Kindly communicate the permissible limit of leakage current of XLPE cable.
Details.
There are 6 runs of 630 sq.mm cable connected to switchgear with 50MVA 220/6.6 KV ,Y/Y ,connected transformer with territory windings. Recently a cable was ground on LV side and Protection on HV side not operated and NGR failed.NGR with NGT at the neutral. NGR has 0.65 ohm on 100% tap. continues rating is 600 amps. .NGT ratio is 4000/400 volts.After rectification of cable new NGR was connected and brought to service.After loading it was 3amps current was at NGR. All cables connected to the system tested with Hipot test of rated voltage.The leakage current observed was 400 milliamps.
Please let me know the permissible leakage current limited in the cable and what would be the reason for failure of NGR (load resistance)
Satyanarayan