-neutral system: I1 + I2 + I3 = 0, or I3 = - I1 - I2

P = V1I1 + V2I2 + V3(-I1 - I2)

P = (V1-V3)I1 + (V2-V3)I2 (2 Wattmeter method)

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: 3 Phase Utility Power Metering

05/24/2018 3:08 PM

I'm wondering if your billing difference is just a difference between real kilowatts and real and reactive power measured in kVA? Adding some reaction correction might save you money.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Participant

Join Date: May 2018
Posts: 3
#5
In reply to #4

Re: 3 Phase Utility Power Metering

05/24/2018 3:24 PM

We have the best PF correction you can hope to have. Our largest power consumers are (2) 3000HP Synchronous Ball Mills. These run at basically Unity PF. Running these two guys keeps our plant power factor generally in the range of 96% for the month

All of our internal metering takes into account Real, Reactive Power.

What I can say is the power company after running tests on metering felt there could possibly be a problem in way they were billing so they have agreed to and have installed another meter on pole before our existing meter. So they could monitor any differences they see between the two. Only issue they forgot to pull CT jumpers on new CT's and the are still shorted so now I have to wait till 6/2 for them to power down again and pull jumpers.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #5

Re: 3 Phase Utility Power Metering

05/26/2018 8:00 AM

This may seem elementary, but you say the bills are excessive. Can you actually read the utility meters yourselves, to check billed kWh against metered kWh? Have you seen bill yourself to see if there are reactive load or unbalanced load additions?

As I see it, misconnection would cause a watthourmeter to read low but with a KVArh meter could read your unity p.f. watt load high.

Ensure the power company checks the phasing & polarity of all connections in the path to the meters aginst meter connection diagram, preferably by injection test.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: 3 Phase Utility Power Metering

05/24/2018 6:17 PM

Interesting problem, but we're missing a piece of the puzzle. That piece is the a comparison between the actual kWhrs billed vs. the sum of all your internal metering points. There are a couple of possibilities that might explain the discrepancies, and knowing the actual/billed readings will provide more information than just the 350,000 delta.

You haven't stated your location, but the fact that the utility has installed a second metering point ahead of yours indicates that they seem to be willing to help you track down the problem.

Regarding the two-wattmeter method, you can see the math here.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8

Re: 3 Phase Utility Power Metering

05/24/2018 11:14 PM

For Unbalanced load, preferable to have 3 Current coil element in the meter.

Similarly 3 Potential coil in the instrument.

Some times instrument will have 3 coils but connection made only from 2 CTs

Similarly connections to the meter might have inter changed like S1 and S2.

Also if current coil c1 is connected phase 1 then potential coil P1 should be connected to phase 1 only

. These suggestion may look odd but some times we miss out these.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); breezez (2); RAMConsult (1); ramvinod (1); redfred (1); Rixter (3)