30 KV Underground Cable Sizing

03/02/2019 5:44 AM

30 KV XPLE Armored cable will be installed for about 3.5 km and will be direct buried under ground, the problem it will cross the truck road twice (total distance 15 mt) and civil solution will be cable duct (cable will be buried in concrete)

Please in this case as per IEC standard, i should size the cable considering direct buried in ground and ignore the 15 mt buried in concrete?

Appreciate your advise to optimize cable cost

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: 30 KV underground cable sizing

03/02/2019 10:36 AM

Ignore.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: 30 KV underground cable sizing

03/02/2019 10:48 AM

You should have the copy at hand. Asking strangers to do this work is unethical. Cablesizer | Cable Sizing Calculations to IEC and NEC Standards

Cable Sizing Calculation - Open Electrical

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: 30 KV Underground Cable Sizing

03/02/2019 3:53 PM

The cable must be sized for the most stringent condition. Though it might be possible to splice in larger cable for the under-the-road places, it might not be practical.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: 30 KV Underground Cable Sizing

03/02/2019 5:09 PM

Seems to me the main consideration here all things being proper, is the thermal conductivity of the backfill...now to me the cable placement could be calculated to render the thermal characteristics equal in some circumstances....going from trefoil to widely spaced flat formation...

https://www.nexans.com/Corporate/2013/60-500_kV_High_Voltage_full_BD2.pdf

http://www.ijera.com/papers/Vol4_issue9/Version%206/W4906159166.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: 30 KV Underground Cable Sizing

03/03/2019 2:22 AM

NEC 2017 Art.310.60 if the ducts total length it is more than 3 m the ampacity in duct has to be considered.

310.60 Conductors Rated 2001 to 35,000 Volts.

(A) Ampacities of Conductors Rated 2001 to 35,000 Volts

(1) Selection of Ampacity. Where more than one ampacity applies for a given circuit length, the lowest value shall be used.

Exception: Where different ampacities apply to portions of a circuit, the higher ampacity shall be permitted to be used if the total portion(s) of the circuit with lower ampacity does not exceed the lesser of 3.0 m (10 ft) or 10 percent of the total circuit.

IEC 60364-5-52[for cables up to 1000 V] does not accept exception:

523.8 (523.7) Variation of installation conditions along a route

Where the heat dissipation differs in one part of a route to another, the current-carrying capacity shall be determined so as to be appropriate for the part of the route having the most adverse conditions.

__________________
Julius
Register to Reply
Associate

Join Date: Jan 2008
Posts: 44
#9
In reply to #5

Re: 30 KV Underground Cable Sizing

03/03/2019 9:17 AM

Thanks alot for your answer can you please share the same phrase of IEC but cables volt more than 1000 V (high voltage cables)

Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#6

Re: 30 KV Underground Cable Sizing

03/03/2019 6:26 AM

I won't get into cable sizing but to cross two roads, try a moaling company, I've had it done with a water pipe & it saved a stack of money.

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: 30 KV Underground Cable Sizing

03/03/2019 7:15 AM

If you ignore the ducted portion of cable and the that portion of cable runs hotter than the rest, what will happen??

It is not that if fault occurs in that 15mtrs portion, the rest of the cable will continue to function??

The total feeder will be down, isn't it!!

__________________
Raghunath
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#8

Re: 30 KV Underground Cable Sizing

03/03/2019 7:27 AM

No. Size it for the ducted section. And don't use concrete. CB sand is used.

You can use as stated previously, directional bore or a pipe jacking system to install a duct(s).

If its a busy road section, be smart and install two poles, gang links, overhead conductor and two terminations, far more cost effective, quicker and safer and offers points of isolation for future faults if the system is MV. HV, 132kV and above stay underground.

Register to Reply
Associate

Join Date: Jan 2008
Posts: 44
#10

Re: 30 KV Underground Cable Sizing

03/03/2019 9:20 AM

Dear all

I really appreciate your answers, it almost covered all the aspect about the issue i request information

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: 30 KV Underground Cable Sizing

03/04/2019 1:23 PM

British Standard 7671 gives full protocols on cable sizing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#12

Re: 30 KV Underground Cable Sizing

03/05/2019 6:45 AM

You need to determine the thermal conductivity of the back fill around the entire length of the cable,and use the worst case(hottest) point to determine the cable size.

There are formulas to calculate the soil thermal conductivity in the NEC.

A chain is only as strong as it's weakest link and proper equipment procedures for feeding and placing the cable must be followed. to prevent damage to the cable.

Installation should be supervised by a fully qualified company with experience in the field.

A 30 KV underground splice is very costly,and introduces another potential failure point.

This is a very hazardous project,and should not be performed by non professionals seeking how-to instructions from a forum.

Good luck on this venture,but don't just cross your fingers and hope for the best..get professional help.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Register to Reply 12 comments
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Bazzer Englander (1); eng.hmk (2); HiTekRedNek (1); IQ (1); lyn (1); PWSlack (1); raghun (1); SolarEagle (1); TonyS (1); Tornado (1)

Previous in Forum: Ground   Next in Forum: Generator and Capacitors

Advertisement