Electric Heater Controller

10/20/2007 3:15 AM

My client has requested an industrial tubular element 230V, 1.1kW electric heater for installing in a water deaerator. the sheet material of heater is Incoloy. I have problem in design and construction of related power contoller with 4-20mA input signal and variable heat ouput proportional to 4-20mA input signal.

The operation of electric heater system should be controlled by two ways:

I) The el. heater should be controlled by thermostat. This thermostat must be adjusted based on the design temperature, and is used to control the power supply for heating system.

II) The Silicon-Controlled-Rectifier (SCR), or thyristor power controller system can be used to control the power supply for heating system.

Please help me with your explanation, thpical circuit digram or a useful link.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Electric Heater Controller

10/20/2007 4:57 AM

I would think that a simple ON/OFF limit switch circuit (simple thermostat) would be sufficient.

Doubtless one of the control chaps will suggest more detailed suggestions.

1.1kw isn't a very big heater...so I'd think that the thermal inertia of the water an the small heater size would make proportional control a bit irrelevant...e.g. You will get loads of hysteresis whatever you do?

I'm happy to be shot down here....

__________________
health warning: These posts may contain traces of nut.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2007
Posts: 49
Good Answers: 1
#2
In reply to #1

Re: Electric Heater Controller

10/20/2007 6:17 AM

thank you Del the Cat (Guru).

Heater duty is compensating the heat loss of the deaerator body and type of controller is the client request and shall be considerred.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Commentator
United States - Member - Northen Member Engineering Fields - Control Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Apr 2007
Location: CookInlet AK
Posts: 67
Good Answers: 2
#3

Re: Electric Heater Controller

10/20/2007 11:05 PM

Try looking at this link.

http://iseinc.com/SCR_Power_Controls.htm

I have used a 2.0Mw unit from this company in the past.

It was a water cooled unit operating at 600VAC.

They should be able to help you out with teh controls side of it also.

Register to Reply
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#4

Re: Electric Heater Controller

10/22/2007 4:19 AM

The two way s you said is one thng.

thermostat is adjustor of controller and scr is excute components of power. you can lack any one of hem.

in fact, thee are lots of such equipments on market for choise. and scr you can just select scr at 10A/500v enough.

the 4-20ma is only a standard remote control signal to contro scr on off to get hte setting temperature.

Register to Reply
Associate

Join Date: Sep 2007
Posts: 49
Good Answers: 1
#6
In reply to #4

Re: Electric Heater Controller

10/22/2007 10:27 AM

Dear cnpower

Ouput power of heater shall be changed from 0 to Pmax. by change of 4-20mA control signal from 4mA to 20mA respectively.

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#8
In reply to #6

Re: Electric Heater Controller

10/22/2007 9:10 PM

Yes, its so called adjust power, but you can get it through voltage.

you can change conduts angle or periodic of scr to achieve it. I can send you a scheme for reference by emial. its not difficult and not too much components.

control signal 4-29ma means 4ma is zero and 20ma is one. they are deffernent concept. not continous. its a encode control.

if not too long and too noise, you neednt use this method and can send a votal or current directly to power amplifier.

Register to Reply
Commentator
United States - Member - Northen Member Engineering Fields - Control Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Apr 2007
Location: CookInlet AK
Posts: 67
Good Answers: 2
#9
In reply to #8

Re: Electric Heater Controller

10/22/2007 9:27 PM

The power controller will vary the output from 0 to 100% based on the input signal of 4 - 20 mA.

For that reason the PID temp controller is used.

Process is compared to Setpoint and the controller adjusts its output to the power controller based on the error.

Process below setpoint, ramp up output to add heat.

Process above setpoint, ramp down output to allow process to cool.

Register to Reply
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#10
In reply to #9

Re: Electric Heater Controller

10/23/2007 12:07 AM

4-20ma is a decrete signal not a continous ramp signal. dont make a mistake. its a code sequency. and canb e convert to analog signal by convertor.

pid was include in controller. of casedu feedback control.

Register to Reply
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#11
In reply to #10

Re: Electric Heater Controller

10/23/2007 12:27 AM

this code can be pwm or other type. we ususally use pwm sign. its simple and universal. the convertor is simole it can be control ed directly by amplifier to drive scr k terminal.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #6

Re: Electric Heater Controller

10/31/2007 9:41 AM

Fine. Then a thermostat is not needed, and a 3-term controller is needed instead. Has the client specified the type of control to be adopted: minimum overshoot? Fastest approach to setpoint?

Eurotherm produces units that will do this (usual disclaimers apply). These units have a self-tune function. There is no need to reinvent the proverbial wheel.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#5

Re: Electric Heater Controller

10/22/2007 8:50 AM

Try this site.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply Score 1 for Good Answer
Commentator
United States - Member - Northen Member Engineering Fields - Control Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Apr 2007
Location: CookInlet AK
Posts: 67
Good Answers: 2
#7

Re: Electric Heater Controller

10/22/2007 11:01 AM

Along with the SCR unit, The list of items needed for the control loop would include:

a). RTD element to measure the Process temp.

b). Temprature controller with a PID loop with 4 - 20 mA or 0-5V output to the SCR unit. This should have a display for Process, Output and Setpoints.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2005
Posts: 394
Good Answers: 1
#12

Re: Electric Heater Controller

10/23/2007 10:16 AM

It is kind of a small heater, but I think you can find a manufacturer offering an off-the-shelf product for your application. Most SCR electric heat controllers take a 4-20 ma or 2-10V signal. The output is pulse width modulated based on the input signal. I recall one mfg stating that their SCR or Triac would switch when the instantaneous current flow was 0 to minimize line noise.

Indeeco webpage says they have models down to 5 amps.

Register to Reply
Power-User

Join Date: Oct 2006
Location: Indonesia
Posts: 102
#13

Re: Electric Heater Controller

10/29/2007 2:35 AM

Abbas,

About this close-loop circuit, try to this site http://www.fastron.com.au/f310-cat.pdf

might this will help.

Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abbas (2); Abu Khansa (1); Bill (1); cnpower (4); CrossFire (3); Howetwo (1); PWSlack (1); user-deleted-1105 (1)

Previous in Forum: transformers calculation.   Next in Forum: 100HZ signal production

Advertisement