Wiring

10/23/2007 2:19 AM

Hi

Can someone tell me how to wire a 3way and a 4way switch for use in the country of France?

Thanks

Bill

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Wiring

10/23/2007 4:04 AM

To do what?

Why is 'France' significant?

Register to Reply
Participant

Join Date: Oct 2007
Posts: 4
#3
In reply to #1

Re: Wiring

10/23/2007 9:04 AM

Because that is were I will be installing the switch for my daughter.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #3

Re: Wiring

10/23/2007 9:11 AM

Wiring a daughter to the mains via a 3- or 4-way switch is not to be recommended, even if her behaviour makes it tempting.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Oct 2007
Posts: 4
#8
In reply to #5

Re: Wiring

10/23/2007 10:42 AM

Thanks

Register to Reply
Guru

Join Date: Aug 2007
Posts: 548
#16
In reply to #5

Re: Wiring

10/24/2007 3:56 PM

logical

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#2

Re: Wiring

10/23/2007 8:57 AM

Here is a diagram.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Wiring

10/23/2007 9:09 AM

The wiring of a light fitting between two switches, as shown in one of the diagrams on that site, would not be permitted in the UK. The original poster needs to bear that in mind.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#7
In reply to #4

Re: Wiring

10/23/2007 9:19 AM

I agree . . . It's not so bad if lamps are incandescent, but if they're fluorescent, then you get a reversal of current in an inductor => BAD

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #7

Re: Wiring

10/23/2007 11:49 AM

The current always reverses in an inductor at the rate of alternation of the current. That's not the reason.

Given the circuit shown there's a 50% chance of a lamp-holder still having a live wire going to it when there's no current flowing, placing the individual that changes a failed lamp at increased risk of shock. Switches in the neutral line are bad practice. What might be acceptable on 120VAC becomes hazardous on 220VAC and above.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#11
In reply to #10

Re: Wiring

10/23/2007 2:12 PM

We're talking about two slightly different things . . .

The illegitimate way to wire a 3-way switch is to put the lamp in the common legs of the two switches. Inductive loads are much worse than non-inductive loads, 'cause the voltage instantly reverses.

I agree with you about breaking the neutral, but the bottom two diagrams are the same, and neutral is not broken -- it's always connected to the lamps.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #11

Re: Wiring

10/31/2007 10:03 AM

<Inductive loads are much worse than non-inductive loads, 'cause the voltage instantly reverses.> On a 50Hz supply the voltage applied to a single-phase load reverses 100 times per second. On a 60Hz supply it is 120 times per second. It doesn't matter whether the load is inductive, capacitive, resistive or some combination; it's not relevant.

<neutral is not broken -- it's always connected to the lamps>

What about when both switches are connected to the live wire and the lamp is off? At this time, anyone changing the lamp and touching either of the two contacts is potentially (aaaargh!) connected to the live wire, risking an electric shock! This is why the arrangement shown in that sketch is not permitted in the UK for connection to the mains.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Oct 2007
Posts: 4
#6
In reply to #2

Re: Wiring

10/23/2007 9:11 AM

Thanks I have this diagram;but the wiring,switches and voltage they use in France are different than what we use in the USA

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#12
In reply to #6

Re: Wiring

10/24/2007 1:11 AM

I have to agree with JRaef in post #9. I have installed switches etc. in US, Europe, and South America. The components may look different, and of course higher voltage allows smaller wire to carry the same power as larger wire at lower voltage, but the function is the same. A three way switch (also known as single-pole double-throw) will always move some conductor to connect point C (common) to either point A or point B. And so on...

As indicated by at least two others, the circuit chosen should maximize safety of the ignorant (only non-energized wires leading to the socket of a lamp in the off position, if possible).

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Wiring

10/23/2007 11:36 AM

Sorry, but AC power does not know borders or languages, it all works the same. The switches may look different, but they would operate the same way; the concepts are fundamentally identical no matter where the circuit is. You may need to apply some human brain power in a process called "adaptive interpretation" in order to make it work. If you (or your daughter) cannot figure this out, you have NO BUSINESS messing with electricity and need to hire a professional electrician. They will not need to ask for help.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2006
Posts: 443
Good Answers: 2
#13

Re: Wiring

10/24/2007 1:57 AM

In the US many newly purchased switches come with a wiring diagram right in the box (small instruction sheet) or on the box, can't speak for products purchased in France though.

Register to Reply
Power-User

Join Date: Mar 2006
Location: Valdosta, GA
Posts: 361
Good Answers: 8
#14

Re: Wiring

10/24/2007 11:30 AM

ouvrez la boîte. lisez les instructions et suivez-les.

Le pouvoir passe par les changements avant le fait d'atteindre la charge dans n'importe quel pays.

__________________
Always use protection.
Register to Reply
Anonymous Poster
#15

Re: Wiring

10/24/2007 1:12 PM

Here's a sketch of two 3 Way and one 4 way switch circuit.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #15

Re: Wiring

10/31/2007 10:14 AM

This arrangement is the recommended way for wiring a single lamp, or a cluster that operates as one, from multiple switches. Changing any switch turns the lamp from on to off or vice-versa. The neutral is carried through to the lamp and the arrangement ensures that, when the lamp is off, no live connection is made to the lamp. This is the correct way for mains voltages so as to ensure safety.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 18 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (3); dkwarner (1); JRaef (1); Keywalker (1); klausmouse (3); PWSlack (5); user-deleted-5 (1); vikas (1)