RTD 3 Wires Max Cable Length

07/10/2019 1:36 AM

Hi All

As i understand, the three wire PT100 RTD is used to eliminate the effect of wire resistance for long distance, which will improve measurement quality, but i am still doubt if i connect the three wire PT100 RTD for a length of 400 meter between the motor and the relay inside substation.

Can somebody comment please?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: RTD 3 wires Max cable length

07/10/2019 2:59 AM

This should clear any <...doubt...>.

The alternative to the installation as described is to mount the transmitter close to the RTD and transmit the temperature as an industry-standard 4-20mA signal. The proverbial "two bits of wet string" will convey 4-20mA.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: RTD 3 wires Max cable length

07/10/2019 4:25 AM

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: RTD 3 wires Max cable length

07/10/2019 4:33 AM

Several Motor Protection Relays offer an RTD module that is mounted near the motor and then has a fiber optic cable connection back to the relay. That’s what I like to use. Virtually unlimited distance.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4

Re: RTD 3 Wires Max Cable Length

07/11/2019 5:44 PM

The information I have seen says:

  • If you have to keep the length long, use 4-wire RTD cable.
  • For long lengths be prepared to have induced signals on the wire, so use shielded cable.
  • Put the transmitter near the RTD and use a much more standard 4-20mA, 0-20mA, or similar signal method.

--JMM

Register to Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#5

Re: RTD 3 Wires Max Cable Length

07/12/2019 1:01 AM

What resistance can your RTD input handle?

A major vendor’s PLC/PAC analog input spec for Pt100 RTD states a maximum of 40 ohms resistance in the lead wires.

400m distance is 800m out-and-back.

20g copper is 0.0333 ohms/meter, which is 26.6 ohms over 800m, the working limit.

22g copper is 0.0530 ohms/meter, which is too high a resistance for this AI at 42.4 ohms over 800m.

I’d be looking at a temp transmitter.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#6

Re: RTD 3 Wires Max Cable Length

07/15/2019 12:42 PM

3 wire RTD measurement assumes that the wiring voltage drop across each lead is equal. A 4 wire measurement will produce the best accuracy.

In theory, 400 meters of cabling length will not significantly affect 3 or 4 wire measurements. In practice, you may start getting false readings at these lengths. The unknowns of non-linear common-mode rejection, filtering, noise sources, and measurement source ranges makes it impossible to predict if this is a signal run too far.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#7

Re: RTD 3 Wires Max Cable Length

05/13/2023 11:16 AM

I know this thread is more than three years old but I'll just give my answer anyway.

The rule of thumb is 200 feet or 61 meters for three-wire RTD's. The actual distance depends on the size of the wire. 18AWG is the usual size.

You also need to use a shielded three-wire cable, not three separate wires. This avoids differences in manufacturing and also ensures that the lengths are as equal as can possibly be. The shield protects against interference especially if you use the whole 200 feet.

The right thing to do, however, is to use a temperature transmitter with a 4-20mA output. Rule of thumb for 4-20mA current is 1000 meters so this should fit your requirements nicely. Use a two-wire shielded cable #18AWG.

Note: using the three-wire method does not "eliminate" the lead resistance. It just minimizes it. We once experimented using the three-wire method and found that the error due to lead wire resistance increases with distance. At 200 feet, the error can exceed one degree Celsius.

Remember also that copper wire is also temperature sensitive. A long wire run that is exposed to the sun will cause your lead resistance to change increasing your error.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bud (1); jmueller (1); JRaef (1); PWSlack (2); redfred (1); Vulcan (1)

Previous in Forum: Foundations, Column and Beams in Substation Control Building   Next in Forum: Testing of Reverse Power Relay

Advertisement