07/18/2018 5:11 AM

Dear All,

I observed Reliance Electric Motor TEFC certification CSA LR7861 (photo as attached) installed in our oil and gas facility. There is nameplate indicate "Recognized Component Electric Motor For Ordinary Locations". No other information in the motor enclosure and could not find the datasheet of it. Is it suitable for use in Hazardous Location especially in class 1 div 2 area?

Thank you for any comment.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Class 1 Div 2 Motor

07/18/2018 5:20 AM

No.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 2)
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#10
In reply to #1

Re: Class 1 Div 2 Motor

07/19/2018 10:22 AM

Gave you a GA! Stupid question: (for the OP) Why have ratings if we are going to ask questions instead of going by the rating? -- JHF

__________________
If it's too good to be true, it probably isn't
Reply
Anonymous Poster #2
#2

Re: Class 1 Div 2 Motor

07/18/2018 5:24 AM
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Class 1 Div 2 Motor

07/18/2018 9:32 AM

Class 1 Div2 implies you could have an explosive atmosphere under fault conditions - like a leak in what looks like a driven compressor in yr photo & inadequate ventilation to disperse it. THIS IS NOT AN "ORDINARY LOCATION".

It is just possible the motor & coupling housing are pressurised with "gas-free" air & an approved pressure monitor/shutdown system.

But, according to memory, "non-sparking" includes not having hazards like a light alloy fan and a steel shroud around it - which can spark by mechanical contact.

Reply
Guru

Join Date: Oct 2008
Posts: 42357
Good Answers: 1695
#4

Re: Class 1 Div 2 Motor

07/18/2018 11:09 AM

As already mentioned, NO!

The appropriate motor must be used and the one you have DOES NOT COMPLY!

By trying to save a penny you could KILL PEOPLE, as in make them PERMANENTLY DEAD!

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33400
Good Answers: 1817
#5

Re: Class 1 Div 2 Motor

07/18/2018 11:24 AM

It might be allowed by code, and might be ok'd by the AHJ...but it's not a good idea....

..."

Re: Class 1, Division 2, Group B

Yes, you can install a TEFC motor in a 1-2-B electrical classification, providing there are no arcing devices. The one thing that you will need to be concerned with is temperature. As you are aware the motors today run hotter than the old days, due to the reduction of iron in the stator.
What you need to know is the AIT, (Auto-Ignition Temperature)of the chemical that you are dealing with, and then you cannot have any item have a surface temperature greater than 80 % of the AIT of the chemical that you have in the classified area.
You mention a TEFC motor, you can actually install a open type motor in a Class 1, Division 2 area, provided that their are no arcing devices. I am totally against installing an open type motor in a classified area, and I would not do it, but the code will allow it."...

http://forums.mikeholt.com/showthread.php?t=64641

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7955
Good Answers: 459
#6
In reply to #5

Re: Class 1 Div 2 Motor

07/18/2018 4:09 PM

Like you say, there's a big difference between allowing something versus recommending something.

Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Class 1 Div 2 Motor

07/18/2018 5:29 PM

That type of motor is a “UL Recognized Component”, not a “UL Listed” motor. The difference is that the motor can only be used as PART OF a listed ASSEMBLY. In that light, you cannot single out that component as a stand-alone device, meaning NO motor that is only “UR” will be “listed” for anything all by itself. If the ENTIRE COMPRESSOR is UL listed for Cl 1 Div 2, the info on thenameplate is irrelevant. So presumably the compressor mfr would have had to engineer and assemble it into the compressor package in a way that meets the requirements for UL listing in the classified area.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Anonymous Poster #1
#8

Re: Class 1 Div 2 Motor

07/19/2018 9:15 AM

I also found motor with the same mark "Recognized Component Electric Motor For Ordinary Locations", but in the motor enclosure also have nameplate indicate the motor suitable to be used in class 1 div 2 GR CD T3. in the nameplate indicate reliance electric 841XL. What is the type of protection for this motor? is it Ex-na?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#9
In reply to #8

Re: Class 1 Div 2 Motor

07/19/2018 9:29 AM

Why isn't the original equipment manufacturer dealing with these concerns over the telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#15
In reply to #8

Re: Class 1 Div 2 Motor

07/19/2018 2:40 PM

I suspect protection type is Ex(p), IEC code - that is pressurised, it might be N - non-sparking, but I have seen that only when motor is outdoor, outside hazard area driving purge duct fan & yr first photo seems to drive adjacent compressor. Is the "green snake" in photo a pipe or cable?

It is a practical way of converting a standard TEFC motor to Ex. The complication is in having pressurised clean air - no problem in a plant using lots of pneumatics - and a certified fail-safe scavenge air pressure & flow monitor which stops the motor for any air fault. Also motor has to have bearing seals which do not mind Δp - not a problem to a maker who has experience with hose proof/ship deck/flooded motors. And some requirements like not having a magnesium alloy casing which sparks if you drop a steel hammer onto it or a fan housing which could contact the fan.

As has been commented, motor would be part of a UL or equivalent certified assembly with nominated critical components and approved drawings - Reliance probably safeguarded themselves by labelling motor "ordinary locations" to avoid users thinking "magic is in motor".

Reply Score 1 for Good Answer
Anonymous Poster #1
#22
In reply to #15

Re: Class 1 Div 2 Motor

07/20/2018 1:57 AM

the "green snake" is grounding cable from structure to motor enclosure.

In other plan that use IEC std, we have ABB motor and its clearly mentioned the Ex protection is Ex-de.

but for the facility that using ANSI std it's not clearly mentioned the Ex protection, only statement classified for Class 1 Div 2 area.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#23
In reply to #22

Re: Class 1 Div 2 Motor

07/20/2018 10:39 AM

Ex-de would be combination of d -flameproof (which is an enclosure with such narrow gaps & wide flanges that no flame will exit if you ignite flammable gas inside enclosure) and e - increased safety, which has such low temperature rise, insulation thickness & clearances it will never spark - probably the terminal box in this case. Ex(e) was much a German technique e.g. flameproof Ex(d) switch in Ex(e) panel: but in some cases, low ignition temperature risk, it is most economic.

Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#11

Re: Class 1 Div 2 Motor

07/19/2018 11:00 AM

Reliance was bought by Baldor and Baldor was bought by ABB.

ABB still carries some of the Reliance brand and frames.

I recommend contacting ABB / Baldor for your questions.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#12
In reply to #11

Re: Class 1 Div 2 Motor

07/19/2018 12:03 PM

<...recommend contacting ABB / Baldor...> Absolutely. This guidance was available to Anonymous Poster #1 at #2⇑.

Slam-dunk.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#13
In reply to #12

Re: Class 1 Div 2 Motor

07/19/2018 12:29 PM

yeah, I was trying to fill in some of the history.

I used to work as an EE at the Reliance Stratford Ontario large AC motor plant.

That plant is now closed and the manufacturing moved to the US - long before Trump. When Rockwell initially bought Reliance the motor plants were quickly spun off to Baldor.

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#14
In reply to #13

Re: Class 1 Div 2 Motor

07/19/2018 1:07 PM

The phone numbers are all in the public domain.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2008
Posts: 42357
Good Answers: 1695
#16
In reply to #13

Re: Class 1 Div 2 Motor

07/19/2018 2:44 PM

Let's keep going off topic, since the OP has been given more than adequate information.

When I worked for an OEM, we used hundreds of TEFC motors. 1-10 HP. Baldor motors run hotter than others. The Baldor engineers I met with told me that this was because their thermal management scheme was better than the competition's so the heat was transferred from the inside to the outside of the motor, keeping the inside cooler.

Their motors gave us good service so I never bothered to test their claims. Have you ever heard this?

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#17
In reply to #16

Re: Class 1 Div 2 Motor

07/19/2018 3:30 PM

I can't comment on the Baldor design, but for the Reliance designs they stuffed more power into a smaller frame. (Typically one frame smaller). The cost for higher temp insulation was less than the cost for copper and iron. Some of those motors ran so hot you would burn yourself if you touched them while running full load.

I am an old traditionalist - class B rise with H insulation.....

Class B rise runs warm, Class H rise is "stinking" hot.

I think all the motor manufacturers chase the same $$$

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42357
Good Answers: 1695
#18
In reply to #17

Re: Class 1 Div 2 Motor

07/19/2018 3:54 PM

That could explain it.

Doesn't matter now, that was many years ago.

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#19
In reply to #18

Re: Class 1 Div 2 Motor

07/19/2018 6:34 PM

yeah, I am past the traditional retirement age - most days I feel like telling people to leave me alone - then an interesting project comes along. I think I need to be more selective with my clients.

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42357
Good Answers: 1695
#20
In reply to #19

Re: Class 1 Div 2 Motor

07/19/2018 8:14 PM

I quit at 70.

Now I cut the grass, clean the pool, do some woodworking and repair lost and abandoned bikes to give to underprivileged/underfunded grade school kids.

Reply Off Topic (Score 5)
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#21

Re: Class 1 Div 2 Motor

07/19/2018 11:39 PM

Here in the u.s. , we have a store, harbor freight, many of the products they sell have a very similar nameplate. Most of these items fall into one of two categories. A. When it finally wears out, you throw it out in the trash. B. If it breaks, you throw it out in the trash and buy a replacement.

Reply
Reply to Forum Thread 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (3); Anonymous Poster (3); Brave Sir Robin (1); Circuit Breaker (1); GW (4); JRaef (1); lyn (4); PWSlack (3); SolarEagle (1); tonyhemet (1); Tornado (1)

Previous in Forum: Query About Voltage Drop in Impedance   Next in Forum: Validation of the Inertia Constant of a Synchronous Generator

Advertisement