Stator Test Results

06/12/2019 2:25 PM

Dear all

we test main stator for old generator 35MVA,5KV manufactured in 1973 by megger

5kv the insulation resistance result is 37MΩ.are this result acceptable or not

because its old generator and we dont have the test report to compare the result.

Thanks for all

Register to Reply
Pathfinder Tags: stator test
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: stator test

06/12/2019 2:57 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5
In reply to #1

Re: stator test

06/13/2019 5:35 AM

Sorry,SE

When I first read the OP,there were no replies,so I googled for info.While I was googleing,you were posting.I did not reload the page before I loaded my reply .If I had I would have seen your reply,and I would not have duplicated the effort.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#2

Re: Stator Test Results

06/12/2019 3:07 PM

Here is a link to information that will probably answer all of your questions.

At first glance, according to the limited information you provided,the generator is ok,but there are other factors to consider before giving it the green light.

Read the information on the link and you will gain an in depth knowledge of the process.

Good luck!

https://www.instrumart.com/assets/Megger-insulationtester.pdfhttps://www.instrumart.com/assets/Megger-insulationtester.pdf

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 806
Good Answers: 65
#3

Re: Stator Test Results

06/13/2019 2:07 AM

If I came across readings as low as 37M Ohm for a 5KV generator of that era 1973 I would recommend a drying out in an oven or with space heaters as the slot insulation may have absorbed moisture. From testing similar equipment the resistance at 5KV should be at least 200+M ohms though for 3.3KV up we used a 10KV Trimax brand insulation tester and recorded the resistance at 1 minute and 5 minutes intervals.

Do you know what form of insulation is used on the windings, paper, enamelled, varnished cloth?

When heating the stator, we took the temp to 70 deg C, measure the insulation hourly and you will find that if it is moisture the resistance firstly high will fall as the moisture migrates through the windings and then rise again as the windings dry out. After drying the stator should be varnished but that may be impractical.

__________________
Hare today, goon tomorrow!
Register to Reply Score 1 for Good Answer
2
Active Contributor

Join Date: Jan 2016
Posts: 16
Good Answers: 1
#4

Re: Stator Test Results

06/13/2019 5:24 AM

To really know if a stator is OK, the megger is only the start. If you get a good polarization number, then your stator is good enough to do all of the rest of your testing. If all of those tests are OK, the over-potential (Hi Pot) test gives you relatively high confidence that the stator will not fail, soon, in service.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Stator Test Results

06/13/2019 1:21 PM

If it is not known beforehand where the OK/Not-OK boundary lies, then why bother carrying out a test at all?

Without a test protocol, all that has been obtained, is a measurement.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

HiTekRedNek (2); Power Prof (1); PWSlack (1); SolarEagle (1); Stef (1)

Previous in Forum: Power Problem   Next in Forum: Greasing Method for Ball Bearings

Advertisement