Motors Applications

06/10/2019 4:31 AM

Can any one suggest me on the below.

we are operation a equipment which requires 30hp 4 pole Duty type S1.

whereas due to some technical error from the supplier we received 30hp 4pole duty type S4.

When i asked for the replacement they said due to non availability it will take a month to replace.

So, Can i use S4 duty motor instead of S1?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Motors Applications

06/10/2019 5:55 AM

It depends upon the application, the details of which have been withheld from the forum.

https://www.engineeringtoolbox.com/iec-duty-cucles-d_739.html

<...due to non availability it will take a month to replace...> Only if the supplier doesn't value the level of business that is being conducted. Getting someone from the buying function onto the case, in order to expedite, would seem like a good idea, as a threat to take the business elsewhere can do wonders to clear log-jams. Escalate it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2019
Posts: 3
#2
In reply to #1

Re: Motors Applications

06/10/2019 6:12 AM

yeah mine was continuous duty whereas S4 was intermittent periodic duty.

but i want to run the S4 motor for continuous duty application.

what was the worst damage can happen if i operate S4 instead of S1?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Motors Applications

06/10/2019 6:27 AM

The <...worst damage can happen...> is that it will burn out.

<...yeah mine was continuous duty whereas S4 was intermittent periodic duty.

but i want to run the S4 motor for continuous duty application...> This information was stated in the original posting and there is no need to repeat it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Motors Applications

06/10/2019 8:06 AM

I agree with PW and expect your continuous use of a motor designed for intermittent use will prematurely burn this motor out. From a purely engineering perspective I would be surprised if this S4 motor will burn out during the months it will take to get an S1 rated motor from this vendor or another vendor, but it might.

From a business perspective, if your purchase order unambiguously requested an S1 motor by rating designation or specific model number then the vendor should offer some mitigating scenario to keep your business. If they don't then buy the correct motor and all future parts from another vendor.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Motors Applications

06/10/2019 9:36 AM

One might wonder why the motor was not rejected at any pre-despatch inspection that took place or upon arrival.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7
In reply to #5

Re: Motors Applications

06/10/2019 10:17 AM

Yes, there are many under explained layers to this motor misapplication.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#10
In reply to #5

Re: Motors Applications

06/11/2019 1:32 AM

Good question.. hardly off topic.
Either the vendors dispatch should have caught it or goods receiving!

__________________
The square root of nothing is what you make it!
Register to Reply
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: Motors Applications

06/10/2019 10:13 AM

The motor might be ok in this application, the only way to know for sure is to monitor the temperature, if the motor starts to overheat you should be prepared to increase air flow through windings,,,.

https://electrical-engineering-portal.com/10-duty-types-three-phase-asynchronous-motors

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Motors Applications

06/10/2019 10:36 PM

If someone else made the mistake, tell them they owe you a correctly specified motor and run this one until it arrives as payment for your trouble, then let them decide if they want it back (if it holds up).

if YOU made the mistake and you cannot return this motor, order the new one and run this one to destruction, hoping that is not going to happen until after the correct one arrives.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9

Re: Motors Applications

06/11/2019 12:12 AM

Continuous duty is not necessarily or always the most severe application. Frequent restarts, especially jogging or plugging, can be worse.

You might need to run your motor continuously, but will it be fully loaded all the time? If not, you might be O.K., but it could be worth discussing with the motor mfr.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#11

Re: Motors Applications

06/11/2019 3:06 AM

Big difference.S1 are continuous duty,S4 are not.

Here is a link that explains the difference in types,with graphs.

https://electrical-engineering-portal.com/10-duty-types-three-phase-asynchronous-motors

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 806
Good Answers: 65
#12

Re: Motors Applications

06/11/2019 5:41 AM

The problem is that the S4 motor is for periodic duty while the S1 is for continuous duty. The running of an intermittant rated motor continuously is the heat build up in the windings from the copper and iron losses and the inability to remove the heat will cause insulation and winding failure and most likely in a very short time which could be less than a day.

My advice from experience is don't even contemplate running the S4 motor in continuous duty S1. Return the motor to the supplier and get one from someone who has read the specifications on your order and can supply an S1.

Remember motors are driven by smoke and once the smoke escapes the motor is dead.

__________________
Hare today, goon tomorrow!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13

Re: Motors Applications

06/12/2019 12:35 PM

I think you can use the S4 duty motor as S1 if-in order to not overload the motor and the maintain the same relative thermal life expectancy [see IEC 60034-1 Annex A] you may reduce the load.

Since the temperature rise in a motor is proportional to the losses the total equivalent current will be Ieq=sqrt((I1^2*t1+I2^2*t2)/Tc) where:

Ieq = continuous load duty S1 equivalent current; I1 is the constant load current multiplied by t1 the time in which I1 is acting, I2 is the starting current and t2 is the starting time. Tc it is one cycle load time. Translated in power units:

Peq=Prated*sqrt((t1+(Ist/Irated)^2*t2)/Tc)

In my opinion for Tc=10 minute t1=2 sec and (Ist/Irated)=8 for 25% 30 hp S4 19hp it could be S1 equivalent

However, the manufacturer has to declare what is the real equivalent S1 duty power for the delivered S4 duty motor.

__________________
Julius
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); brich (1); HiTekRedNek (1); JRaef (1); PWSlack (3); Raghav4593 (1); redfred (2); SolarEagle (1); Stef (1); Tornado (1)