HT Power Transformers

02/03/2020 8:41 AM

We are having two nos.very old transformers. Their ratings are i) 10 MVA, 33KV / 3.3KV and ii) 7 MVA, 33KV / 3.3 KV. We are not able to load them properly as temperatures are increasing. On 10 MVA transformer, we are able to load only 5.5 MVA and on 7 KVA transformer, we are able to load only 3.5 MVA. In fact, we are not knowing the rating of 7 MVA transformer as no details are available and no name plate. But, it is being told by previous people who are working in the company, but there is no authenticity. Is there any way how I will be knowing the existing capacity / rating of the transformers so that I can plan my loads properly. What are the tests specified to know the capacity of the transformer?

Register to Reply
Pathfinder Tags: capacity of HT transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: HT Power Transformers

02/03/2020 10:58 PM

Then load only 5 MVA and 3.5 MVA only.

Check for harmonics.Also check for cooling method, Natural or forced cooling.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3
In reply to #1

Re: HT Power Transformers

02/04/2020 12:05 AM

Harmonics caused by new inverter loads, such as VFDs are likely a reason that a previously cool transformer becomes hot with a similar ampere load.

Also, the designed primary voltage needs to be held close to original design. It is possible that when installed, it may have been repurposed from some other system voltage, perhaps a bit lower, but now increasing load adding to temperature rise. You can test this with the unit unloaded, check the turns ratio.

Also, if liquid cooled, I have found where some cooling fin banks show no temperature rise, while others on the other side of the tank do. 30 year old transformers, I assumed that sludge blocked the entry of oil into the cooling headers at the bottom of the transformer. These transformers were very lightly loaded for a long time.

Low oil level reduces the heat capacity of the cooling equipment.

Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#2

Re: HT Power Transformers

02/03/2020 11:03 PM

The temperature rise is probably the only way to determine the rating of a transformer. But what are their specs for temp. rise? The following link may help determine it:

https://www.copper.org/environment/sustainable-energy/transformers/education/trans_efficiency.html

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#4

Re: HT Power Transformers

02/04/2020 12:33 AM

This may be a long shot, but....

Are you multiplying the line current by 1.732 when calculating MVA? The capacity difference you report is similar to using line to line voltage and line current to calculate MVA. The rated secondary line current of your 10MVA unit is 1750 amperes. However, if you assumed it was 3000 amperes, your transformer would start overloading at 57% load, or 5.77 MVA.

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#5

Re: HT Power Transformers

02/04/2020 11:26 AM

There are standards specifying the methods for various tests to be conducted to test the performance of transformers (IEC standards). You may like to perform open circuit and short circuit heat runs at various currents to get maximum permissible temperature rise ( assuming that you know the class of insulation of the winding and the rated voltage of the windings, cooling parameters i.e. amount of cooling water flow etc. I hope you are not assuming these conditions in absence of rating plate).

Which temperature is limiting the rise of load to your assumed rated load? Is it winding temperature of core temperature? This information is important. A loose core might have resulted in core hot spots. You may like to compare the temperature rise of active parts with older operation logs, if available.

Register to Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#6

Re: HT Power Transformers

02/07/2020 3:16 AM

(Usual disclaimer re. ancient knowledge, etc.) To deal with the symptoms, on a very old transformer I would check for sludge limiting oil flow as someone else suggested. You can do a sludge test if I recall correctly - think it is called an acidity test. Not sure what tests one will do to check actual electrical performance ratings.

Slightly off-topic, I would also do a furan (furaldehyde?) analysis - this checks the condition of the paper insulation without the intrusiveness of taking an actual paper sample for a DP test - as acidity degrades the insulation. In fact, on such old transformers I took samples annually and did the full barrage of tests, including DGA (dissolved gas analysis). It allows for trend analysis and early warning of brooding trouble.

Register to Reply Score 1 for Good Answer
Register to Reply 6 comments