3 Phase Minus 1 Phase Calculation

03/14/2019 10:33 PM

If you are using heating elements on a 3 phase system, VL=415V, you connect these elements in star, which will result in 240V across these elements. What will the voltage be across these elements if you lose one phase. I know one of them will be zero, but the other two is my concern.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: 3 phase minus 1 phase calculation

03/14/2019 11:22 PM

The other 2 should be unaffected if the 3rd phase is open...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2
In reply to #1

Re: 3 phase minus 1 phase calculation

03/15/2019 12:04 AM

If the neutral is absent, each of the two remaining phases will get 207.5 V.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#3
In reply to #2

Re: 3 phase minus 1 phase calculation

03/15/2019 12:59 AM

Thank you , May I ask, how is that calculated?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #3

Re: 3 phase minus 1 phase calculation

03/15/2019 2:31 AM

415/2.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#26
In reply to #6

Re: 3 phase minus 1 phase calculation

03/24/2019 10:07 PM

That would be true if the phases were 180 degrees apart, i.e. single phase. However, they are 120 degrees apart, so the voltage across the elements is unchanged, determined by the ratio of the transformer windings, unchanged.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#28
In reply to #26

Re: 3 phase minus 1 phase calculation

03/25/2019 10:57 PM

The transformer's output voltages are unchanged, as I understand you to have said. In the presence of 3 heaters connected in a wye/star method they are 120 degrees apart with 240 volts across each heater. However, when one heater is disconnected, this central wye/star connection point shifts to be in the middle between the two remaining phases, so the remaining heaters are now effectively connected 180 degrees apart. The voltage across each one is now 415/2=208 volts (rounding up the decimal part). This is true because the original poster's question assumed that there was no other connection between this wye/star point between the three heaters and any other wires in the circuit or transformer secondary. Incidentally, the voltage between the shifted mid-point between the two remaining heaters and the disconnected output has increased to 360 volts from its former 240 volts. You can confirm my math with the trigonometry of a 30/60/90 degree right triangle, the sides being in ratio of hypotenuse = 2x adjacent side and the opposite side being 1.732x the adjacent side.

--JMM

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#29
In reply to #28

Re: 3 phase minus 1 phase calculation

03/26/2019 12:35 AM

The phase relation does not shift, it follows the supply windings, 120 deg displacement. It is still a 3 phase supply, and unless you use a phase shifting transformer, the phases will be displaced 120 deg per cycle or Hertz, as supplied by the upstream transformer or generator. The load current still flows between the two active phases, no neutral is needed to make it work, similar to a star connected motor winding. Except of course the motor will not tolerate being single phased.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#31
In reply to #29

Re: 3 phase minus 1 phase calculation

03/26/2019 8:00 PM

I had not understood before. Thanks.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #2

Re: 3 phase minus 1 phase calculation

03/15/2019 2:53 AM

And increased amperage draw on those 2 lines...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#17
In reply to #7

Re: 3 phase minus 1 phase calculation

03/19/2019 5:22 PM

SE,

I think you missed this one. These are heating elements, which are essentially resistive loads. Standard Ohm's law: I = E/R. Since R is constant, I will decrease because E was dropped from 240 down to 207.5 V. I realize there may be some non-linearity in R, but that is a second order effect.

JMM

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#24
In reply to #17

Re: 3 phase minus 1 phase calculation

03/23/2019 1:11 AM

Yes you are correct, I believe the current declines slightly....good catch

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Control Engineering - Time to take control United States - Member - New Member Engineering Fields - Systems Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Apr 2009
Location: Tampa, Florida, USA
Posts: 2129
Good Answers: 87
#25
In reply to #17

Re: 3 phase minus 1 phase calculation

03/24/2019 9:54 PM

In real life applications R is not really a constant. Most resistive elements have a resistance value that changes as a function of temperature. The change may be small enough to not make a practical difference.

__________________
J B
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#4
In reply to #1

Re: 3 phase minus 1 phase calculation

03/15/2019 1:22 AM

Thank you, but there is no neutral in the design that I mentioned.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: 3 phase minus 1 phase calculation

03/15/2019 1:48 AM

The point where the three phases come together is a neutral point, you can connect it to ground or not, it's still neutral...you have two ways to hook it up, line to line or line to neutral...

..."Once we have three line terminals and a neutral terminal, we can have two kinds of voltages:

A higher voltage (say 400V) between any two lines L₁↔L₂ (red & green) , L₂↔L₃ (green & blue) or L₃↔L₁ (blue & red).

This is called ‘Line Voltage’ or Line to Line Voltage.

A lower voltage (say 230V) between any one line and the neutral ( L₁↔N (red & neutral), L₂↔N (green & neutral) or L₃↔N (blue and neutral) .

This is called ‘Phase Voltage’ or Line to Neutral Voltage."...

If you're using the lower voltage hookup, like you said, then you are line to neutral...

https://www.quora.com/What-is-difference-between-line-to-line-voltage-and-line-to-neutral-voltage

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #4

Re: 3 phase minus 1 phase calculation

03/15/2019 3:54 AM

In that case, the voltage across two of the elements will drop to half the supply voltage (=415/2) and the voltage across the third will be unchanged.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: 3 phase minus 1 phase calculation

03/15/2019 8:36 AM

Correction: if they are connected in star, then the voltage across two of them in the absence of a neutral will be 415/2, assuming identical resistances, and across the third, zero.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#27
In reply to #9

Re: 3 phase minus 1 phase calculation

03/24/2019 10:13 PM

( see #26)

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#12
In reply to #4

Re: 3 phase minus 1 phase calculation

03/15/2019 10:25 PM

there is always a neutral of the 3 phases, maybe no wire, but on ac circuits, it is established capacitively. If there is some disturbance, like a ground fault, then the line to ground voltage will change. The line to line voltage will remain according to the transformer ratio, not arithmetically to half of the line to line voltage, regardless of other posts.

Register to Reply
Power-User

Join Date: Apr 2013
Posts: 188
Good Answers: 1
#13
In reply to #4

Re: 3 phase minus 1 phase calculation

03/16/2019 12:52 AM

If there is no neutral, then it must be a Delta connection.

Register to Reply
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#14
In reply to #4

Re: 3 phase minus 1 phase calculation

03/16/2019 1:23 AM

If there is no neutral, then how can you have heating ? If you omit a neutral line, then you just have an element.

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #14

Re: 3 phase minus 1 phase calculation

03/22/2019 8:10 AM

Er, um, one can have two elements in series across 2 phases.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#16
In reply to #4

Re: 3 phase minus 1 phase calculation

03/16/2019 7:46 AM

The neutral point is virtually grounded even not physically connected to ground when the loads are distributed equally in the system..

__________________
vsar
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19
In reply to #16

Re: 3 phase minus 1 phase calculation

03/22/2019 8:12 AM

That's abstruse.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#21
In reply to #19

Re: 3 phase minus 1 phase calculation

03/22/2019 11:54 AM

Sorry PWSlack, what I meant was, the neutral point in a balanced star configured 3-phase system is virtually sitting at a ground potential..

The neutral wire being at zero potential can be considered grounded, as long as the loads are balanced, Even when not physically connected to the grounding point of the circuit..

__________________
vsar
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#22
In reply to #21

Re: 3 phase minus 1 phase calculation

03/22/2019 8:20 PM

Vsar,

In the electrical trade, the word "grounded" has a very specific definition and intent when used. Even if the neutral wire is at zero potential, it is NOT GROUNDED unless there is a physical connection between this wire and ground at the source of supply such as the service disconnect enclosure or at the source of supply if a separately derived system. Because the neutral wire must be treated as a current carrying conductor, it is only bonded to ground at the service disconnect... Everywhere else in a structure the unbalanced current it carries (due to the resistance of the wire and the current flowing through it) will cause its voltage to be different than the ground voltage.

The original poster of the question was talking about a 3-phase circuit with three equal loads connected together in a star (wye) configuration. The midpoint of this star/wye can act like a neutral, but is not connected to any neutral conductor in the building. In the original post, the question was what would happen to this midpoint of the star/wye when one of the three connections through a heater was lost. At that point, its voltage will shift from a fairly low voltage (close to ground, but not necessarily exactly so) to approximately 120 volts from ground! That definitely is NOT a voltage you would want to see on a neutral. --JMM

Register to Reply Score 1 for Good Answer
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#23
In reply to #22

Re: 3 phase minus 1 phase calculation

03/22/2019 8:48 PM

Jmueller-

I am 100% in agreement with what you stated..

for that very same reason why (in my very first comment), I described that neutral point to appear as a virtually grounded point...Which would be true only As long as the loads are balanced..

Thank you..

__________________
vsar
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#10

Re: 3 phase minus 1 phase calculation

03/15/2019 9:31 AM

It all depends what you mean by "lose one phase." If the one heating element becomes disconnected from its phase voltage source, it is just hanging there off the star point. It has no voltage across it because its circuit is open. The other two elements will still have the same 240V across each one because the phase relationship of their sources remains the same.

If the "lost" element instead becomes shorted, then you are applying its phase voltage to the star point. Then each of the other two elements will have 415V across them.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11

Re: 3 Phase Minus 1 Phase Calculation

03/15/2019 12:20 PM

It all depends on how you lost that phase.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #11

Re: 3 Phase Minus 1 Phase Calculation

03/22/2019 8:13 AM

Some people are so clumsy...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#30
In reply to #11

Re: 3 Phase Minus 1 Phase Calculation

03/26/2019 9:05 AM

It seems that nobody grasped my comment that it all depends on how one loses a phase.

  • If the phase is lost by a break in the wiring between a sound working delta transformer and the resistive star connected heater load then you get the scenario most have discussed.
  • If the phase is lost upstream of the delta transformer then a different scenario happens.
  • If the phase is lost due to an earth fault of one of the transformer output phases a different scenario will occur. Hopefully, circuitry protection will automatically respond to this condition eventually but it is good to understand what the condition is before breakers trip.
  • If an unbalanced load on the failing phase is causing the loss in the core due to saturation.

Each of these scenarios will produce a "phase lost" condition with different voltage results.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 806
Good Answers: 65
#15

Re: 3 Phase Minus 1 Phase Calculation

03/16/2019 3:18 AM

I believe that the statement that when the heaters are connected in star then the above hold true that the heaters will only have 240V RMS across them if the neutral point of the heaters is connected to the neutral point of the supply transformer which would be a star delta connected transformer where the HV of the transformer is connected in delta and the secondary is connected in start where the output of the phase windings on the LV side has a relationship of 240V RMS to the neutral point.

If star point of your star connected heaters are not connected to the star point of the transformer then the star point of the heaters may not be at the same voltage as the star point of the transformer.

When one phase is lost what was the star connection of the heaters becomes the center point of a resistor divider network connected to 415V RMS. To work out the voltage at any instant of the waveform add the peak values of the two remaining phases and multiply by 0.707 to obtain the RMS value. Peak value = 1.414 times the RMS value.

So the common point of the two heaters floats around when referenced to the transformer neutral subject to the individual heater resistances. Nominally the heaters would have 207.5V RMS across them which means that the heater center point could be 40V RMS when measured against a transformer neutral.

__________________
Hare today, goon tomorrow!
Register to Reply
Register to Reply 31 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

eltech (2); Jacko the Aus (1); JBTardis (1); jmueller (4); PeterT (1); PWSlack (5); redfred (2); rwilliams (4); SolarEagle (4); Stef (1); tonyhemet (1); Tornado (2); vsar (3)