Anonymous Poster #1

Gas Insulated Substation

03/21/2019 7:12 PM

Dear Sirs,

If we have two voltage levels, say 132 kV and 220 kV - and we intend to keep GIS for both of them in double bus system, both of them can be kept in same finished ground level or they can also be kept in different finished ground level ?

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#1

Re: Gas Insulated Substation.

03/21/2019 8:46 PM

Separation of some sort might be helpful for equipment identification, also for if one substation goes up in flames, it doesn't burn up its neighbor.

Local codes may have something to say about this, perhaps risk of flood or earthquake.

Without any detail, such as indoor or outdoor, levels above and below, lateral displacement or superimposed, transformer insulation medium, other risk factors; the elevation obove or below some datum point should be inconsequential.

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Gas Insulated Substation.

03/22/2019 4:06 AM

What does the rest of the <...we...> have to say about this?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Gas Insulated Substation

03/22/2019 8:30 AM

From an electrical perspective, there is nothing that I know of that would prevent you from having the different voltage level equipment at different physical elevations, assuming you can make all the necessary physical connections and meet electrical safety clearances. Electrons don't care if they have to flow up, down, or sideways.

As for the physical construction, the factors to consider depend on whether this equipment is in an enclosure/building or outdoors.

In a building, you need to provide access for personnel, for service and maintenance equipment, and probably an overhead crane to lift/move equipment for installation, repair/replacement, etc. You have to consider where control wiring has to run, and how to meet equipment clearances from the structure.

Outdoors you also have to consider things like vehicle & crane access, personnel safety when you have changes of elevation (slopes/drop-offs, etc.), effects of climate (Does it get icy in winter? Water runoff in rainy season?), and other such factors.

But all of this has to go into your design. It may not prevent you from doing what you propose, but it will affect how you design your station.

__________________
To get the right answers, first you need to ask the right questions.
Reply Score 1 for Good Answer
Anonymous Poster #1
#4
In reply to #3

Re: Gas Insulated Substation

03/22/2019 9:03 AM

What about the electrical earthing grid to be provided at 0.5 m below the ground. If the two GIS (of 132 kV and 220 kV) are at elevation difference of say 3 metres.

Best Regards,

Reply
Anonymous Poster #2
#5
In reply to #4

Re: Gas Insulated Substation

03/22/2019 9:15 AM

You probably need an Electrical Engineer to look at this locally. Hire someone?

Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #5

Re: Gas Insulated Substation

03/24/2019 5:29 AM

Off topic? That’s amusing!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Off Topic (Score 5)
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#7
In reply to #4

Re: Gas Insulated Substation

03/22/2019 11:38 AM

Treat each one separately, the depth is to get good conductivity. If one substation has a higher exposure to lightning, maybe not interconnect the arrester earth leads...

Reply Score 1 for Good Answer
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#10
In reply to #4

Re: Gas Insulated Substation

03/23/2019 9:18 AM

What do you propose or suspect will happen with the earth mats/grids? If there is a massive earth fault, where do you think it will go?

Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#11
In reply to #10

Re: Gas Insulated Substation

03/23/2019 9:03 PM

It always returns to the source of the power, or the potential opposite, such as a cloud and the earth.

Usually the system protection will open the faulted circuit, or the weakest link conductor in the return path burns clean, or the potential of the cloud/earth equalizes to a level insufficient to ionize the air between.

That's why you may want to keep your transformer arrester ground leads somewhat separated, so the surge on one line doesn't show up cleanly at the other arresters, while in the process of carrying discharge current. A well designed ground grid for each power system should reduce the cross communication between the two systems

Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#12
In reply to #11

Re: Gas Insulated Substation

03/23/2019 10:19 PM

I think you missed the point, What difference will a 3m elevation make to an earth mat? What difference is going to be made if the stations are in close proximity to one another? (20-200m for instance). If they are km's away of course it will change, as the soil resistance will change.

If the 132kv is next to a 220kV yard the earth mats will definitely be connected and commoned. No matter what elevation.

I don't want to be in a station that has an earth connection that burned clean.

Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#13
In reply to #12

Re: Gas Insulated Substation

03/24/2019 12:13 AM

I think maybe you are needlessly over-analyzing the situation with no facts. Your audience also can be of little help with the ambiguous configuration you present. The resistivity of the soil with respect to the distance to the center of the earth will be unmeasurable in the 3 meter range you are talking. Without details on the configuration and equipment, the soil composition and resistivity, a ground fault may or may not pass through the equipment between the two substations. For instance, if there is a risk of fault current between the two substations, plus walking access between the two, you need to design for low touch and step potentials along the communication path.

Your grounding system carries little to no current under normal conditions. If you drop a line conductor on to the ground, then it may conduct back to the power source, it may not, depending on many different conditions that you have not considered.

The method you use to interconnect the adjacent ground grids should take into consideration the possible fault locations and types, and you will generally want to avoid direct interconnection (copper to copper) of your lightning arrester ground leads, for example. If your grounding is correctly designed, it will be unnecessary to interconnect them other than the earth between them.

If the line drops on to the structure supporting your insulators, the current will flow back to the source directly through the copper or concrete electrodes and bonding you have designed, the short term current rating is sized to allow full possible fault current and clearing before melting. That design is what will prevent your system from burning your ground conductor clear. However, it is possible and probable under some conditions, one of your ground connections will fail. You need to consider that in your design as well.

Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#16
In reply to #11

Re: Gas Insulated Substation

03/24/2019 6:36 AM

Original hypothetical question: 'What about the electrical earthing grid to be provided at 0.5 m below the ground. If the two GIS (of 132 kV and 220 kV) are at elevation difference of say 3 metres.' (10 feet)

I am now intrigued as to why an elevation of 3m (9.89feet), would make a significant difference on an earth mat in any substation/switchyard?

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#19
In reply to #16

Re: Gas Insulated Substation

03/24/2019 9:09 AM

Well obviously the lower substation will naturally have better lightning protection since the upper substation will be the lightning rod for the area.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#20
In reply to #19

Re: Gas Insulated Substation

03/24/2019 10:01 AM

How you wish that were true. We may as well have chocolate teapots or a trap door in canoes.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#21
In reply to #20

Re: Gas Insulated Substation

03/24/2019 10:27 AM

Will the canoe trap door be how Hiawatha gets into his shallow draft submarine?

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#22
In reply to #21

Re: Gas Insulated Substation

03/25/2019 6:14 AM

Submarine for elevated water ways, Hiya-Waters submarine, complete with chocolate teapot, skylight and trap door in case it requires push starting while submerged.

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #10

Re: Gas Insulated Substation

03/24/2019 5:27 AM

It will go through a circuit protection device, which will disconnect it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #4

Re: Gas Insulated Substation

03/24/2019 8:16 AM

Earthing can be improved by releasing a large quantity of seawater over the earthing mat.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#18
In reply to #17

Re: Gas Insulated Substation

03/24/2019 8:45 AM

That improvement is a bit fishy.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #3

Re: Gas Insulated Substation

03/22/2019 10:51 AM

Just because Physics says you can do something, it doesn't mean that one should do that thing.

This all depends on what electrical codes should be followed. Determining which electrical code should be followed requires knowing where this installation will be placed.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #6

Re: Gas Insulated Substation

03/22/2019 12:57 PM

Anonymous Poster Land is an exceptionally large place...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#9

Re: Gas Insulated Substation

03/23/2019 7:28 AM

Is this 220KV primary, onto a Tfx of secondary 132kV? Is this for a harsh environment where the GIS is indoors as GIS outdoors would be a total waste of investment. What are the limitation on using Air Insulated bars?

Many stations are build on two levels, it all depends on the Geotech results and cost of remediations, if its level or terraced.

Your poorly worded question here, will draw poor results and misleading information.

"IF we have..", then you say "we intend to.." It makes me doubtful of your facts.

If you build your station on a slope, put the 220 above, and the 132 below, gravity will assist the flow of electrons, as it is all downhill.

Reply
Reply to Forum Thread 22 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); IQ (7); PeterT (1); PWSlack (5); redfred (3); rwilliams (4)