Configuring Goose in Schneider PX4 Devices

10/28/2018 1:23 PM

I am trying to configure goose messages in Schneider P443 and P546. Somehow, the files are not getting to the IEC 61850 configurator. Am a bit puzzled here.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: configuring goose in Schneider PX4 devices

10/28/2018 2:58 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Configuring Goose in Schneider PX4 Devices

10/28/2018 11:01 PM

Perhaps you could define such terms as "goose", "Schneider", "PX4", and "IEC 61850 configurator", to say nothing of "P443" and "P546". As it stands, there is no excuse for anyone to attend to such matters.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Configuring Goose in Schneider PX4 Devices

10/29/2018 12:44 PM

GOOSE is an acronym (Generic Object Oriented Substation Event) for a high speed (sub-cycle) communication packet system used in protective relaying, especially those that are protecting generators. P443 and P546 are Schneider's "MiCOM" line of protective relays; P443 is a Distance Relay, P546 is a Current Differential Relay. IEC 61850 is the general communication protocol for all protective relays. GOOSE is a subset of IEC 61850 and uses the same network, but is given priority over all other communications because its purpose is to take actions far faster than anything else.

As to why it isn't showing up in the relay configurator, that's actually a question for the Schneider Tech Support line because whatever the problem is, it will be specific to the Schneider MiCOMM equipment.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Associate

Join Date: Jun 2015
Posts: 49
#4
In reply to #3

Re: Configuring Goose in Schneider PX4 Devices

10/29/2018 1:05 PM

Thanks a lot. I have contacted Schneider support as well

Register to Reply
Register to Reply 4 comments