Under ground 11 kv cable

10/25/2007 9:27 AM

Can we lay more than one cables carrying 11kV in the same conduit. Is there any standard?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Under ground 11 kv cable

10/25/2007 9:52 AM

It depends upon the country, which isn't stated.

Register to Reply
Anonymous Poster
#2

Re: Under ground 11 kv cable

10/25/2007 10:00 AM

Yes you can install more than one conductor in a single conduit as long as there is no prohibition in your electrical code. We routinely install three 23KV cables in PVC conduits. Make sure the bending radius is long enough so that you don't damage your cable when pulling it in to the equipment.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Under ground 11 kv cable

10/25/2007 10:22 PM

It is better to install in separate conduits so that in the vent of a fault and cable burst the other cable is not damaged.In earlier days when cables were laid in In underground trenches even then 11KV and large size cables separated by suitable means though they were in the same trench.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Active Contributor

Join Date: Oct 2007
Location: Philippines
Posts: 17
#4
In reply to #3

Re: Under ground 11 kv cable

10/26/2007 4:06 AM

For Clarity, what type of cable we are talking about?? 11kv- 1core or 3 core cables

Register to Reply
Associate

Join Date: Jul 2007
Posts: 37
#5
In reply to #4

Re: Under ground 11 kv cable

10/26/2007 9:46 AM

Its 11kV, 3-Core, 90mm cable.

Register to Reply
Active Contributor

Join Date: Oct 2007
Location: Philippines
Posts: 17
#6

Re: Under ground 11 kv cable

10/27/2007 12:24 AM

there's no restrictionwhether to lay it adjacent to other circuit. the only restriction is the derating factors which should be considered during sizing of conductors.

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#7
In reply to #6

Re: Under ground 11 kv cable

10/27/2007 12:38 AM

let me share some of my experience with all, while i working in middle east project, that country code strictly prohabitate more than one cable in single duct, cable size is 11 kv, 240 sq mm, 3c but when i worked for new british embassy in doha, qatar, it is allowed to lay more than one cable in single duct but there is a restriction of duct length, in INDIA, it is not recomonded, even multiple layer allowed under special case.

__________________
manirul
Register to Reply
Guru
Canada - Member - Toronto, Ontario (South Parkdale On The Lakeshore) Engineering Fields - Marine Engineering - Great Lakes School Of Marine Technology (Owen Sound and Port Colbourne) Technical Fields - Architecture - Private Practice 1976-1990 Technical Fields - Education - Toronto Teachers' College 1971 Technical Fields - Marketing/Advertising - Founding Member Hobbies - Hunting - Founding Member Hobbies - Target Shooting - Founding Member

Join Date: Mar 2006
Location: Toronto Ontario Canada
Posts: 1265
Good Answers: 14
#8

Re: Under ground 11 kv cable

10/27/2007 10:38 AM

Hi, Syed Ziauddin!

It's not my area of expertise, but it seems to me that if the cables are trefoiled, there might be no adverse effects from bundling them.

In addition, if money is not an issue, you might also shield the cables with a mu metal foil and surround either the outer insulation or the conduit with grounded wire mesh to eliminate possible emf and rf propagation into the human environment near the underground tunnels.

But when is money ever not an issue?

Mark

Register to Reply