Fluke 435-II

12/03/2019 9:39 AM

The current range default setting for Fluke 435-II is 3000A.

Manual states, the default settings are good to start.

Does this need to be changed to match the load current?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Fluke 435-II

12/03/2019 10:03 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Dec 2019
Posts: 5
#3
In reply to #1

Re: Fluke 435-II

12/03/2019 3:04 PM

From The manual

"The Range of waveforms is preadjusted for a good display in almost all cases. This is based upon Nominal Voltage (Vnom) and Current range (A Range). If desired, you can change the Range."

So for 60-70A load current expected, the current range should be set to 100A?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #3

Re: Fluke 435-II

12/03/2019 3:11 PM

The current could spike well above what's expected...so a comfortable safety margin should be incorporated...I would set to maximum circuit capacity++, or above trip current..

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Fluke 435-II

12/03/2019 12:49 PM

If you are measuring amps above 3000 then you need to set the range higher...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#5

Re: Fluke 435-II

12/03/2019 11:35 PM

I believe the range should be set to the range of the current probes In use. Different types of current probes used with these power quality instruments have different ranges.

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#6

Re: Fluke 435-II

12/03/2019 11:37 PM

The default range (or the highest) is where you start. If reading is less than 1/3 scale, you downrange to get a higher indication for better accuracy.

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Member

Join Date: Dec 2019
Posts: 5
#7
In reply to #6

Re: Fluke 435-II

12/04/2019 1:49 PM

Thanks. I have another issue.

The network is 3 phase 4 wire, but the panel of interest is 3 phase 3 wire.

Shall I connect the neutral ct and voltage probe to the ground wire.

Thanks

Register to Reply
2
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#8
In reply to #7

Re: Fluke 435-II

12/04/2019 5:06 PM

No, follow the instrument instructions to configure the Fluke for 3-wire. The manual shows how to do this on page 24-10 (Page 124 of the .PDF).

Register to Reply Good Answer (Score 2)
Member

Join Date: Dec 2019
Posts: 5
#9
In reply to #8

Re: Fluke 435-II

12/04/2019 8:16 PM

Thanks. I did it in delta with phase to phase voltage 600v as it was suggested by fluke technical supports

Appreciated your response and hopefully did the correct thing

Register to Reply
Member

Join Date: Dec 2019
Posts: 5
#10
In reply to #9

Re: Fluke 435-II

12/05/2019 4:43 PM

One more clarification I have about the connection.

I connected the phases correctly as labeled on the panel (L1, L2, L3 left to right) and I got rotation CBA. I switched L1 and L3 Voltage and CT sensors and got the correct Indication ABC.

I considered the labels and the colour codes on the feeder cable wrong. or could it be a setting parameter that reads CBA although the rotation should be ABC. I saw some setting video for older version which has indication of sequence or rotation, which indicate opposite direction or rotation

Obviously asking to change is a lot of work, as all the motors (28 nos.)are connected and running.

Let me know your input on the equipment if there is a setting issue.

Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#11
In reply to #10

Re: Fluke 435-II

12/05/2019 6:18 PM

I don't change something that works. It would be a good idea to document what you find, for instance which color wire is connected to L1 and so forth.

Phase rotation is arbitrary anyways. CBA or ABC doesn't really matter if your motor rotates in the desired direction. But Fluke gives you an ambiguous symbol anyways.

Flip your A and C connections and the arrow should show the other direction. For whatever that's worth.

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments: