How Do You Correctly Calculate the Heat Transfer Load?

02/24/2020 11:30 AM

I'm trying to determine the heat transfer load of a sealed cabinet I'm a bit confused about the formula that is apparently used for it. I would appreciate some help. The formula is:

(q = (To - Ti ) ÷ [(1/ho ) + (1/hi ) + R] x 5.67

Definition of Variables— q = Heat transfer load per unit of surface area To = Maximum ambient temperature outside the enclosure Ti = Maximum rated temperature of the electrical components ho = Convective heat transfer coefficient outside the cabinet Still air: h = 1.6 Relatively calm day: h = 2.5 Windy day (approx. 15 mph): h = 6.0 hi = Convective heat transfer coefficient inside the cabinet Still air: h = 1.6 Moderate air movement: h = 2.0 Blower (approx. 8 ft.3/sec.): h = 3.0 R = Value of insulation lining the interior of the enclosure walls No insulation: R = 0.0 1/2 in. or 12 mm: R = 2.0 1 in. or 25 mm: R = 4.0 1-1/2 in. or 38 mm: R = 6.0 2 in. or 51 mm: R = 8.0

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: How do you correctly calculate the heath transfer load?

02/24/2020 11:50 AM

It's analogous to an electrical circuit, where heat flow (q) is like current (I), temperature differential (To-Ti) is like voltage (V).

Ohm's law for electrical current: I = V / R, current = voltage / resistance.

Equivalent law for flow of heat: (q = (To - Ti ) ÷ [(1/ho ) + (1/hi ) + R] x 5.67

To pass from inside to outside the heat has three "obstacles", internal convection (1/hi), conduction through the cabinet wall (R), and external convection (1/ho). It's like three resistors in series for an electrical circuit. Note that the convection "resistance" is the inverse of the convective "conductance", (hi or ho).

I hope this helps...

Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#2
In reply to #1

Re: How do you correctly calculate the heath transfer load?

02/24/2020 11:59 AM

Hi Rixter, thanks for your answer. The part that is not clear to me is the calculation of the ∆T, for me the value will be negative... I've considered To as 30°c while the Ti which is the rated temperature of the electronic components running inside my enclosure is 60°c.

So To-Ti is -30...

Register to Reply
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: How do you correctly calculate the heath transfer load?

02/24/2020 12:28 PM

All the negative sign indicates is that the heat flow is going from the inside to the outside.

A parallel is that of the convention in an exothermic chemical reaction: heat flow also comes out in negative numbers, as heat flows out of the system as a result of the reaction taking place.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Feb 2020
Posts: 22
#4
In reply to #3

Re: How do you correctly calculate the heath transfer load?

02/24/2020 12:32 PM

PWSlack i thought about that but I wasn't sure!

Thank you so much!

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#5
In reply to #2

Re: How do you correctly calculate the heath transfer load?

02/24/2020 2:40 PM

The guy that derived the formula picked the opposite direction. Maybe he was figuring for an ice chest.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#9
In reply to #2

Re: How do you correctly calculate the heath transfer load?

02/25/2020 8:42 AM

Presumably you need to ensure the calculated total heat loss (q*cabinet surface area) at least = the heat generated by the electronic components. If so, for safety you would most likely use the lowest figures for h, but have no insulation, as insulation would reduce heat flow.

What is the blower doing? If it draws outside air through the cabinet and then vents it, it might keep the inside temperature within limits without worrying about the convective heat losses.

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#7
In reply to #1

Re: How do you correctly calculate the heath transfer load?

02/24/2020 10:10 PM

Funny about your analogically example,... i had explained to green engineer about an electrical circuit by using a pneumatic circuit about 2 months ago.

And one can even see the light bulb lighting up in their eyes... so to speak...

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Score 1 for Off Topic
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#6

Re: How Do You Correctly Calculate the Heat Transfer Load?

02/24/2020 10:06 PM

Not quite that simple,... hence your question. I’ve written excel sheets with vbasic that did that, but it’s been quite a while since, so I did a quick internet search ... and Concluded, I was born about 25 years too late, could have saved me some time because there’re all over the internet.

there are a number of variables you need to solve concurrently, and to do this without going through details, you would need to enter an approximate starting point (number) and then solve using iterations. And the more iterations that are used, the more accurate it is... theoretically accurate that is.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Power-User

Join Date: Nov 2008
Location: Port Glasgow, Free Republic of Scotland
Posts: 360
Good Answers: 30
#8

Re: How Do You Correctly Calculate the Heat Transfer Load?

02/24/2020 11:37 PM

the other issue of course is units

seeing that ugly 5.67 suggests to me that this is a calculation in Imperial / US Customary units. Its also not clear to me if the 5.67 should be in the numerator or denominator

This is a rearrangement of Q = U A ΔT

Where U - overall heat transfer coeff 1/U = 1/hi + 1/ho + R

so you have Q/A = (To - Ti) / (1/hi + 1/ho + R)

I would normally go with

Q - W

A - m2

q - W/m2

T - K (or °C) they are the same for temp changes

h - W/m2K

R - m2K/W if using Thermal Insulance (the R value you quote)

or if using Specific thermal resistance mK/W and you will multiply by the insulation thickness (symbol t measured in m)

In this case you end up not needing a conversion factor and

q = (To - Ti) / (1/hi + 1/ho + R)

or q = (To - Ti) / (1/hi + 1/ho + Rt)

Your data is throwing around various Imperial units with different length and time dimensions and so you should carefully work through the calculation to determine the unit correction factor.

The insulation term (R or Rt) would be the first place I would look.

__________________
Free advice guaranteed or your money back
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#10

Re: How Do You Correctly Calculate the Heat Transfer Load?

03/08/2020 1:19 PM

You seem to be overly worried about the sign, without focussing on the numbers, Mildred. Those who give a damn about the sign will be few and far between.

__________________
Good moaning!
Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#11

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/27/2020 4:19 AM

Hi again, can anyone explain to me this table?

I don't understand why the bigger is the ΔT the less air flow you need...
I would have thought that if you have a bigger number it means you need more air to cool the enclosure. Sorry if I'm being stupid but I can't read it.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#12
In reply to #11

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/27/2020 6:30 AM

You can't cool below ambient with just air....the greater the differential the more air you need...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#13
In reply to #12

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/27/2020 6:48 AM

I know that, that's the thing if the ambiente temperature is 35°c and inside the enclosure the temperature reaches 75°c the ΔT is 40. If you cross reference 40 with lets say 1500w load you get a lower air flow than if your ΔT was 20 for instance.
That's not clear to me...

I would imagine that the bigger is the ΔT the bigger is the volume of air necessary to lower the internal temperature close to the ambient one.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#14
In reply to #13

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/27/2020 9:10 AM

You are calculating the airflow needed to dissipate the heat being produced according to maximum temperature allowed...If your components have a max operating temp of 120°, and your max ambient is 95°, and your equipment is generating 200 watts of heat, you need enough airflow to dissipate 200 watts of heat with a 25° operating range above the max ambient of 95°...The amount of air flow will depend on the enclosure area, let's say you have a 1 cu ft enclosure...then you need to determine the static pressure of the enclosure...

The volume of air will always allow for some heat rise in the enclosure, that's what you are looking at...You have to keep the level of heat rise below the max operating temp minus the ambient....

https://blog.exair.com/2017/03/22/not-a-fan-of-fans-because-rising-air-temp-will-kill-your-electronics/

http://cyntech.co.uk/cooling-power-supplies/

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#16
In reply to #14

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/27/2020 4:49 PM

I still don't get the last table...

It's not clear to me why the bigger is the difference between the ambient temperature and the internal temperature and the least air flow you need.

Sorry if being stupid but I don't get how to read that table.

"You have to keep the level of heat rise below the max operating temp minus the ambient"

That's what I want to do but I'm not getti how I can determin the airflow needed to lower the internal temperature at least 30° [outside is 35°c and inside is 76°c]

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#15
In reply to #13

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/27/2020 11:22 AM

I think you're getting 2 different thiongs mixed up.

To calculate heat flow through a system of known conductivity, heat flow q is proportional to ΔT, as in your formula q = (To - Ti ) ÷ [(1/ho ) + (1/hi ) + R] x 5.67.

But if you want to calculate air flow qair (m3/s) to remove a given heat load q,

qair = q/ΔT/C where q is in kW, ΔT = max temp acceptable in the enclosure minus incoming air temp, and C = air specific heat, in the region of 1.2 kJ/m3/K

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2020
Posts: 22
#17
In reply to #15

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/27/2020 4:55 PM

Yeah I need the second formula then.

But how does it work with the numbers I have?

Incoming air temp. 35°c

Max acceptable internal temp 35°c

Internal temperature during normal working cycle 76°c [when outside is 35°c]

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#18
In reply to #17

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/27/2020 7:14 PM

If your max operating temperature for internal components is 76°C and your ambient temperature is 35°C, then the differential is 41°C....So if you have 1500 watts total load just look at the chart and determine how much air flow you need to keep the temperature within operating parameters...I would allow a safety margin, you always design cooling to overcome the temperature on the hottest day, that is your design temperature...If your hottest day is going to be 48°C, then that is your design ambient...So your max temperature for your components should target below 76°C to say 60°C...So you need to make a determination what duty cycle you want for the fan, over a certain temperature it runs all the time or it cycles on temperature with a thermostat...So when the temperature hits 60°C the fan kicks on and stays on until the temperature hits 45°C, say as an example, so you have a 15°C differential...

Now the amount of air flow you need can be found with the chart... the difference between 76°C and 60°C these are your max operating conditions, is 16°C, 1500 watts is equal to 5100 btu's/hr, so we look at the chart and see we need about 350 cfm...So to overcome static pressure and recovery time we would probably go with about 450 cfm...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#19
In reply to #18

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 5:24 AM

Much more clear, one thing though, the operating temperature is not 76°c. That is the temperature that the totem reaches inside while operating in a sunny day. The max operating temperature for the electric components inside should not be bigger than 35°c

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#20
In reply to #19

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 5:50 AM

The design temperature here in Florida is 95°F - 75°F , that means we size the A/C units at the tonnage that will pull the temperature down to 75°F on a 95°F day....The design temperature of the electrical components is the maximum temperature that they will continue to function properly...

..."Conventional electronic components are designed to operate over a specified temperature range with upper limits generally set at 70°C for commercial applications, 85°C for industrial applications, and 125°C for military applications."...

Ref...

So when you are designing a system for cooling, there is a reason, for dwellings it's comfort and humidity control, but for electrical components, it's to keep them operating properly...In some cases that requires forced ventilation...in some cases it requires A/C... In any case you use the design temperature as a guide for sizing cooling components...Now whether it's cooler outside than the design temperature only means that the unit will have to run less, but on the days that it reaches the design temperature, it will still do it's job....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#22
In reply to #20

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 7:50 AM

Most of the stuff inside there will work with no problems around 70° but I have also quite big LCD display in there and the company specified that they have to be around maximum 50°C to avoid quick pixels deterioration and invalidate the warranty.

To be on the safe side I wanted to keep the temperature around the ambient one.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#21
In reply to #17

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 7:05 AM

The 2 statements

Max acceptable internal temp 35°c

Internal temperature during normal working cycle 76°c [when outside is 35°c]

appear to be contradictory. Is the 76°C the temperature reached in the sun? (which your design is presumably trying to prevent). But that wouldn't be Internal temperature during normal working cycle. Please explain.

If possible, a sunshade could be provided. Otherwise, you would need to estimate the heat input from the sun, add this to the heat generated by the internal kit, and design the ventilation flow for that.

But if the outside temperature (hence cooling air input temperature) is 35°C you clearly cannot have inside temperature the same or air flow is ∞. There has to be a compromise. When you have decided on the ΔT available you can find the air flow either from the chart posted or my formula.

__________________
Give masochists a fair crack of the whip
Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#23
In reply to #21

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 7:58 AM

So "appear to be contradictory. Is the 76°C the temperature reached in the sun?" yes that is the temperature that the volume inside my enclosure will reach in a summer sunny day,
during normal working cycle. That's why I must reduce that temperature to avoid deterioration of the components inside. [critical temperature for some of those electrical components is 50°c so I would want to try to lower the temperature to 35°-40° max]

"If possible, a sunshade could be provided. Otherwise, you would need to estimate the heat input from the sun, add this to the heat generated by the internal kit, and design the ventilation flow for that."
No shading is possible and yes I did all the calculations considering internal heat load, heat dissipation through the enclosure walls, solar gain etc. and I found out that the temperature hit 76°c.
"design the ventilation flow for that"
that's where I'm stuck, I can't get around the determination of the air flow volume necessary to lower that temperature.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#24
In reply to #23

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 9:10 AM

"yes that is the temperature that the volume inside my enclosure will reach in a summer sunny day," In that case it's not the "Internal temperature during normal working cycle."

What heat load have you arrived at?

With outside air temperature 35° and maximum inside 40° that gives ΔT 5°. From that it's easy to calculate air flow using my formula. Give me your heat load and I'll do it for you.

__________________
Give masochists a fair crack of the whip
Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#28
In reply to #24

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 11:48 AM

Does this make sense?

https://drive.google.com/file/d/1QmHRDlzNZZUMBrME2DPNE3EBie3XJfHA/view?usp=sharing

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#25
In reply to #23

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 9:56 AM

Maximum temperature reached sitting the Sun has no meaning in calculating heat gain, which is the btuh gain....

..."Heat Load Transfer Heat load transfer is the heat lost (negative heat load transfer) or gained (positive heat load transfer) through the enclosure walls with the surrounding ambient air.

This can be calculated by the following formula:

Heat load transfer (BTU/H) = 1.25 x surface area (sq. ft.) x (max. outside ambient air (°F) – max. allowable internal enclosure temperature air (°F)) Surface Area (sq. ft.) = 2 [(H x W) + (H x D) + (W x D)] / 144 sq. inches Note: 1.25 is an industry standard constant for metal enclosures;

...0.62 should be used for plastic enclosures. Once you have determined your Internal Heat Load and the Heat Load Transfer, you can choose the proper size unit by calculating the needed cooling capacity. Cooling capacity (BTU/H) = Internal Heat Load ± Heat Load Transfer"...

https://www.stego-usa.com/nc/support/calculation-tools/cooling-calculation/

https://cdn.automationdirect.com/static/specs/enccoolingselection.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#26
In reply to #25

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 10:46 AM

In #23 OP said he's already done the calcs.

There's no mention of wall conductivity in your formula, so I assume it just applies to sheet metal enclosure. I can't see anything about heat from the sun.

__________________
Give masochists a fair crack of the whip
Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#27
In reply to #26

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 11:44 AM

Does this make sense?

https://drive.google.com/file/d/1QmHRDlzNZZUMBrME2DPNE3EBie3XJfHA/view?usp=sharing

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#29
In reply to #27

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 2:11 PM

What are the measurements of the cabinet? Your heat gain seems reeally high...I think you are figuring heat gain in BTU's per hour and CFM air flow in CF per minute...Is this cabinet to be in the shade or direct sun exposure...You might just need louvered ventilation...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#31
In reply to #29

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 3:28 PM

In #23 OP said it's in the sun and can't be shaded.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#30
In reply to #27

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/28/2020 3:25 PM

If the inputs are correct I don't see a problem. Assuming the heat transfer load calc with the 5.67 factor is correct (I don't know the source).

No calc is given for the solar heat gain.

Possibly insulation would help, this would reduce the solar gain and also the -ve heat transfer load, and there might be a net reduction.

The 76.6° figure isn't used as far as I can see. Using ΔT 5° and 1156 watt I make air flow just over 400 cfm, so 500 cfm for some safety is reasonable.

__________________
Give masochists a fair crack of the whip
Register to Reply
Power-User

Join Date: Jan 2009
Posts: 227
Good Answers: 11
#34
In reply to #15

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/08/2023 1:32 AM

The point of the graph is that the less airflow you have, the greater your temperature rise will be for a particular value of thermal power to be dissipated.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#33
In reply to #13

Re: How Do You Correctly Calculate the Heat Transfer Load?

07/04/2023 7:07 AM

The opposite is true. The closer the approach desired to the selected temperature, the more fluid at that temperature will be needed to make the approach from the calculated temperature.

Because of the heat dissipation, the selected temperature can never be equal to the ambient temperature, as that would require an infinitely large fluid flow.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Feb 2020
Posts: 22
#32

Re: How Do You Correctly Calculate the Heat Transfer Load?

09/02/2020 12:14 PM

Guys, I have a question, when I calculate the internal heat load I take into account everything that absorb power.

I have a doubt...if I have for instance 15w led module obviously goes in the calculation but what about its transformer [which is indeed a 15W driver]

How does it work, do I take in to account both like 15W + 15W?

Obviously both produce heat...

Thanks

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#35
In reply to #32

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/08/2023 3:31 AM

You seem to be looking at the nominal size rating of these components instead of the actual wattage load...If you look at a circuit breaker at 15 amp rating and 120v line that = 1800 watts, that's the max safe load, not the actual wattage being used...The efficiency of the driver is likely to be around 80%, so you would add 20% of the load as heat to the 15 watt LED, or 3 watts...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#36
In reply to #35

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/08/2023 6:09 AM

You might have added that an 1800 watt breaker only dissipates a few watts (maybe, if it has a coil) whether it's at max load or lower actual load.

For the LEDs the driver data might include input power at design 15 watt output, hence heat loss, and the LEDs may not consume 15 watt, reducing the internal heat load.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#37

Re: How Do You Correctly Calculate the Heat Transfer Load?

08/08/2023 9:32 AM

Friends,

Lots of good information and questions in this topic. A few I will add:

  • Always include the units as you work the formulas--a mixture of imperial and metric will result in errors that are easy to catch when the units are included.
  • For the display, the manufacturer seems to be stating the maximum ambient temperature for it, not the actual maximum surface temperature the components are safely operating at internally. So the 35ºC needs to be heeded.
  • A few posts have mentioned radiative heating/cooling, but the various formulas I have seen don't include this. This is directly related to the surface's reflectivity (the inverse of emissivity), a unitless number that ranges from nearly 0 to 1. To minimize heat gain due to direct solar exposure, the reflectivity needs to be as high as possible, so a black or average metal surface is a poor choice (white is much better, as is a polished silvery surface). To increase heat transfer OUT of the enclosure, its interior walls need a low reflectivity, but if the walls are warmer than the desired interior temperature a high reflectivity is desired.
  • Wally 89, you are a newer member of the community. Welcome. Keep asking questions and keep studying. Mistakes are made by all of us, so lean from them also.
  • The lifespan of electronic components is significantly reduced (or increased) by changes in their operating temperature. An approximate rule-of-thumb is a 10ºC increase above the specified operating temperature cuts the life span by 50%; a similar decrease results in a much greater life span. So yes, you can operate devices at too high a temperature if you are willing to sacrifice their life. Of course there are limits on how high, when the component fries instantly.

--JMM

Register to Reply
Register to Reply 37 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Codemaster (8); Crabtree (1); jmueller (1); MNIce (1); phoenix911 (2); PWSlack (2); Rixter (2); simonsd (1); SolarEagle (7); Wally89 (12)

Previous in Forum: Pressure Vessel Erection   Next in Forum: Design Standard for Free Standing FRP Stack

Advertisement