Previous in Forum: Oil Reclamation on Energized Transformer   Next in Forum: Ground
11 comments
Motor
02/27/2019 4:58 PM
Dear all
good day
6.6 kv motor the temperature of s-phase reading 25 c° above another phases
please can any one explain what are the possible reasons for this?
thanks for all
Pathfinder Tags: motor
Re: motor
02/27/2019 5:06 PM
Loose connection...
Good Answers: 804
Re: motor
02/27/2019 6:18 PM
That or bad winding insulation / turn-to-turn short on the same winding (not going to ground).
Re: motor
02/27/2019 6:28 PM
Have you checked the volts and amps on each phase? Any imbalances?
Re: motor
02/27/2019 7:13 PM
I suppose it's possible the s-phase sensor is faulty. Do they all read the same when the motor is cold (unenergized)?
Re: motor
02/27/2019 9:40 PM
You might have a very unhappy spider in the motor wiring.
Good Answers: 804
Re: motor
02/28/2019 9:59 AM
“You might have HAD a very unhappy spider in the motor wiring. “
It would be an EX-spider by now...
Re: motor
02/28/2019 10:37 AM
6 kV is three times the nominal bug zapper voltage. You're right, that spider is long gone. I wonder what is the resistivity of an exoskeleton.
Re: motor
02/27/2019 11:54 PM
Hi Asser
What do you use to measure the phase temperature of the motor winding?
NTC, PTC semiconductor, Thermister, Thermocouple, RTD. any of which can be out of calibration or failing.
Have seen RTDs fail slowly in 6.6KV fan motors.
If you can measure the windings resistance and inductance when the motor has just been shut down but still hot that may give you some results to work with.
You could hire a contractor to carry out a DLA, diaelectric loss angle test on the motr if you suspect a motor problem.
Regards Stef.
Hare today, goon tomorrow!
Re: motor
03/01/2019 4:16 AM
if the motor not working should be check the sensor but if the motor working should be check the current in each phase if the current not symmetrical check the motor
Re: Motor
02/28/2019 6:11 AM
<...can any one explain what are the possible reasons for this?...>
Yes. Someone local and armed with test equipment can. If that individual is not on the staff, then it may be worthwhile hiring someone.
Re: Motor
03/30/2019 6:35 AM
what is the sensor?platinum Resistance Temp(RTD).Check the lead wire and Socket .many possibilities are there.
Register to Reply 11 comments