Cooling a Packed Bed with an A/C

05/24/2018 3:15 PM

Scenario:

A cylindrical 10'D x 16'H vessel is filled with 9' of packing in the middle of the vessel(think small pellets). You have a 2 large nozzles at the top and 1 large nozzle at the bottom(~ 20-24" in diameter). To cool the packing in the vessel you use an air conditioner flowing air into either the top or bottom with a blower on the opposite end.

Is it best to cool putting the A/C coming in at the top or the bottom? Why?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Cooling a Packed Bed with an A/C

05/24/2018 4:18 PM

Is the air recirculated?

Register to Reply
Participant

Join Date: May 2018
Posts: 4
#3
In reply to #1

Re: Cooling a Packed Bed with an A/C

05/24/2018 4:44 PM

The air is not recirculated. It is outside air passed through an HVAC once.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9911
Good Answers: 1141
#2

Re: Cooling a Packed Bed with an A/C

05/24/2018 4:32 PM

I'm guessing you should feed it from the bottom. The A/C air is being heated by the contents of the vessel causing the air to rise. If you feed it from the top, you are opposing the convective flow.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#4

Re: Cooling a Packed Bed with an A/C

05/24/2018 4:45 PM

I wonder...

At what air(?) speed will there be enough turbulent friction for these "packing peanut" pellets to ignite in spontaneous combustion?

At what air(?) speed will these packing peanuts be lifted up or packed down to block any air flow?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Participant

Join Date: May 2018
Posts: 4
#5
In reply to #4

Re: Cooling a Packed Bed with an A/C

05/24/2018 4:59 PM

Not enough velocity to fluidize the bed. Think blowing through a straw into large cup of ice?

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#7
In reply to #5

Re: Cooling a Packed Bed with an A/C

05/24/2018 5:48 PM

"Not enough velocity to fluidize the bed. Think blowing through a straw into large cup of ice"

Sounds like, in this description, you believe cold air should supplied from the bottom of the vessel.

I agree with you, Usbport, and Rixter.

Why once through and not recirculated?

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: Cooling a Packed Bed with an A/C

05/24/2018 6:21 PM

"Why once through and not recirculated?"

I got the impressing there was no air outlet, no "through" just blowing into a closed tank.

"The air is not recirculated. It is outside air passed through an HVAC once."

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#17
In reply to #8

Re: Cooling a Packed Bed with an A/C

05/25/2018 2:45 PM

Well, that could be, I suppose.

Seems like a static condition would soon develop if warmed air isn't exhausted. Prolly would work better if the cold inlet air is filtered through several slices of baloney.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#11
In reply to #5

Re: Cooling a Packed Bed with an A/C

05/24/2018 8:51 PM

Well that's at least one additional bit of information. Trouble is I used two of the twenty questions to find that bit of information. You don't play by the rules of the game.

Without enough coolant flow this Thorium bed of pellets can possibly thermally run away to the point of fusing the pellets. Do you think it is wise to hide information from us?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Optical Engineering - Member Engineering Fields - Engineering Physics - Member Engineering Fields - Systems Engineering - Member

Join Date: Apr 2010
Location: Trantor
Posts: 5363
Good Answers: 647
#6

Re: Cooling a Packed Bed with an A/C

05/24/2018 5:43 PM

Blowing in from the bottom gives you two advantages. The first is that under normal conditions hot air rises, so you making use of natural convective flow. The second is that the upwelling air will help lift and separate the pellets, allowing the air to flow between them better. These two processes work together to cool the pellets.

Conversely, blowing down means you are fighting the convective flow, and you are pushing the pellets together - which both hurt your scheme of trying to cool the pellets.

__________________
Whiskey, women -- and astrophysics. Because sometimes a problem can't be solved with just whiskey and women.
Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#10
In reply to #6

Re: Cooling a Packed Bed with an A/C

05/24/2018 7:37 PM

In addition to natural convection assisting total flow, natural convection when flowing from the bottom up will also help to distribute airflow where it is most needed, reducing hot spots and allowing more rapid heat transfer.

Flow paths that add the most heat will undergo the greatest expansion and experience the greatest bouyance. This works to bring higher flow rates to the hottest areas.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#9

Re: Cooling a Packed Bed with an A/C

05/24/2018 6:44 PM

If there are two nozzles at the top one could be used to inject cold air which would want to sink.

The other open nozzles at the top And bottom would allow for convection removal of additional heat.

The location of nozzles is a factor needing consideration. As well as rater of flow through each nozzle.

.my guess

..

__________________
High Tolerance is Beautiful
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Cooling a Packed Bed with an A/C

05/25/2018 5:01 AM

Here's another vote for "in at the bottom". That way, the bed is being lifted, though only slightly, and the incoming air is working with natural convection, and not against it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Nov 2007
Location: Western NC
Posts: 92
Good Answers: 3
#13

Re: Cooling a Packed Bed with an A/C

05/25/2018 11:00 AM

I would think with small pellets as you stated, that an A/C wouldn't put enough air pressure out to ventilate through 9' of it. Seems like it would restrict it pretty well unless you have a very hefty blower. How big of an A/C are you talking about?

Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#16
In reply to #13

Re: Cooling a Packed Bed with an A/C

05/25/2018 2:43 PM

Depends on the packing factor which depends on the pellet size distribution. A bed of spherical pellets of uniform size ends up with about a 30% void. The differential pressure across depends on effective pore hydraulic diameter to the fourth power. So a tank full of basketballs will have much lower resistance than a tank full of b-b's. Then it is just a matter of matching the AC fan curve to the effective hydraulic diameter and length.

There are also two schools of thought on the nozzle entrance. Cold air added to a warm tank will want to sink, promoting air flow. Cold air placed in the bottom will warm and want to rise. Neither case is the full story and most likely a computational flow dynamic model would be needed to optimize it. I suspect that the natural circulation component is going to be much less contribution than the fan curve and compressible flow hydraulic circuit elements.

Register to Reply
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#14

Re: Cooling a Packed Bed with an A/C

05/25/2018 1:36 PM

Question breakdown.

A. 10 foot diameter and 16 foot high vessel. Using the word, " high " would indicate that 10' is horizontal and 16' is vertical.

B. 9 feet of packing in the middle. Nothing to indicate what the packing is made of other than pellets. Pellets could range from pea gravel to styrofoam peanuts. As all mass has weight, a presumption would be that there is open space approximately 7 feet from the top of the vessel. Or the packing is equally divided between the top and bottom, leaving an open space of 3.5' on the top and the bottom.

C. Nozzles, the measurement of 20-24" is not clearly stated as to if this is the outside measurement or of the inside measurement. Also the configuration of the nozzle (s) , flat fan, adjustable, flood jet, hollow cone, etc. Length, etc.

D. Cool. Why do the pellets need to be cooled. If there are only nozzles entering into the vessel, how does air conditioned air enter the vessel. If the blower is placed on the top or bottom and air conditioning is placed on the top or bottom ( blower placed opposite of air conditioner ) , what conditions are required to create equivalency between top and bottom cooling effect.

E. Blower. As the blower creates positive pressure and the a/c and nozzles do also, under what means will air be extracted if all entries are into the vessel and none are provided for relief.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#15
In reply to #14

Re: Cooling a Packed Bed with an A/C

05/25/2018 2:21 PM

This is why I made the absurd proposal that the pellets were Thorium pellets. Thorium pellets would need cooling due to fission reactions.

We also have no idea what if any voids would nominally exist between any pellets. If the pellet geometry tessellates like rectangular or hexagonal bricks then no cooling fluid (air?) could possibly migrate through.

IMHO this is nonsense.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#18
In reply to #15

Re: Cooling a Packed Bed with an A/C

05/25/2018 3:02 PM

Yet another secret part of the instructor's scenario may be that the (presumed) waste heat needs to be harvested, perhaps with a peltier device as a thermoelectric generator, this producing enough power to operate the mechanical A/C units.

This process is also likely enhanced with a baloney filter of some sort.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#20
In reply to #15

Re: Cooling a Packed Bed with an A/C

05/30/2018 3:48 PM

Thorium mixed oxide pellet reactor research is happening. I doubt they are cooling this with an air conditioner but it does fit the stated conditions.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Participant

Join Date: May 2018
Posts: 4
#19

Re: Cooling a Packed Bed with an A/C

05/30/2018 3:09 PM

Clarifications:

The blower will be pulling air out of the reactor.

The pellets are metal oxide pellets that need to be cooled in order to be extracted from the vessel (no head being generated)

The pellets are about 75-95 lbs/ft^3 and individual pellet is about the size of rabbit feed.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#21
In reply to #19

Re: Cooling a Packed Bed with an A/C

05/30/2018 6:25 PM

Why, then, chilled air and not ambient?

I still vote air inlet at the bottom, exhaust from the top.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#22

Re: Cooling a Packed Bed with an A/C

06/02/2018 3:43 PM

Heat transfer is based on differential temperature, so just as a typical counter-flow heat exchanger, the cooler medium is introduced at the hotter end, which one might think could be at the top of the vessel.

Measurements could confirm this...

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#23
In reply to #22

Re: Cooling a Packed Bed with an A/C

06/03/2018 6:46 PM

Measurements would probably refute.

There are some problems in your statement.

"... so just as a typical counter-flow heat exchanger, the cooler medium is introduced at the hotter end, which one might think could be at the top of the vessel. ..."

'Cooler medium is introduced at the hotter end' is not a true statement for counter-flow heat exchangers. The cooler medium is introduced at the cooler end where the hot medium is exiting and has already cooled substantially...hence counterflow.

Your statment would hold true for parallel flow and kind of true for cross flow.

"...the hotter end, which one might think could be at the top of the vessel...."

Why? Why would one think that? If the pellets were recently deposited, why would there be a likelihood of segregation of hot pellets to the top? If the hot pellets had been sitting for a period, why wouldn't a hotter region be more likely to be in the middle?

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#24
In reply to #23

Re: Cooling a Packed Bed with an A/C

06/03/2018 11:25 PM

The vessel could be similar to a reactor, with static internal elements, (similar to a RTO, perhaps), where simple convection would place the warmer components at the top.

I may have my heat exchanger terminology mixed up, but you get the principle. It is common practice with steam to water tube and shells, if I'm remembering correctly?

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#25
In reply to #24

Re: Cooling a Packed Bed with an A/C

06/04/2018 5:01 AM

I get the principle though I suspect if you think about it, the counterflow heat exchanger does not have the cool stream entering where the warm stream enters (where it will be at highest temp) but where it exits (lowest temp).

Moreover, I think the analogy to heat exchangers with physical separation of hot and cold streams is misleading when considering direct contact heat exchangers.

Consider that if cool air is fed in the top, the air pulled from the bottom will be more likely to be denser cooler less boyant air. This means the air that has removed the least heat will be the most rapidly removed. The air that has already taken the most heat will be more likely to stick around in counter currents and pockets as it will be more buoyant.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#26
In reply to #25

Re: Cooling a Packed Bed with an A/C

06/04/2018 12:58 PM

The point is the differential temperature dictates the heat transfer, so the cooler air in at the hotter end should move more heat. It is likely the specific heat of the fill/ packing is higher than the cooling medium, so get the heat out while you can is the philosophy I’m going with, short of an actual thermal modeling exercise...

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#27
In reply to #26

Re: Cooling a Packed Bed with an A/C

06/04/2018 3:47 PM

So once your cooler air at the hotter end has removed more heat and become warmer, where does it go?

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#28
In reply to #27

Re: Cooling a Packed Bed with an A/C

06/04/2018 5:44 PM

back to its source, the great enthalpy of our planet, from what I understand...

A one pass heat exchange in the microcosm of the vessel