3P or 4P ACB in Outgoing Feeders for TN-S system

08/21/2019 2:49 PM

In a L.V. Switchboard for TN-S system, apart from the Incomers & Bus-Couplers need to be 4P ACB, is it necessary to have 4P ACBs for Outgoing feeders as well? If so why?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: 3P or 4P ACB in Outgoing feeders for TN-S system

08/21/2019 3:22 PM

Depends on the load characteristics and the grounding scheme...

https://cr4.globalspec.com/thread/26706/3-pole-or-4-pole-or-TPN-ACB-Air-circuit-breaker

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
4
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#2

Re: 3P or 4P ACB in Outgoing feeders for TN-S system

08/22/2019 1:32 AM

If the load is 3-phase balanced load such as a motor, there is no reason why you need to take neutral to the load. In such a case, the ACB can be three pole.

Idea is not to allow neutrals to be mixed up at any location.

Secondly, when there are single phase loads directly connected to the switchboard, it is possible that the neutral can assume some voltage due to unbalanced loading condition (among three phases) and hence needs to be isolated while shutting down the load downstream, for reasons of safety.

__________________
Raghunath
Register to Reply Good Answer (Score 4)
Participant

Join Date: Aug 2019
Posts: 2
#4
In reply to #2

Re: 3P or 4P ACB in Outgoing feeders for TN-S system

08/23/2019 3:14 AM

Thanks. There are a few lighting loads distributed equally & normally balanced.

The neutrals are no getting mixed up as Incomer & Bus-Coupler ACBs are 4P.

However in a given Bus section, since Outgoing feeders are all 3P & Neutral continuous, when any Outgoing feeder(3P) is switched OFF for maintenance, will any unbalance or earth fault in some other O/G Feeder in the same bus affect someone working on the neutral although the supply is OFF.(in the feeder under shutdown)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: 3P or 4P ACB in Outgoing feeders for TN-S system

08/23/2019 3:28 AM

An <...earth fault...> will only persist until the circuit protective device(s) disconnect the fault.

<...unbalance...> causes current to flow in the neutral conductor and it can achieve voltages, which are a function of the current flowing and the earth loop impedance. Many installations have a neutral link that is opened to enable persons to work. Downstream of the link it is possible, and desirable if not mandatory, to apply an earth connection prior to working.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: 3P or 4P ACB in Outgoing feeders for TN-S system

08/22/2019 5:42 AM

On TN-S systems the neutral is kept permanently connected. Neutral test links are fitted on larger breakers and switches.

UK private networks have to be TN-S.

The UK LV distribution system has degenerated to TN-C-S, a retrograde step in my opinion. The colonials had this system for years, the use of multiple low kVA “pole pigs” instead of large high kVA district transformers.

Something I’ll never agree with is linking MV and LV neutrals.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: