Power Problem

06/10/2019 1:10 PM

I have a decent background in electronics and controls but not in high voltage systems.

I have a customer site where I need to place a 230 VAC, 1P compressor. All they have available is 480/277 3P.

This is my plan: Feed a suitably size 277V-to-230V transformer using one leg of the 480 and a neutral (or ground). This should give me 230VAC, 1P.

Anyone see any holes in this plan?

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Power problem

06/10/2019 1:27 PM

No problem with the concept, as long as the transformer and wiring is properly sized for the load....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #1

Re: Power problem

06/11/2019 7:09 AM

Indeed. The OP would do well to have a local qualified Electrician review the proposed installation and properly assess the cabling and overload protection. In the UK, such individuals would be following the provisions of BS7671, which gives full protocols for a safe and correctly-documented installation that would satisfy the end-user's fire indemnity insurance provider.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Power problem

06/10/2019 1:28 PM

This will result in an unbalanced load, probably slight enough not to be a problem. If you use a 480/240 transformer on two phases, the imbalance will be less. If there already is a small imbalance, you could take advantage of it by adding the new load to the least loaded of the existing phases.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Power Problem

06/10/2019 2:41 PM

The principle involves putting an unbalanced load onto the supply. All single phase connections present imbalance and the trick is to spread them around the phases so as to minimise the neutral current. So the proposed installation should not be viewed in isolation.

The detailed design of the arrangements lies squarely in the domain of the Electrical Engineer. If the requisite skills are not to hand, then for safety's sake the deployment of someone who does has them would be highly recommended as a minimum, and mandatory in some jurisdictions.

And <...480/277 3P...> is not <...high voltage...> as the boundary between "low voltage" and "medium voltage" is generally taken as 1000V; from the information presented the proposed installation lies entirely in the "low voltage" domain.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
6
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Power Problem

06/10/2019 4:50 PM

480 to 240V transformers are very very common. 277 to 240V transformers are likely special order because almost nobody does it that way. There is zero advantage to trying to use 277V L-N vs 480V L-L to feed your transformer.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 6)
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#19
In reply to #4

Re: Power Problem

06/11/2019 1:07 PM

480V L-L it is then. Thanks for the advice.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: Power Problem

06/10/2019 5:07 PM

Under no circumstances should this transformer be connected between a phase conductor and a "ground" this would fail inspection and present a serious shock hazard.

Grounds (or a bonding conductor) are only permitted to carry current during a fault event and will do so only until the overcurrent device opens to clear the fault.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#24
In reply to #5

Re: Power Problem

06/13/2019 3:28 PM

FYI:

Please note,there is a big difference between an equipment bonding conductor,and a Grounded conductor.The terms lead to much confusion even among experienced electricians.GROUNDING conductor is the equipment grounding conductor.It is connected to a separate bus bar terminal in the panel,not to the neutral bus bar terminals.The GROUNDED conductor is connected to the ground rod.The Grounded and Grounding conductor are bonded together in the main panel only,but in sub fed panels,they must not be bonded together.In single phase systems,the Grounded conductor is used as the neutral,and carries the unbalanced load,but the Grounding conductor is to prevent shock hazards from the equipment and carries no current except in a fault condition.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Active Contributor

Join Date: Feb 2018
Posts: 13
#6

Re: Power Problem

06/11/2019 1:48 AM

The first question is how large is the 1P compressor motor? That will determine the size of the transformer. The second item is a 277V to 230V transformer exists somewhere, but it will be expensive. It would be a better choice to get a standard 480V to 230V single phase step down transformer and just wire it between any two of the three legs of your 480V source. Please note that a neutral is NOT the same as a ground.

Register to Reply
Power-User

Join Date: Aug 2010
Location: Wales, UK
Posts: 391
Good Answers: 18
#17
In reply to #6

Re: Power Problem

06/11/2019 11:38 AM

Hi Rick,

Usually 3 HP but some manufacturers do a 4 HP.

__________________
Best advice I can give as you get older "Never miss an opportunity to relieve yourself"
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#7

Re: Power Problem

06/11/2019 2:52 AM

It is illegal for anyone to perform electrical installation or repair unless properly licensed in the state of Florida, or one of the reciprocal states. Do you know the difference between Grounded, and Grounding conductor? If you are licensed, consult your local inspector, or AHJ. They will be glad to advise you. If you are not licensed, you are subjecting yourself to potential liability if something goes wrong.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#15
In reply to #7

Re: Power Problem

06/11/2019 11:14 AM

We work worldwide. This site is not in Florida.

We are not installing the transformer, just providing it.

The compressor is for a bulk CO2 storage vessel, it is 1 HP.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Commentator

Join Date: Apr 2018
Location: Newtongrange (10 miles from Edinburgh, Scotland, UK (1,000,000 miles from the real world)
Posts: 63
Good Answers: 1
#16
In reply to #15

Re: Power Problem

06/11/2019 11:20 AM

Are you able to say which country or even continent, this thing is to be installed in?

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#20
In reply to #16

Re: Power Problem

06/11/2019 2:00 PM

It will be here in the US.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#18
In reply to #15

Re: Power Problem

06/11/2019 11:52 AM

You still need to have the customer tell you if phase to neutral or phase to phase is required or if it does not matter. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 806
Good Answers: 65
#8

Re: Power Problem

06/11/2019 5:29 AM

Probably from a cost point of view why not just replace the single phase motor with a 480V 3P motor and Appropriate 3 P pressure switch. Here 3P motors are as cheap as chips much cheaper than either 1 P motors or transformers and the transformer needs adequate fuse/ CB protection all adding to the cost.

3P motor removes the imbalance problems.

__________________
Hare today, goon tomorrow!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#11
In reply to #8

Re: Power Problem

06/11/2019 6:17 AM

Stef. Good idea!

Although from my experience of compressors, the OP needs to be aware that the motor could be a 'special' with a mounting frame to give correct alignment and fit of drive shaft couplings. ...something the manufacturer might supply - but at a price.

Still, a good idea.....an option I would explore first.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Commentator

Join Date: Apr 2018
Location: Newtongrange (10 miles from Edinburgh, Scotland, UK (1,000,000 miles from the real world)
Posts: 63
Good Answers: 1
#9

Re: Power Problem

06/11/2019 5:35 AM

I'm told that there are no daft questions but this might come close: what is the supply frequency on the rating plate of the compressor and of your 480V supply?

I only ask because 230V 50Hz is the normal single phase supply in Europe and 480V 60Hz is, I think, the normal 3ph supply in North America.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21
In reply to #9

Re: Power Problem

06/12/2019 10:57 AM

See #20⇑.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#22
In reply to #9

Re: Power Problem

06/13/2019 11:14 AM

In my opinion you have a network of 400 V and 50 Hz [U.K.] and a motor of 480 V and 60 Hz. That means, since 400/50=480/60 the motor has to work well.

__________________
Julius
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Apr 2018
Location: Newtongrange (10 miles from Edinburgh, Scotland, UK (1,000,000 miles from the real world)
Posts: 63
Good Answers: 1
#23
In reply to #22

Re: Power Problem

06/13/2019 12:23 PM

The 230V/ 50Hz is a red herring as we know now that the plant is in the US. A single phase supply from 480V/ 60Hz supply would be 276V/ 60Hz. The options are then:

  1. replace the motor with a 1ph 276V 60Hz m/c or
  2. use a 3ph 480V 60Hz m/c.

The load is only 1hp so the higher efficiency of a 3ph m/c bill be outweighed by the additional cost of control gear, A 2.7A out of balance load should be tolerated in a well designed industrial distribution system so the single phase motor is probably the one to go for.

That only leaves the mystery of the 230v 60Hz motor. That would need a transformer as the fluxing level would be different. Protection of the system with regard to neutral points and earthing has taxed better minds than mine in this thread so that is clearly also a concern. You are right, a 400v 5Hz motor would be happy on a 480v 60Hz supply, electrically at least; whether the compressor would be happy with the over (or under) speed is a different matter. When I lived in Japan in the 1990s many of my American friends bought Japanese domestic market white goods that ran on 100V/ 50Hz, took them home on repatriation and ran them on 110V/ 60Hz perfectly happily. Unless there is a power network in North America that uses 400/230V 60Hz for low voltage distribution, I am struggling to understand how or why one would use such a machine. I look forward to being educated!

Register to Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#10

Re: Power Problem

06/11/2019 5:50 AM

Here is a group who would know better than many of us engineers. They are a mixture of licensed Electricians as well as electrical inspectors (ie AHJs). Their job is to be safe and legal.

https://www.electrical-contractor.net/forums/ubbthreads.php

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#13

Re: Power Problem

06/11/2019 9:58 AM

This is a question for the customers chief engineer or head of facility maintenance. In the absence of either it will depend on the phase balance of the customers' electric system. If that is unknown, it must be measured before an answer can be given. There can be either a situation where you MUST use one phase to neutral and others where you MUST use line to line (phase to phase). You cannot use a general rule to make this determination. As others have mentioned, be sure you have a good understanding of the difference between the neutral and ground, the proper way to ground a separately derived system, and the required disconnecting means both upstream and downstream of the new transformer. Pretty simple stuff for most electricians. - JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru
Engineering Fields - Engineering Physics - New Member

Join Date: Oct 2006
Location: MSP, MN
Posts: 728
Good Answers: 8
#14

Re: Power Problem

06/11/2019 10:13 AM

I used a motor-generator set when we built systems for foreign countries and had to test them here. As I recall, they are cheap and reliable, and completely isolate the load from whatever power you have: M-G set

Here's a list of folks who make them: M-G makers

Register to Reply
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: