Validation of the Inertia Constant of a Synchronous Generator

07/18/2018 8:33 PM

Hello everybody,

I want to validate the inertia constant of a synchronous generator, stated by its supplier.

I have all the necessary instruments to study the behaviour of the generator including oscillo-perturbography recording devices.

I need your help to decide the best testing procedure. I can perform load reject or load acceptance tests.

I think that if I choose a load acceptance test, the generator inertial response will depend on the response of all the other generators on the grid.

Am I right? But how can I determine the figures of a single generator if all the others react to a generation loss and subsenquently load acceptance?

I am looking forward to hear your expert advices.

Register to Reply
Pathfinder Tags: Inertia constant
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Validation of the inertia constant of a synchronous generator

07/18/2018 8:40 PM

Are you testing the system, or just the generator?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Feb 2018
Posts: 9
#3
In reply to #1

Re: Validation of the inertia constant of a synchronous generator

07/19/2018 4:28 AM

Hello there.

I work for an utility in Madeira island and we have wind, solar, natural gas and fuel generators.

We have the generators manufacturers inertia figures but not the fuel prime-movers.

I want to study the synchronous inertial response of the generators but I cannot isolate them from the grid. Typically a fuel generator produces around 8 MW and the top load of the grid is around 115 MW.

Is it possible to get results with this scenario?

Thanks.

Register to Reply
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Validation of the inertia constant of a synchronous generator

07/18/2018 10:24 PM

Is this machine installed and you want to run various experiments on it?

Are you trying to determine its dynamic response to system disturbances?

How big is this machine, and what is the prime mover?

What is its size relative to the system that it is attached to?

I hope you realize that the dynamic response of any generator depends upon many things besides its H-constant, and isolating a single physical constant (its inertia) in a multivariable/multiloop control system is a real challenge.

Personally I would start with the physical dimensions and masses of the entire rotating prime mover/generator system, and calculate the Flywheel Effect (GD2), then use the method in this CIGRE paper to compare against the number supplied by the manufacturer. Your answer will be within +/- 10% of the supplied value. Been there, done that....

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
Member

Join Date: Feb 2018
Posts: 9
#4
In reply to #2

Re: Validation of the inertia constant of a synchronous generator

07/19/2018 4:41 AM

Hello and thanks for your reply.

The machine is installed and is one of several in the utility I work for in Madeira island.

You´re right, the goal is to study the generator dynamic response to system disturbances.

The prime-mover is a fuel engine and the alternator typically produces around 8 MW for a top load of 115 MW.

That's my main problem: I cannot isolate one machine for testing. Any generation loss that I perform will have the load acceptance response of all the other synchronous generators connected to the grid at that moment. I can measure the response of one of those generators but how can I reach a plausible inertia figure result?

I have just printed it and I will study the CIGRE document you have provided.

Thanks for your help.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #4

Re: Validation of the inertia constant of a synchronous generator

07/19/2018 1:53 PM

After reading about your isolated grid and it's multiplicities of generation resources, I would suggest that you run a simulation of the dynamics first, long before you attempt any type of live testing, then you can determine if it's really necessary to perform any real-time tests.

First, the prime mover is a multi-fuel diesel engine, so not only is its mass rotating, it is also reciprocating, and this makes its moment of inertia dynamic, not static like the alternator rotor.

Second, your 8MW machine represents only 5% of the system load, so its response is like the tail wagging the dog.

Third, you have an interesting mix energy sources, including solar, wind, battery, hydro, thermal, and modeling some of them is highly dependent on their manufacturer.

I would start by reading the technical papers and contacting the authors that have already done studies similar to yours, and then there's Google, CIGRE, and IEEE for source documents.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7
In reply to #4

Re: Validation of the inertia constant of a synchronous generator

07/19/2018 5:01 PM

So, really you are interested in the engine-generator response, it is their combined inertia which matters.

I think a load rejection test is most likely to give an accurate measure of inertia, if you do not have any maker's figure. But if the maker used CAD design system and got it to compute mr2 bit by bit & sum them, you will not get a more accurate result by test (even if mr2 was computed by "hand" integration).

The real issue is how the system will react to loss of a generator or putting on a big load. So when you reject load on one generator, it is of even more interest to record the response of the system at several points, perhaps generator sites. You may have to set up a system to trigger or mark all recorders at same time or synchronise their clocks by cable or radio link/standard time transmission, so you have accurate phase differences.

There is also the issue of losing a big load for test purposes. I have heard of single shaft gas turbines being motored to provide a test load, they draw more than they generate - may be more problems with "pogo-stick" engines - in any case, I think their motoring losses are a small part of the output rating.

As already posted by RAMconsult, you must use all available data to make a system model including the probable step load increase/decrease possible & simulate load loss/addition on model to assess what is tolerable for test. Load reject on smallest genset first - previous experience of accidental or fault trip-outs may give a real check on what is possible and the probable system inertia/MW versus Hz [MW versus Volt] response of loads.

Usually, generator excitation response to add/cut VArs or get a rotor swing can be faster than prime-mover kW response. Some AVRs have a datum-step facility for setting response or a potentiometer can be switched -in/out of the resistive volt-sensing chain by relay.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Validation of the Inertia Constant of a Synchronous Generator

07/19/2018 9:24 AM

Why?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Validation of the Inertia Constant of a Synchronous Generator

07/26/2018 4:23 AM

Deleted.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Carlos Melim (2); PWSlack (2); RAMConsult (2); SolarEagle (1)

Previous in Forum: Class 1 Div 2 Motor   Next in Forum: Variable Frequency Drive

Advertisement