Member

Join Date: Sep 2007
Posts: 9

Heat Exchangers and Super Heated Steam?

09/27/2007 2:56 PM

My question is about a heat exchanger thats a shell and tube type. It has 130 tubes and they make four passes and its about 16 feet long and 3 feet in diameter. Its used to condense superheated steam at 5 psi and 375 F and heat up water. The water is suppose to be heated from 110 F to 180 F, but its usually only heats up to 140 F. Steam is coming through both sides at the top and condenses at the bottom and the water comes through the bottom and goes through the tubes and out the top. Now the tube bundle just fits in the shell so there isn't a lot of extra space inside the shell for natural condensing that I can tell. Now I know that superheated steam is not very practical for heat exchangers because its heat transfer coefficient is poor and its hard on the equipment from the heat when the steam is going through the tubes. But i was wondering how bad the super heated steam was for this application since its just going through the shell and condensing. Our tube bundles get cracks in them also, brass and stainless steal bundles both got ruined so far over about an 8 year period each. I'm assuming this is from the steam, but I'm not sure, no one that works here knows either and they are just ordering a new stainless steel bundle of tubes. I suggested to de-superheat the steam before it goes into the heat exchanger with spray nozzles or whichever method, but my boss doesn't think its worth it. I just wanted some suggestions on this situation as what is best to do.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#1

Re: Heat Exchanger

09/27/2007 3:43 PM

ok, one thing at a time,

Its used to condense superheated steam at 5 psi and 375 F and heat up water.

- sounds like your using it as regen

One thing to get the energy out of the steam, you have to condense it.

As far as 5 lbs of steam thats nothing, it's about 212 degrees.

whats the volume in lbs/hour of steam?

And your right getting that transfer is difficult, this is done by impingement the steam right onto the tube,

- As far as super heated steam

?????

- I do not know the flowrate of the water but the bundle may be undersized.

Whats the surface area?

- as far as life, 8 years may not be bad. have you had the water test for minerals and hardess, tube bundle may be fouling.

- As far as cracking,

1.) what type of HX is it, U-tube, counterflow.

2.) What type of stainless, (could be 304SS with what your said)

3.) is it ASME cert. with a "U" stamp.

4.) where is it cracking, give a clue to the actual cause.

5.) what the start-up procedure, do your run water, and then open the steam, could be thermal shock.

I think I covered it, but if not, others would post added info.

Your find this out, and we can come up with some answers i'm sure,

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#2
In reply to #1

Re: Heat Exchanger

09/27/2007 4:14 PM

Design Flow rates of water and steam would be useful.

Is it really 110F water or is it colder than that?

what is the tube diameter?

Do the old tubes show any sign of fouling on the water side?

Is shall side baffled for multiple steam passes?

Are there any operrational pressure and temperature readings from both sides at inlet and outlet?

What kind of flow controls on either the steam or water? If steam is shut off, does the shell have a vacuum breaker?

Anyone else with curious minds?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#3
In reply to #1

Re: Heat Exchanger

09/27/2007 4:26 PM

"- sounds like your using it as regen"

must have started too early this morning posted by mistake, don't know where I got that from with the info provided, and the steam temperature is about 320 degrees not 212 or 375

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#4
In reply to #3

Re: Heat Exchanger

09/27/2007 8:38 PM

What kind of steam trap is installed?

Any vertical lift for the condensate, or is it all downhill to a receiver or pump?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Power-User

Join Date: Jun 2007
Location: Port Neches, Texas -- Bond Point
Posts: 117
Good Answers: 3
#5

Re: Heat Exchangers and Super Heated Steam?

09/28/2007 9:09 AM

Stainless steel, heat and calcium = cracked stainless. check your condensate for calcides. Even calcium in insulation will cause this if it gets wet. We cracked up a 100 foot ss tower with 5/8" plate that had to be taken down in pieces.

__________________
Support your local Shriners, they have provided FREE medical assistance for over 800,000 kids so far.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#7
In reply to #5

Re: Heat Exchangers and Super Heated Steam?

09/28/2007 9:30 AM

calcium in insulation? I did not know that, I knew chlorides

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#6

Re: Heat Exchangers and Super Heated Steam?

09/28/2007 9:20 AM

What is your Question actually?

(1) The water is suppose to be heated from 110F to 180F, but usually only heats up to 140F? or (2) De-super heating steam? or both???

You've "stalled" the Temperature-controlled Heat exchanger with a wrong trapping system : wrong-type / under capacity steam trap or have lifted condensate from the heat exchanger to return main.

You need to install a Condensate Power Pump packaged unit at the heat excanger to drain the condensate into the receiver. Install the Trap at the pump outlet.

This will over come "stall" conditions.

When the heat exchanger stalls, there are excessive damage to heat exchanger tubes and steam traps internals due to excessive water hammering of condensate mains & systems.

Super heated steam is gas and slows up the heating process. For process steam it must be saturated with a water injector & control valve.Fine mist of water is sparyed and controlled at saturated steam pemperature.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply Off Topic (Score 4)
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#8

Re: Heat Exchangers and Super Heated Steam?

09/28/2007 9:54 AM

What is your Question actually?

(1) The water is suppose to be heated from 110F to 180F, but usually only heats up to 140F? or (2) De-super heating steam? or both???

You've "stalled" the Temperature-controlled Heat exchanger with a wrong trapping system : wrong-type / under capacity steam trap or have lifted condensate from the heat exchanger to return main.

You need to install a Condensate Power Pump packaged unit at the heat excanger to drain the condensate into the receiver. Install the Trap at the pump outlet.

This will over come "stall" conditions.

When the heat exchanger stalls, there are excessive damage to heat exchanger tubes and steam traps internals due to excessive water hammering of condensate mains & systems.

Super heated steam is gas and slows up the heating process. For process steam it must be saturated with a water injector & control valve.Fine mist of water is sparyed and controlled at saturated steam pemperature

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply Off Topic (Score 5)
Anonymous Poster
#9

Re: Heat Exchangers and Super Heated Steam?

09/28/2007 2:44 PM

The steam is going through the tubes??????

If yes then is wrong (inefficient). why???because condesate steam is at 220 F.

So if you have too much condesation then actually is like reducing the surface area for heat transfer. Also there is a possibility of water hammering through the passes (you mention four?)

On the other hand if you use steam at the outside of the tubes (on shell site) then the steam can removed more easier , with out flow restrictions or hamering

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#10

Re: Heat Exchangers and Super Heated Steam?

09/29/2007 2:49 AM

i replied 2 times but the matter did not print.????

What is your Question?

Is it water not being heated up to 180F? or Is it reasons for damage to heating coils of the heat exchanger or Is it Super heated steam?

The reason the water is not being heated up is because the heat exchanger has reached a "stall" conditions being temperature controlled becuse of either condensate lifting from steam traps/ wrong type & under capacity steam traps.

The coils have drastically water logged and resulting in excessive water hamering of both coils inside and condensate lines outside. Under these conditions there is extensive damage to heating coils and steam trap internals.

The only option is to take the steam trap (preferbly Ball Float thermostatic) ideally sized by gravity slope to a Packaged Condensate Power Pump if more than one Heat Exchangers involved. If only this Heat Excanger involved then remove steam trap and take the discharge of the heat excanger to the receiver of the condensate power pump. Install the Steam Trap at the discharge of the pump to return to overhead main.

As regards Superheated steam this is like gas and delays heating because it has to wait it it reaches saturation temperature before condensing.

This if not desuperheated will increase process heating time like in your case.

Prefer installing a de-superheater with Water Control Valve & temperature controller to spray water in fine mist to de superheat.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#11
In reply to #10

Re: Heat Exchangers and Super Heated Steam?

09/29/2007 4:15 AM

Ducon, you are right.

I think a wrong trapping system, wrong type and/or under capacity steam trap is the reason of the problem. Installing a new steam trap with the appropriate type and position, and maintaining the steam at tube side not shell side -as suggested by Guest- can overcome the problem of insufficient heating of water.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#12
In reply to #11

Re: Heat Exchangers and Super Heated Steam?

09/29/2007 6:30 AM

Asak & Thanks.

We've a lot of Dye Houses here and they all use Theis HT Dyeing Machines. All have Heat exchangers which are Temperatured-control with Control Valves and everbody lifts condensate from the steam traps. its like monkey see - monkey do type of a thing here. They copy what the other guy did and all land up with the same problem of water hammering, water logging & stalling of the heat exvchangers as he is experiencing.The condensate Power Pump is the the only solution if he wants to return his cndensate.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Member

Join Date: Sep 2007
Posts: 9
#13

Re: Heat Exchangers and Super Heated Steam?

10/01/2007 8:20 AM

Thank you everyone for your input. It's helping out alot.

Register to Reply
Member

Join Date: Sep 2007
Posts: 9
#14

Re: Heat Exchangers and Super Heated Steam?

10/01/2007 8:45 AM

I dont think we have a steam trap for our heat exhangers. They just take steam in the shell and condense it and the water goin through the tubes gets heated up in the process. But our tube bundles get ruined, destroyed almost. River water runs through the tubes and superheated steam at 375 degrees F is being condensed in the shell. The cracking of the tubes is in all different parts of the heat exchanger. It has no pump also it just drains to our conensate tank. The steam comes in from the top, hits steel plates connected to the tube bundle and goes through three sections seperated by two baffles. The steam comes in from two different parts at the top on the right and left sides and the heat exchanger is split in the middle by a steel plate blank.

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#15
In reply to #14

Re: Heat Exchangers and Super Heated Steam?

10/01/2007 11:45 AM

Is the primary purpose of this heat exchanger to heat the river water or to condense the superheated steam?

What is the quality of the river water? Is it raw, or do you run through a strainer, filter, or other water pre-treatment?

Where does the hot river water flow?

From your sketch, I would think have a U-tube bundle in the heat exchanger, and I think that tube fouling from hard water and river mud are the source of performance problems with water not reaching 180F. If the water needs treatment before using it in your process, I would try to relocate the treatment to be before this heat exchanger.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#23
In reply to #15

Re: Heat Exchangers and Super Heated Steam?

10/03/2007 4:31 PM

U are right. What is the quality of the River water? How hard is it?

Are the tubes ss 304/316 only or ss 304L/316L.

If ss 304/316 only then irrespective they are stainless steel rust will take place with the quality of non treated river water and this is where they are cracking.

If ss 304/316L then where they welded with Argon under controlled conditions?

There has to be an answer hidden somewhere or is he not aware of the exact type of tube material & its welding?

If he is taking as per his sketch direct to a condensate tank with no gravity flow then there will be water logging giving rise to silent hammering resulting in the cracking.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Member

Join Date: Apr 2007
Posts: 5
#16
In reply to #14

Re: Heat Exchangers and Super Heated Steam?

10/01/2007 12:37 PM

Did you try to increase the steam pressure?

Register to Reply
Member

Join Date: Sep 2007
Posts: 9
#17

Re: Heat Exchangers and Super Heated Steam?

10/02/2007 10:31 AM

It's not a U-tube bundle, it has a straight tube bundle, the water is directed by the end caps on the shell. The river water is strained, but that is all. The purpose of the heat exchanger is pretty much just to get some use out of our 5psi exhaust steam and to help warm up the raw water before it goes into our hot process softener. But super heated steam's heat transfer coefficient is not good and it is also hard on the equipment. I'm wondering if the super heated steam is the root cause for our tube bundles getting destroyed. And if so if it would be worth it to put a control valve system and a de-superheating station on the steam lines going into the heat exchanger to raise efficiency since saturated steam has a much higher heat transfer coefficient, but most of all to save our tube bundles. They are very expensive.

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#18
In reply to #17

Re: Heat Exchangers and Super Heated Steam?

10/02/2007 10:39 AM

What is the diameter, wall thickness and material of the tubes?

Have you checked on a heavier wall thickness?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#19
In reply to #17

Re: Heat Exchangers and Super Heated Steam?

10/03/2007 10:41 AM

Suggest you go to Spirax Sarco site and check up their tutorials .

Also contact both Spirax & Armstrong and they may help you out.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#20
In reply to #19

Re: Heat Exchangers and Super Heated Steam?

10/03/2007 12:32 PM

That is an excellent site.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Member

Join Date: Sep 2007
Posts: 9
#21

Re: Heat Exchangers and Super Heated Steam?

10/03/2007 2:24 PM

alrite thanks for your replys

Register to Reply
Member

Join Date: Sep 2007
Posts: 9
#22

Re: Heat Exchangers and Super Heated Steam?

10/03/2007 2:28 PM

the tube diameter is half inch made out of stainless steal, im not sure what grade and i dont know what the wall thickness is

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#24
In reply to #22

Re: Heat Exchangers and Super Heated Steam?

10/03/2007 5:11 PM

How are the tubes destroyed? cracking, bursting, warping, plugged?

If straight tube bundle, is one end free to float, or are both end fixed to the shell?

If one tube sheet is floating, is the shell surface smooth enough to allow the sheet to slide back and forth? Any irregularities to cause the floating sheet to bind up and get stuck?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Member

Join Date: Sep 2007
Posts: 9
#25

Re: Heat Exchangers and Super Heated Steam?

10/04/2007 10:07 AM

Both ends of the tube bundle are fixed and the tubes look like their bursting and cracking.

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#26
In reply to #25

Re: Heat Exchangers and Super Heated Steam?

10/04/2007 3:27 PM

You've to contact your heat exchanger manufaturer or scan google and find out some reputable manufactuer to help answer your cracking problem. If both ends are fixed then the tubes are bulgeing and cracking. Try Armstrong International - they make tubular heat exchangers and they may answer the reasons.

Soory can't help you much now but do keep posted if you get the right answer.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#27
In reply to #26

Re: Heat Exchangers and Super Heated Steam?

10/04/2007 10:09 PM

Armstrong is good, so is Bell & Gossett div of ITT.

Fixed tube sheet with large temp differences has a lot of thermal expansion stress that has no place to go. I would guess either manufacturer would recommend a U-tube bundle or a bundle with the return tube sheet with a floating tube sheet.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Member

Join Date: Sep 2007
Posts: 9
#28

Re: Heat Exchangers and Super Heated Steam?

10/05/2007 8:29 AM

How would a U-tube bundle help? Also how would a floating tube bundle help? I'm just curious. Thanks.

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#29
In reply to #28

Re: Heat Exchangers and Super Heated Steam?

10/05/2007 9:25 AM

One end of the tube bundle is fixed to the tube sheet, whilee the other end is free to expand and contract with thermal changes. A heat exchanger with both ends fixed does not have this flexibility so the tubes are stressed more. The other option would be to determine the added tube thickness needed to withstand the stress, and I'm not that smart.

For you application with raw river water, the floating tube might be a better but more costly option. The tubes can be cleaned easily in place, U-tubes have a bend that is a natural spot to collect dirt and is difficult to pass a brush through.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.